RE: [Repeater-Builder] MOVs for power supply primary

2010-06-12 Thread Jeff DePolo

OK, you're looking for something in the middle then.

For parallel protectors,  LEA CFS or SP series, or Transtector Apex II, may
be more in the price range you're looking for (under $1000).  Since I don't
use protectors of that kind regularly, I don't have any other
recommendations other than to stick with repetuable manufacturers and read
the data sheets.  The cheaper ones will probably be MOV-only.  Others may
use a combination of MOV's, SAD's, and/or gas discharge tubes.  There are
pros and cons to each...

I don't know of any series protectors that fall into the price range of what
I would think you're looking for.  

Someone else (Eric?) mentioned Square D.  The only Square D ones I've used
are the ones that are built into the panel (Surgelogic or something like
that?), not the add-on ones.  We had to replace one in a 3-phase 480/277
panel not too long ago, that's the only reason I'm familiar with them (they
have an audible alarm that goes off when the arrestor detects a fault, a
nice feature).

--- Jeff WN3A


 -Original Message-
 From: Repeater-Builder@yahoogroups.com 
 [mailto:repeater-buil...@yahoogroups.com] On Behalf Of Chuck Kelsey
 Sent: Wednesday, June 09, 2010 8:51 PM
 To: Repeater-Builder@yahoogroups.com
 Subject: Re: [Repeater-Builder] MOVs for power supply primary
 
   
 
 OK, I'm familiar with those single-point grounding panel 
 protection devices.
 
 How about a service panel protector for home use?
 
 And a service panel protector for a small (200A) 3-phase panel?
 
 I ask, rather than simply Google for it, because Google could 
 come up with 
 some units that are not good.
 
 Chuck
 WB2EDV



RE: [Repeater-Builder] MOVs for power supply primary

2010-06-09 Thread Jeff DePolo

Hmmm.  That's a tougher one.  Mostly I use the Polyphasers (PLDO-120US-15A
or -20A) at sites that don't have facility-wide protection.  The TrippLite
Isobar Ultra series is another (ISOBAR8ULTRA et al).  The Isobars also have
a $50,000 equipment warranty (can't say I've ever had to use it, don't know
how much red tape there is to go through).  I like the Polyphasers because
it's designed to mount to a ground panel/bus bar, so I mount it to the bus
bar that has all of my other arrestors (coax, telco, etc.) on it to provide
a common-point ground.  The Isobar doesn't have provisions for direct
grounding - it relies only on the equipment grounding conductor in the AC
cord, but the TrippLite has arguably better EMI/RFI filtering than the
Polyphaser.

--- Jeff WN3A


 -Original Message-
 From: Repeater-Builder@yahoogroups.com 
 [mailto:repeater-buil...@yahoogroups.com] On Behalf Of Chuck Kelsey
 Sent: Tuesday, June 08, 2010 4:48 PM
 To: Repeater-Builder@yahoogroups.com
 Subject: Re: [Repeater-Builder] MOVs for power supply primary
 
   
 
 OK, I should have been more specific. What would be a 
 reasonable unit for a 
 repeater site that may have only a couple thousand dollars worth of 
 equipment inside?
 
 Chuck
 WB2EDV
 
 - Original Message - 
 From: Jeff DePolo j...@broadsci.com mailto:jd0%40broadsci.com 
 To: Repeater-Builder@yahoogroups.com 
 mailto:Repeater-Builder%40yahoogroups.com 
 Sent: Tuesday, June 08, 2010 4:22 PM
 Subject: RE: [Repeater-Builder] MOVs for power supply primary
 
 
  Probably the ones I've had the most luck with are the 
 Islatrol series from
  Control Concepts. I think they have been bought out by 
 Emerson or Liebert
  or one of the other companies that have power divisions. 
 Anyway, they 
  call
  these active tracking filters. They not only are TVSS's 
 but also filter
  noise, low-amplitude spikes, etc. Right now I'm typing from 
 a mountaintop
  site (broadcast) that we re-built a few years ago. We put 
 in an Islator
  I-2100 (120/240V single-phase). The old equipment shelter 
 which had been
  here since 1990 had the same model unit. In the 15+ years we've been
  managing and maintaining the site, we've had zero 
 surge-related failures,
  and this site sticks out like a sore thumb as far as 
 lightning goes. In 
  the
  last few years I've used the same series of arrestors for 
 new site builds 
  at
  a dozen sites or so and have had no power-related problems.
 
  Others that make comparable-quality products include 
 Joslyn, Transtector,
  and Innovative Technologies.
 
