Re: [RE-wrenches] Panel Fire

2009-02-11 Thread William Miller
Dear Wind-Sun: The incident described on your forum is very Interesting and scary. It is impossible to make any definitive conclusions from the vague information provided, but here are a few things that got my attention: --If I could detect, from the before photos provided, a first rate

Re: [RE-wrenches] Magnum MS4448AE Compatibility Question

2009-02-11 Thread Darryl Thayer
Some of the hot surface ignitors I have seen draw a lot of current, in the order of amps. I would expect the inverter to drop out if it were overloaded however. Also does the magnum drop voltage at very low loads? Where the furnace controls can not function due to low voltage or poor wave

Re: [RE-wrenches] anchoring racks to concrete roof

2009-02-11 Thread August Goers
Jay - If it is a flat roof it seems like a ballasted system might be the way to go. What is the beam/truss configuration? -August August Goers Luminalt Energy Corporation From: jay peltz j...@asis.com To: RE-wrenches re-wrenches@lists.re-wrenches.org

Re: [RE-wrenches] anchoring racks to concrete roof

2009-02-11 Thread Karl Schwingel
Hi Jay, not having any experience with these roofs (what a weird way to build a roof) if you're doing a flat or near flat mount, I'd look at the currrent issue of Solar professional magazine. lots on flat roof mounts. Ballasted is probably going to be your best bet. if a high tilt (hot

Re: [RE-wrenches] anchoring racks to concrete roof

2009-02-11 Thread jay peltz
Hi Guys, This mount install is not on a flat roof, well a few hundred sq feet are, but mostly on some tilt. Also they do get hurricanes there, so not sure how well the ballasted work in that high of wind. As to the construction, not of my choice anyway. I've never see in here in the US

Re: [RE-wrenches] Magnum MS4448AE Compatibility Question

2009-02-11 Thread jay peltz
I dont' know if you can power just the part this is giving problems and not the big load which is pumping? but had a similar problem with an SW trace. I installed a Exeltech inverter to power that load specifically and ever since has worked fine. The guys at Exeltech make a wave form that

Re: [RE-wrenches] anchoring racks to concrete roof

2009-02-11 Thread Jason Lombard
I will Third the motion for a ballasted system in this case. On Tue, Feb 10, 2009 at 6:35 PM, jay peltz j...@asis.com wrote: I've got a client with a foam core concrete covered roof. the concrete is 2.5 thick + over metal mesh over 6 ridged foam and then the same on the inside. What anchor

Re: [RE-wrenches] Magnum MS4448AE Compatibility Question

2009-02-11 Thread Hans Frederickson
A few years back, we had a customer who was having similar problems. I don't recall if it was a Buderus boiler, but the generator was a Generac. This was a simple generator backup system. We were able to get the boiler to work reliably after adjusting the governor on the generator so that it ran

Re: [RE-wrenches] Panel Fire

2009-02-11 Thread Bill Brooks
Wrenches, Thanks to the wind-sun folks for sharing this fire story. There is a lot of conjecture in the thread, and much of it is wrong. With all due respect to Solar-Guppy, PV module encapsulant, EVA, is highly flammable, and tedlar will burn as well. The good news is that there is not a lot

Re: [RE-wrenches] Panel Fire

2009-02-11 Thread Bill Brooks
Wrenches, After looking more closely at the pictures, it appears that they may not be glass-covered modules. Given the poor manufacturing practices, this was a fire waiting to happen the moment they turned it on. The amazing thing is that the installer is going to reinstall the module-and

Re: [RE-wrenches] Panel Fire

2009-02-11 Thread Wind-sun.com
At the very least, it shows a good reason to not use any of those off-brand (or no brand) cheap unlisted panels that have been floating around lately. .. Northern Arizona Wind Sun - Electricity From

Re: [RE-wrenches] anchoring racks to concrete roof

2009-02-11 Thread Ken Schaal
Hi Jay I have experience with similar structures. Is this a Monolithic Dome? Key Dome? In any case, with 2.5 of concrete, it almost certainly has welded wire or rebar or both embedded, so you have lots of strength. Just need to get lucky when you drill holes to miss the metal. No need to

Re: [RE-wrenches] Panel Fire

2009-02-11 Thread Travis Creswell
Yeah, spooky pictures. Certainly that was non-glass glazing. I can make out a way too unsecured wire at the top left of the array but that might have been secured before the conflagration event. Could these panels have been home made by someone in their garage? I regularly loose cells for sale

Re: [RE-wrenches] Magnum MS4448AE Compatibility Question

2009-02-11 Thread Allan Sindelar
Wrenches, Thank you to you Wrenches who have responded. Keep them coming; I'm collating all as part of our customer support on this. We have several ideas to try out. Darryl, it's not excessive draw. I had a Kill-a-Watt on the AC input during on-site testing. I saw a momentary peak of 360W (for

