Re: [RE-wrenches] Grid-Tied Radian Force Discharge

2024-04-25 Thread Maverick Brown via RE-wrenches
DaveWhat is the size of the battery bank and what is the typical load, let’s say at night or some other peak time? Bank size, SOC and demand can influence voltage. LBCO at 47.2 could be too high under smaller bank higher load situations. Also, with the AC coupled solar in an off grid case, what is

Re: [RE-wrenches] Grid-Tied Radian Force Discharge

2024-04-25 Thread Dave Tedeyan via RE-wrenches
A minor update here. I had the grid zero DOD volts set to 48, and the low battery cut out was set to 47.2v. But the homeowner told me that their loads cut out at some point. Does anyone know whether it is possible that Outback would be using a temperature compensated voltage for one of those

Re: [RE-wrenches] XW Pro Firmware 2.04 melting devices

2024-04-25 Thread Dave Angelini Offgrid Solar via RE-wrenches
To be fare, Schneider does tell you to follow the commissioning guide. It should be in the firmware though and should be a warning. It is only an issue with older XWP BTW. Let us know what you end up doing Kevin please. Dave Angelini Offgrid Solar "we go where powerlines don't"

Re: [RE-wrenches] XW Pro Firmware 2.04 melting devices

2024-04-25 Thread Kevin Pegg via RE-wrenches
Hi Chris, Thanks. Ugh it’s even more irritating to learn this is obviously a known issue. Yes, I tested gen in bypass mode system off and it is all within spec, forgot to mention that. Kevin From: RE-wrenches On Behalf Of Chris Sparadeo via RE-wrenches Sent: April-25-24 11:30 AM To:

Re: [RE-wrenches] XW Pro Firmware 2.04 melting devices

2024-04-25 Thread Kevin Pegg via RE-wrenches
Yes, PLEASE! Provide us with off-grid firmware for XW Pros! The reason I was updating firmware was to enable AC1 gen charging, for clients with dual generators. The Insight FW 1.18 clearly said it supported that feature, but that’s not true. Schneider now tells that XW FW 2.07 will enable AC1

Re: [RE-wrenches] XW Pro Firmware 2.04 melting devices

2024-04-25 Thread Chris Sparadeo via RE-wrenches
Hi Kevin, Let me chime in here. Last year I experienced something nearly identical to what you are describing. 3 ea. XW pros in an off-grid application. Things were working fine, but wanted to upgrade firmware for a comms issue I was having with closed loop BMS and Insight. After the 2.04

Re: [RE-wrenches] XW Pro Firmware 2.04 melting devices

2024-04-25 Thread Dave Angelini Offgrid Solar via RE-wrenches
Good advice Michael! I had one that the grid code got set by FW and reverting did not help. Had to start fresh. I certainly would try the revert as it is so much easier. There just is too much grid firmware being changed and it does not need to be done offgrid. I beg people and

Re: [RE-wrenches] XW Pro Firmware 2.04 melting devices

2024-04-25 Thread Michael Morningstar via RE-wrenches
Go back to V1.11. I had the same thing happen with an XWPRO and a Central Maine Diesel with a DynaGen controller. Frequency and Peak to Peak was less than perfect and the inverter, IF it would qualify the power, sounded like a garbage disposal. Eric B at Schneider suggested reverting back to the

Re: [RE-wrenches] 120 Vac and 12Vdc mixed distribution system

2024-04-25 Thread Michael Morningstar via RE-wrenches
Ray, I'm in the same situation. My strategic plan was to work into early old age ( in 20-25 years). But now, I spend half of my time troubleshooting and replacing equipment on my dime. Between that, competing with Grid-Tied guys, and having to justify my mark-up to clients comparing my pricing to

Re: [RE-wrenches] Solar pumping stormwater

2024-04-25 Thread Windy Dankoff via RE-wrenches
Dear Mac, For a non-battery, PV-direct system, you will need to shop for an appropriate AC pump, and an AC pump controller, AKA "pump inverter". 3-phase is ideal for this because it's better for this variable-speed application. However, this power level, you probably will have to settle for

Re: [RE-wrenches] XW Pro Firmware 2.04 melting devices

2024-04-25 Thread Ray Walters via RE-wrenches
That sounds like a generator problem.  I've seen many gen sets put out a horrible waveform under load, when battery charging. The waveform, (if you have an O-scope) usually has a spike on the front of the wave, and then the wave flattens significantly after.  The peak should be 169 v on a 120

Re: [RE-wrenches] 120 Vac and 12Vdc mixed distribution system

2024-04-25 Thread Ray Walters via RE-wrenches
Hi Michael; I don't think its 12v, I have old Trace 48 v systems still humming along 24 years later, too. Some of it, is the customers. The old school off grid folks knew how to conserve energy, watch the sun, and were not going to call unless they couldn't fix it themselves. Also, the

Re: [RE-wrenches] 120 Vac and 12Vdc mixed distribution system

2024-04-25 Thread Michael Morningstar via RE-wrenches
Here's a different take. Just food for thought and not necessarily a suggestion. Those 1st or 2nd Gen 12V systems were/are for me the most reliable and trouble free systems. I'd install one and never hear back from my customer for a decade or more. I regularly see "rats nest" wired 12V/Trace DR/UX

Re: [RE-wrenches] 120 Vac and 12Vdc mixed distribution system

2024-04-25 Thread Bradley Bassett via RE-wrenches
I had a lot of trouble keeping QO breakers functional on a 12VDC distribution system. I'd have to move them around every week or so to keep a good contact on the plug in contacts. They seem to work fine on a 24VDC system. I went to using MNPV or MNDC breakers instead in PV combiner or other

[RE-wrenches] Solar pumping stormwater

2024-04-25 Thread Mac Lewis via RE-wrenches
Hello Wrenches, Im looking for recommendations on solar pumps for a stormwater overflow application. The water will be cruddy so the pump would need to be able to tolerate that, although we will do our best to mitigate that. I'd like to be able to pump about 20,000 gallons per day or so at a