  There is one big difference (to me anyway) between TVSS's, 
 that being
  whether they are the series or parallel type. Series type takes the 
  utility
  service (or transfer switch output if there's a generator 
 too) as its 
  input,
  and provides a protected output to feed the panel(s). 
 Parallel type is
  typically connected to a breaker in the panel, which puts 
 it in parallel
  with all of the loads. I much prefer series. Parallel type 
 can be less
  effective because a) there will always be some inductance 
 and resistance 
  in
  the wiring between the panel and the protector, b) if the 
 TVSS conducts,
  there's a good chance it will trip the breaker in the 
 panel, resulting in 
  no
  protection until the breaker is reset, and c) they are much 
 less effective
  as a noise filter. The upside to parallel type is they can 
 easily be 
  added
  at any time just by popping breakers in the panel and feeding the 
  arrestor.
  Series, on the other hand, are in-line with the service 
 conductors, so if
  you want to add one (or repair one), you have to take the 
 service down.
  Series tends to also be more expensive, especially for 
 three-phase and
  unlike parallel type, the price goes up as the current 
 rating goes up for
  obvious reasons.
 
  A good 200A single-phase arrestor of the ilk I'm talking 
 about starts at
  about $1000 and goes up quite a ways from there. I think these 
  single-phase
  I-2100's were in the $2000 range. I recently spec'ed a 
 120/208 3-phase
  Transtector (parallel type) for another site where I'm much 
 less concerned
  about power-wise, and that was about $1800. No cheap, but 
 where you're
  protecting equipment in the 6 and 7 figure range, it's a 
 no-brainer. If
  you're repeater is a Micor mobile and an Astron, it might be hard to
  justify... :-)
 
  --- Jeff
 
 
 
 
 



Re: [Repeater-Builder] MOVs for power supply primary

2010-06-09 Thread Chuck Kelsey
OK, I'm familiar with those single-point grounding panel protection devices.

How about a service panel protector for home use?

And a service panel protector for a small (200A) 3-phase panel?

I ask, rather than simply Google for it, because Google could come up with 
some units that are not good.

Chuck
WB2EDV



- Original Message - 
From: Jeff DePolo j...@broadsci.com
To: Repeater-Builder@yahoogroups.com
Sent: Wednesday, June 09, 2010 1:13 PM
Subject: RE: [Repeater-Builder] MOVs for power supply primary



 Hmmm.  That's a tougher one.  Mostly I use the Polyphasers (PLDO-120US-15A
 or -20A) at sites that don't have facility-wide protection.  The TrippLite
 Isobar Ultra series is another (ISOBAR8ULTRA et al).  The Isobars also 
 have
 a $50,000 equipment warranty (can't say I've ever had to use it, don't 
 know
 how much red tape there is to go through).  I like the Polyphasers because
 it's designed to mount to a ground panel/bus bar, so I mount it to the bus
 bar that has all of my other arrestors (coax, telco, etc.) on it to 
 provide
 a common-point ground.  The Isobar doesn't have provisions for direct
 grounding - it relies only on the equipment grounding conductor in the AC
 cord, but the TrippLite has arguably better EMI/RFI filtering than the
 Polyphaser.

 --- Jeff WN3A


 -Original Message-
 From: Repeater-Builder@yahoogroups.com
 [mailto:repeater-buil...@yahoogroups.com] On Behalf Of Chuck Kelsey
 Sent: Tuesday, June 08, 2010 4:48 PM
 To: Repeater-Builder@yahoogroups.com
 Subject: Re: [Repeater-Builder] MOVs for power supply primary



 OK, I should have been more specific. What would be a
 reasonable unit for a
 repeater site that may have only a couple thousand dollars worth of
 equipment inside?

 Chuck
 WB2EDV

 - Original Message - 
 From: Jeff DePolo j...@broadsci.com mailto:jd0%40broadsci.com 
 To: Repeater-Builder@yahoogroups.com
 mailto:Repeater-Builder%40yahoogroups.com 
 Sent: Tuesday, June 08, 2010 4:22 PM
 Subject: RE: [Repeater-Builder] MOVs for power supply primary

 
  Probably the ones I've had the most luck with are the
 Islatrol series from
  Control Concepts. I think they have been bought out by
 Emerson or Liebert
  or one of the other companies that have power divisions.
 Anyway, they
  call
  these active tracking filters. They not only are TVSS's
 but also filter
  noise, low-amplitude spikes, etc. Right now I'm typing from
 a mountaintop
  site (broadcast) that we re-built a few years ago. We put
 in an Islator
  I-2100 (120/240V single-phase). The old equipment shelter
 which had been
  here since 1990 had the same model unit. In the 15+ years we've been
  managing and maintaining the site, we've had zero
 surge-related failures,
  and this site sticks out like a sore thumb as far as
 lightning goes. In
  the
  last few years I've used the same series of arrestors for
 new site builds
  at
  a dozen sites or so and have had no power-related problems.
 
  Others that make comparable-quality products include
 Joslyn, Transtector,
  and Innovative Technologies.
 