[RE-wrenches] inverter search

2009-02-11 Thread Marco
Any recommendations for a grid-tie battery-less inverter that can handle a DC voltage as low as 100V? thanks, marco Marco Mangelsdorf, Ph.D., President Electrical Contractor License C-26351 69 Railroad Avenue, Suite A-7 Hilo, Hawaii 96720 USA (808) 969-3281, fax 934-7462

Re: [RE-wrenches] Panel Fire

2009-02-11 Thread Allan Sindelar
One detail I haven't heard mentioned yet and am curious about - the photo of the fire damage appears to show the corner of another west(?)-facing array. I find it curious that the system owner described a 2 kW system made up of eight 250W(!) modules, which are clearly visible in the topmost system

Re: [RE-wrenches] inverter search

2009-02-11 Thread Allan Sindelar
SB700 comes close. PV Powered's 1100 comes closer, as does the Kaco 1501xi. Beyond that, Outback GTFX with batteries or Enphase. Allan -Original Message- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Marco Any

Re: [RE-wrenches] inverter search

2009-02-11 Thread Bill Brooks
Marco, Is 100V the absolute floor, or is it the normal operating voltage. I believe the Power-One inverter can go down to 90V. Bill. -Original Message- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Marco Sent: Wednesday,

Re: [RE-wrenches] Panel Fire

2009-02-11 Thread Brian Sipp
I may be very wrong here and I don’t mean to impugn anyone’s integrity, but don’t forget that in this era of digital animation movies you can’t always believe what you see in a photo either. (I'm sure no one here has ever Photoshopped a photo to make it more presentable looking.)  I couldn't

Re: [RE-wrenches] Panel Fire

2009-02-11 Thread Michael Welch
This seems corroborating. It has GOT to be the same situation: http://www.examiner.com/x-432-Wedding-and-Marriage-Examiner~y2009m2d10-Our-wedding-anniversary-like-a-house-on-fire-literally Search the page for solar to get to the crux of it, and . P.S. Tempered glass won't melt, but clear

Re: [RE-wrenches] Panel Fire

2009-02-11 Thread Ken Schaal
Amazing how this ' stuff ' just bounces around--Note the ' for more info' box at the bottom of the examiner article. It's the Fire Link.com story wrenches discussed last week--- Ken - Original Message - From: Michael Welch To: 'RE-wrenches' Sent: Wednesday, February 11,

Re: [RE-wrenches] Panel Fire

2009-02-11 Thread Christopher Freitas
Michael - it gets worse - if you look at the bottom of the website with the story about them having to leave Disneyland to run back to there house which was on fire - there are some links to related items: For more info: Screamin' is right: my favorite ride at the park Traditional

Re: [RE-wrenches] SEIA stuff

2009-02-11 Thread Peter Parrish
Please send it to me too. Muchos gracias, Peter Peter T. Parrish, President California Solar Engineering, Inc. 820 Cynthia Ave., Los Angeles, CA 90065 Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885 CA Lic. 854779, NABCEP Cert. 031806-26 peter.parr...@calsolareng.com -Original

Re: [RE-wrenches] Panel Fire

2009-02-11 Thread Wind-sun.com
You have probably never looked close at many photos. I think there is a danger of getting paranoid here and ascribing some deep conspiracy to the simple fact of some non-spec or even non-legal panels burning up. It is known as depth of field, and is familiar to anyone photographer that has

Re: [RE-wrenches] another firefighter mis-information link (was: Panel Fire)

2009-02-11 Thread Kurt Albershardt
On 2/11/09 6:48 PM, Michael Welch wrote: This seems corroborating. It has GOT to be the same situation: http://www.examiner.com/x-432-Wedding-and-Marriage-Examiner~y2009m2d10-Our-wedding-anniversary-like-a-house-on-fire-literally

Re: [RE-wrenches] Wrenches attending AEE Dealer Conference?

2009-02-11 Thread Bill Brooks
I'll be teaching Thursday afternoon and Friday morning. See you there. Bill. -Original Message- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David Palumbo Sent: Wednesday, February 11, 2009 7:51 PM To: RE-wrenches

Re: [RE-wrenches] FW: Panel Fire

2009-02-11 Thread Wind-sun.com
Re: [RE-wrenches] FW: Panel FireA new term for bargain basement modules? .. - Original Message - From: David Brearley To: al...@positiveenergysolar.com ; RE-wrenches Sent:

Re: [RE-wrenches] FW: Panel Fire

2009-02-11 Thread David Brearley
Allan, there are 4 modules pictured in the ³before² photo, not 8. The after photo show the ³good² modules, the ones that did not burn. This suggests there are 4 module each on two separate roof faces. Please have another look at the before picture and count the frames. In the before picture each