2024-04-26 Thread Dave Tedeyan via RE-wrenches
Maverick and Mac I am using Flextime here so that we are only using Grid Zero mode from 2-6am, when there is no solar coming in. The rest of the time, the system is in Grid tied mode so that we can take advantage of as much solar as possible. But the battery bank is two strings of the NSB190 FT

Re: [RE-wrenches] Grid-Tied Radian Force Discharge

2024-04-26 Thread Mac Lewis via RE-wrenches
Hello Dave, Be sure you calibrate the flexnet and the inverter voltage. My gut feeling is that the Delta voltage you have is too tight. If you have the system on Optics, I'd set the LBCO pretty low, then observe how much voltage sag (or where your voltage cliff is) you are getting at the

Re: [RE-wrenches] Grid-Tied Radian Force Discharge

2024-04-25 Thread Maverick Brown via RE-wrenches
DaveWhat is the size of the battery bank and what is the typical load, let’s say at night or some other peak time? Bank size, SOC and demand can influence voltage. LBCO at 47.2 could be too high under smaller bank higher load situations. Also, with the AC coupled solar in an off grid case, what is

Re: [RE-wrenches] Grid-Tied Radian Force Discharge

2024-04-25 Thread Dave Tedeyan via RE-wrenches
A minor update here. I had the grid zero DOD volts set to 48, and the low battery cut out was set to 47.2v. But the homeowner told me that their loads cut out at some point. Does anyone know whether it is possible that Outback would be using a temperature compensated voltage for one of those

Re: [RE-wrenches] Grid-Tied Radian Force Discharge

2024-04-24 Thread Dave Tedeyan via RE-wrenches
Maverick and Steve, Thank you much for pointing me in the right direction here. I was looking at the Radian setting and not the Mate3S settings. I've decided to use the flextime schedule to have it go to grid zero mode at night when we will not be exporting any solar power anyway. It really does

Re: [RE-wrenches] Grid-Tied Radian Force Discharge

2024-04-23 Thread Steve Higgins via RE-wrenches
Yes, Grid Zero would work, but the customer wouldn't be selling power to the utility. You could program the Radan to sell more power by lowering the sell voltage. I would get aggressive with it for at least 20-30 cycles to see if you can recover some capacity. Ideally, to recover lost capacity

Re: [RE-wrenches] Grid-Tied Radian Force Discharge

2024-04-23 Thread Maverick Brown via RE-wrenches
You can do it in one of several easy ways.HPX mode on the Mate. High Battery transfer. When the battery voltage and/or SOC is above the setpoint drop the grid. When the battery voltage or state of charge goes below the setpoint pick up the grid. This case the Mate  is doing the driving. Also

[RE-wrenches] Grid-Tied Radian Force Discharge

2024-04-23 Thread Dave Tedeyan via RE-wrenches
Hi All, I have an AC coupled Radian that is used to back up certain loads when the grid is down. It is paired with the Northstar Blue (Outback) batteries. The system sits in float nearly all the time. During a recent grid outage, the batteries had less than half the capacity that I would have