  There is one big difference (to me anyway) between TVSS's,
 that being
  whether they are the series or parallel type. Series type takes the
  utility
  service (or transfer switch output if there's a generator
 too) as its
  input,
  and provides a protected output to feed the panel(s).
 Parallel type is
  typically connected to a breaker in the panel, which puts
 it in parallel
  with all of the loads. I much prefer series. Parallel type
 can be less
  effective because a) there will always be some inductance
 and resistance
  in
  the wiring between the panel and the protector, b) if the
 TVSS conducts,
  there's a good chance it will trip the breaker in the
 panel, resulting in
  no
  protection until the breaker is reset, and c) they are much
 less effective
  as a noise filter. The upside to parallel type is they can
 easily be
  added
  at any time just by popping breakers in the panel and feeding the
  arrestor.
  Series, on the other hand, are in-line with the service
 conductors, so if
  you want to add one (or repair one), you have to take the
 service down.
  Series tends to also be more expensive, especially for
 three-phase and
  unlike parallel type, the price goes up as the current
 rating goes up for
  obvious reasons.
 
  A good 200A single-phase arrestor of the ilk I'm talking
 about starts at
  about $1000 and goes up quite a ways from there. I think these
  single-phase
  I-2100's were in the $2000 range. I recently spec'ed a
 120/208 3-phase
  Transtector (parallel type) for another site where I'm much
 less concerned
  about power-wise, and that was about $1800. No cheap, but
 where you're
  protecting equipment in the 6 and 7 figure range, it's a
 no-brainer. If
  you're repeater is a Micor mobile and an Astron, it might be hard to
  justify... :-)
 
  --- Jeff








 



 Yahoo! Groups Links

RE: [Repeater-Builder] MOVs for power supply primary

2010-06-09 Thread Eric Lemmon
Chuck,

Square D makes a line of heavy-duty, commercial-grade surge protectors for
both 120/240 VAC residential and 208Y/120 VAC commercial systems:
http://tinyurl.com/27tnma7
These are very good products, but- like any really good stuff- are
definitely not cheap.  I guess that one's definition of cheap changes
after suffering a $5,000 loss due to a lightning strike!

73, Eric Lemmon WB6FLY
 

-Original Message-
From: Repeater-Builder@yahoogroups.com
[mailto:repeater-buil...@yahoogroups.com] On Behalf Of Chuck Kelsey
Sent: Wednesday, June 09, 2010 5:51 PM
To: Repeater-Builder@yahoogroups.com
Subject: Re: [Repeater-Builder] MOVs for power supply primary

  

OK, I'm familiar with those single-point grounding panel protection devices.

How about a service panel protector for home use?

And a service panel protector for a small (200A) 3-phase panel?

I ask, rather than simply Google for it, because Google could come up with 
some units that are not good.

Chuck
WB2EDVsnip


snip



Re: [Repeater-Builder] MOVs for power supply primary

2010-06-09 Thread Chuck Kelsey
Thanks Eric.

Chuck


- Original Message - 
From: Eric Lemmon wb6...@verizon.net
To: Repeater-Builder@yahoogroups.com
Sent: Wednesday, June 09, 2010 10:07 PM
Subject: RE: [Repeater-Builder] MOVs for power supply primary


 Chuck,

 Square D makes a line of heavy-duty, commercial-grade surge protectors for
 both 120/240 VAC residential and 208Y/120 VAC commercial systems:
 http://tinyurl.com/27tnma7
 These are very good products, but- like any really good stuff- are
 definitely not cheap.  I guess that one's definition of cheap changes
 after suffering a $5,000 loss due to a lightning strike!

 73, Eric Lemmon WB6FLY




Re: [Repeater-Builder] MOVs for power supply primary

2010-06-08 Thread AA8K73 GMail
It's an Onan 4CCK-3R/1J  1800 RPM,  10 HP,
2 cylinder, gasoline, 3.5 KW, 4 KW surge,
from 1965 with 57 hours use on it.

In the 2003 Northeast USA power blackout,
it ran two homes, including two refrigerators
and a freezer.

Perhaps not a home-size unit, but the
advantage is that is sips gasoline at a
low rate.  After three days of the 2003
power failure, we had used up the stored
gasoline and I was beginning to siphon fuel
from the vehicles, as no gas stations were
operational.  My Comcast broadband Internet
was gone after the first hour and my dialup
IP answered and connected, but nothing past
their site.  I had just removed my Direc
satellite Internet service two months before.
Since Comcast cable TV wasn't there, I connected
an outside antenna and was able to get the
Detroit TV stations 50 miles away.  It was
nice to be able to see the stars again,
without all the light pollution.


My Astron VS-50M has a 10 Ampere fuse in it,
but apparently there wasn't enough remaining
current available from the generator to open it.

I added the GE 130 Volt MOV (from Newark) to
the Astron myself.  I took my MOV out and
everything works fine.


My first impulse was that there was a problem
with the generator, until I isolated the
symptom to that Astron and I realized that
plus 10% voltage was tripping my MOV.



Ray Brown wrote:
  
 
 
 - Original Message -
 From: AA8K73 GMail aa8...@gmail.com mailto:aa8k73%40gmail.com
 
  
   I added a 130 Volt MOV across the hot and neutral
   of an Astron 50 Amp power supply for a repeater
   and had an interesting effect.
  
   We lost AC power and switched over to the generator.
   When the load was added to the generator, the Onan's
   voltage sagged a bit and the throttle opened to
   bring the speed back. It overshot slightly and was
   high enough to trip the MOV. That short slowed the
   generator down until the voltage was too low and
   then the generator sped up again. And again it fired
   the MOV and slowed down until it cleared. It kept
   oscillating with huge voltage swings until I unplugged
   the Astron power supply.
 
 That's very interesting, all right.
 
 Was this a single-cylinder 3600 RPM generator, or was it one of
 the twin-cylinder motor-home generators?
 
 I used to work for an Onan distributorship back when (70's)
 and we had a similar problem with a Southwestern Bell setup.
 They had a 2.5 LK, which was a single cylinder genset that ran
 at 1800 RPM. They switched a 500 watt load in and out several
 times a minute. When the 500 W load hit, it did the same thing
 you had described. I brought up a 1 KW load (heater elements)
 and plugged them in the circuit full-time, and it worked like a
 champ, going between about 40% and 60% of full load.
 Pretty stable. :-)
 
 Ray, KB0STN
 






Yahoo! Groups Links

* To visit your group on the web, go to:
http://groups.yahoo.com/group/Repeater-Builder/

* Your email settings:
Individual Email | Traditional

* To change settings online go to:
http://groups.yahoo.com/group/Repeater-Builder/join
(Yahoo! ID required)

* To change settings via email:
repeater-builder-dig...@yahoogroups.com 
repeater-builder-fullfeatu...@yahoogroups.com

* To unsubscribe from this group, send an email to:
repeater-builder-unsubscr...@yahoogroups.com

* Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/



Re: [Repeater-Builder] MOVs for power supply primary

2010-06-08 Thread Chuck Kelsey
Jeff -

Could you suggest some makes and models and maybe explain why they are 
superior to others?

Chuck
WB2EDV


- Original Message - 
 Good surge arrestors/TVSS's are expensive, and like most things in life, 
 you
 get what you pay for.  If your site has a good surge arrestor at the 
 service
 entrance, you really shouldn't need anything extra.

 --- Jeff WN3A



Re: [Repeater-Builder] MOVs for power supply primary

2010-06-08 Thread Chuck Kelsey
And, boy were there stars!

Chuck
WB2EDV



- Original Message -   

 It was
 nice to be able to see the stars again,
 without all the light pollution.
 
 







Yahoo! Groups Links

* To visit your group on the web, go to:
http://groups.yahoo.com/group/Repeater-Builder/

* Your email settings:
Individual Email | Traditional

* To change settings online go to:
http://groups.yahoo.com/group/Repeater-Builder/join
(Yahoo! ID required)

* To change settings via email:
repeater-builder-dig...@yahoogroups.com 
repeater-builder-fullfeatu...@yahoogroups.com

* To unsubscribe from this group, send an email to:
repeater-builder-unsubscr...@yahoogroups.com

* Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/



RE: [Repeater-Builder] MOVs for power supply primary

2010-06-08 Thread Jeff DePolo

Probably the ones I've had the most luck with are the Islatrol series from
Control Concepts.  I think they have been bought out by Emerson or Liebert
or one of the other companies that have power divisions.  Anyway, they call
these active tracking filters.  They not only are TVSS's but also filter
noise, low-amplitude spikes, etc.  Right now I'm typing from a mountaintop
site (broadcast) that we re-built a few years ago.  We put in an Islator
I-2100 (120/240V single-phase).  The old equipment shelter which had been
here since 1990 had the same model unit.  In the 15+ years we've been
managing and maintaining the site, we've had zero surge-related failures,
and this site sticks out like a sore thumb as far as lightning goes.  In the
last few years I've used the same series of arrestors for new site builds at
a dozen sites or so and have had no power-related problems. 

Others that make comparable-quality products include Joslyn, Transtector,
and Innovative Technologies.

There is one big difference (to me anyway) between TVSS's, that being
whether they are the series or parallel type.  Series type takes the utility
service (or transfer switch output if there's a generator too) as its input,
and provides a protected output to feed the panel(s).  Parallel type is
typically connected to a breaker in the panel, which puts it in parallel
with all of the loads.  I much prefer series.  Parallel type can be less
effective because a) there will always be some inductance and resistance in
the wiring between the panel and the protector, b) if the TVSS conducts,
there's a good chance it will trip the breaker in the panel, resulting in no
protection until the breaker is reset, and c) they are much less effective
as a noise filter.  The upside to parallel type is they can easily be added
at any time just by popping breakers in the panel and feeding the arrestor.
Series, on the other hand, are in-line with the service conductors, so if
you want to add one (or repair one), you have to take the service down.
Series tends to also be more expensive, especially for three-phase and
unlike parallel type, the price goes up as the current rating goes up for
obvious reasons.

A good 200A single-phase arrestor of the ilk I'm talking about starts at
about $1000 and goes up quite a ways from there.  I think these single-phase
I-2100's were in the $2000 range.  I recently spec'ed a 120/208 3-phase
Transtector (parallel type) for another site where I'm much less concerned
about power-wise, and that was about $1800.  No cheap, but where you're
protecting equipment in the 6 and 7 figure range, it's a no-brainer.  If
you're repeater is a Micor mobile and an Astron, it might be hard to
justify... :-)

--- Jeff

 -Original Message-
 From: Repeater-Builder@yahoogroups.com 
 [mailto:repeater-buil...@yahoogroups.com] On Behalf Of Chuck Kelsey
 Sent: Tuesday, June 08, 2010 11:34 AM
 To: Repeater-Builder@yahoogroups.com
 Subject: Re: [Repeater-Builder] MOVs for power supply primary
 
   
 
 Jeff -
 
 Could you suggest some makes and models and maybe explain why 
 they are 
 superior to others?
 
 Chuck
 WB2EDV
 
 - Original Message - 
  Good surge arrestors/TVSS's are expensive, and like most 
 things in life, 
  you
  get what you pay for. If your site has a good surge arrestor at the 
  service
  entrance, you really shouldn't need anything extra.
 
  --- Jeff WN3A
 
 
 
 
 



Re: [Repeater-Builder] MOVs for power supply primary

2010-06-08 Thread Chuck Kelsey
OK, I should have been more specific. What would be a reasonable unit for a 
repeater site that may have only a couple thousand dollars worth of 
equipment inside?

Chuck
WB2EDV

- Original Message - 
From: Jeff DePolo j...@broadsci.com
To: Repeater-Builder@yahoogroups.com
Sent: Tuesday, June 08, 2010 4:22 PM
Subject: RE: [Repeater-Builder] MOVs for power supply primary



 Probably the ones I've had the most luck with are the Islatrol series from
 Control Concepts.  I think they have been bought out by Emerson or Liebert
 or one of the other companies that have power divisions.  Anyway, they 
 call
 these active tracking filters.  They not only are TVSS's but also filter
 noise, low-amplitude spikes, etc.  Right now I'm typing from a mountaintop
 site (broadcast) that we re-built a few years ago.  We put in an Islator
 I-2100 (120/240V single-phase).  The old equipment shelter which had been
 here since 1990 had the same model unit.  In the 15+ years we've been
 managing and maintaining the site, we've had zero surge-related failures,
 and this site sticks out like a sore thumb as far as lightning goes.  In 
 the
 last few years I've used the same series of arrestors for new site builds 
 at
 a dozen sites or so and have had no power-related problems.

 Others that make comparable-quality products include Joslyn, Transtector,
 and Innovative Technologies.

 There is one big difference (to me anyway) between TVSS's, that being
 whether they are the series or parallel type.  Series type takes the 
 utility
 service (or transfer switch output if there's a generator too) as its 
 input,
 and provides a protected output to feed the panel(s).  Parallel type is
 typically connected to a breaker in the panel, which puts it in parallel
 with all of the loads.  I much prefer series.  Parallel type can be less
 effective because a) there will always be some inductance and resistance 
 in
 the wiring between the panel and the protector, b) if the TVSS conducts,
 there's a good chance it will trip the breaker in the panel, resulting in 
 no
 protection until the breaker is reset, and c) they are much less effective
 as a noise filter.  The upside to parallel type is they can easily be 
 added
 at any time just by popping breakers in the panel and feeding the 
 arrestor.
 Series, on the other hand, are in-line with the service conductors, so if
 you want to add one (or repair one), you have to take the service down.
 Series tends to also be more expensive, especially for three-phase and
 unlike parallel type, the price goes up as the current rating goes up for
 obvious reasons.

 A good 200A single-phase arrestor of the ilk I'm talking about starts at
 about $1000 and goes up quite a ways from there.  I think these 
 single-phase
 I-2100's were in the $2000 range.  I recently spec'ed a 120/208 3-phase
 Transtector (parallel type) for another site where I'm much less concerned
 about power-wise, and that was about $1800.  No cheap, but where you're
 protecting equipment in the 6 and 7 figure range, it's a no-brainer.  If
 you're repeater is a Micor mobile and an Astron, it might be hard to
 justify... :-)

 --- Jeff



RE: [Repeater-Builder] MOVs for power supply primary

2010-06-08 Thread Wayne Cornick
I use Tripplite Isobar Ultra. Usually ends up with the power
switch rocker blown across the room when hit hard but equipment is well
protected. 

 

Wa9ne

 

 

 

-Original Message-
From: Repeater-Builder@yahoogroups.com
[mailto:repeater-buil...@yahoogroups.com] On Behalf Of Chuck Kelsey
Sent: Tuesday, June 08, 2010 3:48 PM
To: Repeater-Builder@yahoogroups.com
Subject: Re: [Repeater-Builder] MOVs for power supply primary

 

  

OK, I should have been more specific. What would be a reasonable unit for a 
repeater site that may have only a couple thousand dollars worth of 
equipment inside?

Chuck
WB2EDV




No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 9.0.829 / Virus Database: 271.1.1/2923 - Release Date: 06/08/10
01:35:00




Re: [Repeater-Builder] MOVs for power supply primary

2010-06-07 Thread Don Kupferschmidt
Don't use Radio Shack.  You're just asking for trouble.  Buy from a quality 
supplier.  Others on the list can give you preferred vendors.

Don, KD9PT



  - Original Message - 
  From: kq7dx 
  To: Repeater-Builder@yahoogroups.com 
  Sent: Monday, June 07, 2010 7:38 PM
  Subject: [Repeater-Builder] MOVs for power supply primary



  Hello to group,
  Is putting a MOV from hot to ground, neutral to ground, on the primary of the 
transformer of the power supply a good idea..
  I have a ICE surge suppressor on in front as well but thought I would put 
more inside the supply for back up.

  Also, are the MOVs that radio shack sell any good. Rated at 130VAC. Any body 
used them...

  Last question: when MOVs fail or take a surge do they fail in a shorted 
condition taking out the fuse till the MOV can be replaced, or do they blow or 
fail open leaving the supply working. 

  Thanks for the help..
  73s



  

Re: [Repeater-Builder] MOVs for power supply primary

2010-06-07 Thread AA8K73 GMail

I added a 130 Volt MOV across the hot and neutral
of an Astron 50 Amp power supply for a repeater
and had an interesting effect.

We lost AC power and switched over to the generator.
When the load was added to the generator, the Onan's
voltage sagged a bit and the throttle opened to
bring the speed back.  It overshot slightly and was
high enough to trip the MOV.  That short slowed the
generator down until the voltage was too low and
then the generator sped up again.  And again it fired
the MOV and slowed down until it cleared.  It kept
oscillating with huge voltage swings until I unplugged
the Astron power supply.

Sigh.


kq7dx wrote:
  
 
 Hello to group,
 Is putting a MOV from hot to ground, neutral to ground, on the primary 
 of the transformer of the power supply a good idea..
 I have a ICE surge suppressor on in front as well but thought I would 
 put more inside the supply for back up.
 
 Also, are the MOVs that radio shack sell any good. Rated at 130VAC. Any 
 body used them...
 
 Last question: when MOVs fail or take a surge do they fail in a shorted 
 condition taking out the fuse till the MOV can be replaced, or do they 
 blow or fail open leaving the supply working.
 
 Thanks for the help..
 73s
 


Re: [Repeater-Builder] MOVs for power supply primary

2010-06-07 Thread Ray Brown

- Original Message - 
From: AA8K73 GMail aa8...@gmail.com


 
 I added a 130 Volt MOV across the hot and neutral
 of an Astron 50 Amp power supply for a repeater
 and had an interesting effect.
 
 We lost AC power and switched over to the generator.
 When the load was added to the generator, the Onan's
 voltage sagged a bit and the throttle opened to
 bring the speed back.  It overshot slightly and was
 high enough to trip the MOV.  That short slowed the
 generator down until the voltage was too low and
 then the generator sped up again.  And again it fired
 the MOV and slowed down until it cleared.  It kept
 oscillating with huge voltage swings until I unplugged
 the Astron power supply.

  That's very interesting, all right.

  Was this a single-cylinder 3600 RPM generator, or was it one of
the twin-cylinder motor-home generators?

  I used to work for an Onan distributorship back when (70's)
and we had a similar problem with a Southwestern Bell setup.
They had a 2.5 LK, which was a single cylinder genset that ran
at 1800 RPM. They switched a 500 watt load in and out several
times a minute. When the 500 W load hit, it did the same thing
you had described. I brought up a 1 KW load (heater elements)
and plugged them in the circuit full-time, and it worked like a 
champ, going between about 40% and 60% of full load. 
Pretty stable. :-)


Ray, KB0STN







Re: [Repeater-Builder] MOVs for power supply primary

2010-06-07 Thread kevin valentino
I agree fully with NOT using Radio Shack low quality run-off manufacturer 
seconds. Use NTE 140V. The trick is you need to use THREE. One across the hot 
and neutral. one from hot to ground and one from neutral to ground. MOV's are a 
funny dog they do not usually short but degrade very quickly depending on 
number of incoming spikes they suppress. Used them alot to supress the reverse 
EMF in electromagnetic locking devices, 8+ H, yes henrys! , not micro or milli. 
suggest replacing annually.
Kevin

--- On Mon, 6/7/10, kq7dx kq...@yahoo.com wrote:


From: kq7dx kq...@yahoo.com
Subject: [Repeater-Builder] MOVs for power supply primary
To: Repeater-Builder@yahoogroups.com
Date: Monday, June 7, 2010, 8:38 PM


  



Hello to group,
Is putting a MOV from hot to ground, neutral to ground, on the primary of the 
transformer of the power supply a good idea..
I have a ICE surge suppressor on in front as well but thought I would put more 
inside the supply for back up.

Also, are the MOVs that radio shack sell any good. Rated at 130VAC. Any body 
used them...

Last question: when MOVs fail or take a surge do they fail in a shorted 
condition taking out the fuse till the MOV can be replaced, or do they blow or 
fail open leaving the supply working. 

Thanks for the help..
73s








RE: [Repeater-Builder] MOVs for power supply primary

2010-06-07 Thread Eric Lemmon
Two things leap out at me:  Your generator has some very serious regulation
problems, and may be undersized, and your Astron power supply must not have
the correct fuse installed.  If the MOV fires, the fuse is sized to blow
instantly.  That said, Astron has been known to install MOVs that have a
wide tolerance, and those near the low end may go into avalanche mode at
only a few volts above nominal 120 VAC.  The national standard for nominal
utilization voltage is 120 +/- 5%.  That means the utility can supply
anything between 114 and 126 VAC and be within the required tolerance.  126
VAC is darned close to 130 VAC, and that MOV is already getting hot!

73, Eric Lemmon WB6FLY


-Original Message-
From: Repeater-Builder@yahoogroups.com
[mailto:repeater-buil...@yahoogroups.com] On Behalf Of AA8K73 GMail
Sent: Monday, June 07, 2010 6:47 PM
To: Repeater-Builder@yahoogroups.com
Subject: Re: [Repeater-Builder] MOVs for power supply primary

  


I added a 130 Volt MOV across the hot and neutral
of an Astron 50 Amp power supply for a repeater
and had an interesting effect.

We lost AC power and switched over to the generator.
When the load was added to the generator, the Onan's
voltage sagged a bit and the throttle opened to
bring the speed back. It overshot slightly and was
high enough to trip the MOV. That short slowed the
generator down until the voltage was too low and
then the generator sped up again. And again it fired
the MOV and slowed down until it cleared. It kept
oscillating with huge voltage swings until I unplugged
the Astron power supply.

Sigh.

kq7dx wrote:
 
 
 Hello to group,
 Is putting a MOV from hot to ground, neutral to ground, on the primary 
 of the transformer of the power supply a good idea..
 I have a ICE surge suppressor on in front as well but thought I would 
 put more inside the supply for back up.
 
 Also, are the MOVs that radio shack sell any good. Rated at 130VAC. Any 
 body used them...
 
 Last question: when MOVs fail or take a surge do they fail in a shorted 
 condition taking out the fuse till the MOV can be replaced, or do they 
 blow or fail open leaving the supply working.
 
 Thanks for the help..
 73s



Re: [Repeater-Builder] MOVs for power supply primary

2010-06-07 Thread Richard W. Solomon
Harbach sells a set of three that is for the SB-220. You might 
look at them.

73, Dick, W1KSZ


-Original Message-
From: kq7dx kq...@yahoo.com
Sent: Jun 7, 2010 8:38 PM
To: Repeater-Builder@yahoogroups.com
Subject: [Repeater-Builder] MOVs for  power supply primary

Hello to group,
Is putting a MOV from hot to ground, neutral to ground, on the primary of the 
transformer of the power supply a good idea..
I have a ICE surge suppressor on in front as well but thought I would put more 
inside the supply for back up.

Also, are the MOVs that radio shack sell any good. Rated at 130VAC. Any body 
used them...

Last question: when MOVs fail or take a surge do they fail in a shorted 
condition taking out the fuse till the MOV can be replaced, or do they blow or 
fail open leaving the supply working. 

Thanks for the help..
73s







Yahoo! Groups Links






RE: [Repeater-Builder] MOVs for power supply primary

2010-06-07 Thread k7pfj
I replaced two in two ASRON power supplies that got zapped with 220 and seem
to be still working. I would recommend getting a good brand if you have the
resource.

 

 

Mike Mullarkey K7PFJ

 

  _  

From: Repeater-Builder@yahoogroups.com
[mailto:repeater-buil...@yahoogroups.com] On Behalf Of kq7dx
Sent: Monday, June 07, 2010 6:39 PM
To: Repeater-Builder@yahoogroups.com
Subject: [Repeater-Builder] MOVs for power supply primary

 

  

Hello to group,
Is putting a MOV from hot to ground, neutral to ground, on the primary of
the transformer of the power supply a good idea..
I have a ICE surge suppressor on in front as well but thought I would put
more inside the supply for back up.

Also, are the MOVs that radio shack sell any good. Rated at 130VAC. Any body
used them...

Last question: when MOVs fail or take a surge do they fail in a shorted
condition taking out the fuse till the MOV can be replaced, or do they blow
or fail open leaving the supply working. 

Thanks for the help..
73s





RE: [Repeater-Builder] MOVs for power supply primary

2010-06-07 Thread Eric Lemmon
Regarding your last question, an MOV normally will go into avalanche mode
when the applied voltage exceeds its threshold value.  It becomes a low
shunt resistance, which should blow the input fuse in the device it is
protecting.  Once the voltage is removed and the MOV cools off, it usually
recovers.  However, usually is not always the case, so it may be prudent
to replace all three MOVs after a surge event.

As others have noted, an MOV rated at 130 VAC is suitable for a 120 VAC
appliance only if its tolerance is tight, say +/- 2%.  You won't find these
at Radio Shack.  It may be a good idea to install MOVs rated at 140 VAC with
a 10% tolerance.  Always protect the device with a fuse sized as recommended
by the manufacturer, and don't substitute a fast-blow fuse for a time-delay
fuse, or vice-versa.

73, Eric Lemmon WB6FLY
 

-Original Message-
From: Repeater-Builder@yahoogroups.com
[mailto:repeater-buil...@yahoogroups.com] On Behalf Of kq7dx
Sent: Monday, June 07, 2010 5:39 PM
To: Repeater-Builder@yahoogroups.com
Subject: [Repeater-Builder] MOVs for power supply primary

  

Hello to group,
Is putting an MOV from hot to ground, neutral to ground, on the primary of
the transformer of the power supply a good idea?
I have a ICE surge suppressor on in front as well but thought I would put
more inside the supply for back up.

Also, are the MOVs that radio shack sell any good?  Rated at 130VAC. Any
body used them?

Last question: when MOVs fail or take a surge do they fail in a shorted
condition taking out the fuse till the MOV can be replaced, or do they blow
or fail open leaving the supply working? 

Thanks for the help..
73s



RE: [Repeater-Builder] MOVs for power supply primary

2010-06-07 Thread Jeff DePolo
 Hello to group,
 Is putting a MOV from hot to ground, neutral to ground, on 
 the primary of the transformer of the power supply a good idea..
 I have a ICE surge suppressor on in front as well but thought 
 I would put more inside the supply for back up.

I'm not that big of a fan of MOV's, but if you really feel the need to add
them across the transformer primary, as long the input to the power supply
is properly fused, whatever floats your boat.
 
 Also, are the MOVs that radio shack sell any good. Rated at 
 130VAC. Any body used them...

I'm not sure that there's anything that Radio Shack sells any more that's
any good, is there?

Seriously, I'd buy 

 Last question: when MOVs fail or take a surge do they fail in 
 a shorted condition taking out the fuse till the MOV can be 
 replaced, or do they blow or fail open leaving the supply working. 

My experience that small MOV's fail in one of two ways.  Either they fail
shorted, quite often with no outward visible signs, or they fail open
catastrophically as a zillion pieces of shrapnel that can cause damage to
nearby components, wiring, people, livestock, etc..

Another downside to MOV's is that after they've successfully quenched an
over-voltage event of any significant energy, their clamping voltage
changes.  So, you may end up with less and less protection over time.

Good surge arrestors/TVSS's are expensive, and like most things in life, you
get what you pay for.  If your site has a good surge arrestor at the service
entrance, you really shouldn't need anything extra.

--- Jeff WN3A





RE: [Repeater-Builder] MOVs for power supply primary

2010-06-07 Thread kevin valentino
There is no reason to have to put them period.
Extra protection is well.. to each his own. MOV's are not the greatest, but 
certainly wont hurt
Kevin B.S.E.E.

--- On Mon, 6/7/10, Jeff DePolo j...@broadsci.com wrote:


From: Jeff DePolo j...@broadsci.com
Subject: RE: [Repeater-Builder] MOVs for power supply primary
To: Repeater-Builder@yahoogroups.com
Date: Monday, June 7, 2010, 11:54 PM


  



 Hello to group,
 Is putting a MOV from hot to ground, neutral to ground, on 
 the primary of the transformer of the power supply a good idea..
 I have a ICE surge suppressor on in front as well but thought 
 I would put more inside the supply for back up.

I'm not that big of a fan of MOV's, but if you really feel the need to add
them across the transformer primary, as long the input to the power supply
is properly fused, whatever floats your boat.

 Also, are the MOVs that radio shack sell any good. Rated at 
 130VAC. Any body used them...

I'm not sure that there's anything that Radio Shack sells any more that's
any good, is there?

Seriously, I'd buy 

 Last question: when MOVs fail or take a surge do they fail in 
 a shorted condition taking out the fuse till the MOV can be 
 replaced, or do they blow or fail open leaving the supply working. 

My experience that small MOV's fail in one of two ways. Either they fail
shorted, quite often with no outward visible signs, or they fail open
catastrophically as a zillion pieces of shrapnel that can cause damage to
nearby components, wiring, people, livestock, etc..

Another downside to MOV's is that after they've successfully quenched an
over-voltage event of any significant energy, their clamping voltage
changes. So, you may end up with less and less protection over time.

Good surge arrestors/TVSS's are expensive, and like most things in life, you
get what you pay for. If your site has a good surge arrestor at the service
entrance, you really shouldn't need anything extra.

--- Jeff WN3A