hanks,
>> Kienan
>>
>> *Green-Go Solar Wholesale Distribution LLC*
>>
>> *kienan@dist.solar*
>>
>> *(801) 631-5584(Cell)*
>>
>> *www.distribution.solar*
>>
>> On Oct 9, 2023, at 8:33 AM, Dave Tedeyan via RE-wrenches <
>> re-wren
Hi all,
I am going to try out the Nuance OSPREY PowerRack as a ground mount option
that does not require an excavator. I am wondering two things about it:
1. Does anyone have experience with this, and do you like it?
2. What drill do you use for the drive rod?
It seems like the Milwaukee 2" SDS
Mine was a roof mount. We had very few SolarWorld projects. In fact, this
might be our only one.
On Fri, Nov 10, 2023, 8:10 AM Chris Schaefer via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> I'd be curious to know of the connector failures y'all have experienced,
> were the majority
Fascinating. I emailed the list a little while back asking if anyone knew
of a way to make a warranty claim with Solarworld. We had a system with 36
of these panels, and basically every module to module connector was crispy
and deformed as Ray mentioned. I never was successful in getting in touch
Hi All,
I just got some of the Qcell 360w AC modules that have the Enphase
microinverter factory applied to the back. The module is the half cut cell
type with the DC leads coming from either side of the middle of the module.
The modules come with the wires taped to the back of the module. If you
not sag enough to touch the roof, or is the tape the only thing
> preventing the leads from touching the roof?
>
> Jason Szumlanski
> Florida Solar Design Group
>
>
>
>
> On Thu, Jun 2, 2022 at 9:37 AM Dave Tedeyan via RE-wrenches <
> re-wrenches@lists.r
tor
>
> On Thu, Jun 2, 2022 at 6:37 AM Dave Tedeyan via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> Hi All,
>>
>> I just got some of the Qcell 360w AC modules that have the Enphase
>> microinverter factory applied to the back. The module is
Hi All,
I am expanding on an existing Sunpower system, with non Sunpower equipment
(SMA inverters). In order to get their consumption monitoring to work
properly, I would like to install a production CT for the PVS5. Does anyone
know whether you can use an Enphase production CT with a Sunpower
them
> statically remain in location without the tape, the loop will prevent
> drooping and if properly located rest on the rail.
> Jerry
>
> On Wed, Jun 29, 2022 at 1:07 PM Dave Tedeyan via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> Hi all,
>
Hi all,
Does anyone have any experience with EG4 products? I am doing an off-grid
consultation for someone who plans on getting EG4 inverter and lithium
batteries. The equipment seems so cheap, yet appears to be somewhat legit.
They do at least have UL1741 listing. But their 6500w
Hi All,
The last SMA-41 inverter I commissioned, had the option for SunSpec rapid
shutdown with Secure Power Supply. I just talked to a level one tech who
was not particularly familiar, but told me that with a sunspec rapid
shutdown device like the JMS-F, you can still use the Secure Power Supply
Hi All,
I've got someone who wants to tie their off-grid system with a Magnum
inverter (which I think is a 4024 PAE inverter) to the grid. Since the
Magnum inverter cannot be grid tied, I was wondering if there is some kind
of simple grid tie inverter that can be the grid interface, while keeping
stallation Professional
> ---
>
>
>
> On 2022-10-07 11:42, Dave Tedeyan via RE-wrenches wrote:
>
> Hi All,
>
> I've got someone who wants to tie their off-grid system with a Magnum
> inverter (which I think is a 4024 PAE inverter) to the grid. Since the
> Magnum inv
Hi All,
I need to get some replacement vent fans for a Schneider CC. Tech support
gave me the replacement part number as Sunon pf80251b1--a99. Looking
around online, I cannot find anything with that exact part number, but I
have found a bunch that is off by one digit - Sunon
I have heard from my distributor that SMA is in the process of ending the
-41 line and will be coming out with a new line of inverter that is
UL1741-SB certified. I've been told SMA says Q2 next year is when the new
line will be available, but my vendor says that it always slips. This is a
bummer
Hi All,
I have a system where the solar panels (with Enphase IQ8) are on a detached
garage and the IQ gateway is in the house. The gateway is in the house so
that it can gather consumption data, and there is an internet connection
there. There are other loads in the garage, so it is impossible to
Hi Jeremy,
I've seen that whitepaper from SMA about using the USB to power a Vonets
wifi adapter. It does not work well at all. I tried this and it worked
great for about a week. Then one of the two inverters stopped being able to
power the Vonets at all, and the other Vonets device could not
Hi All,
I have a service request to replace a Locus LGate120 with a Vision CatM1
meter. I have never used the Vision meters, and have not used an LGate120
in many years. Does anyone know if this will be a 1 to 1 swap? As in, is
the meter specific to the meter enclosure, or can I just pull out the
imit it might be the feeders. It's all process of elimination.
>> Lots of fun
>>
>>
>> On Thu, Feb 23, 2023, 9:03 AM Dave Tedeyan via RE-wrenches <
>> re-wrenches@lists.re-wrenches.org> wrote:
>>
>>> Hi All,
>>>
>>> I've got a custo
e is a drop and how much. Now turn off everything and
> power up the solar again watch the voltage at the meter if it climbs up and
> close to limit it might be the feeders. It's all process of elimination.
> Lots of fun
>
>
> On Thu, Feb 23, 2023, 9:03 AM Dave Tedeyan via RE-wren
Hi All,
I've got a customer who is having issues with high voltage at their house.
This first became an issue after installing 23.1kw of AC solar output. They
have some GREE heat pumps which have been having some failures. The heat
pump people are saying that the problem is that the voltage is
Hi Matt,
I've used these in the past when on a comp roof and there was no good way
to get into the rafters (or TJI's in this case)
https://sunmodo.com/nanomount/
You might want to replace the screws with something shorter and beefier
though to get more grip if you are only going into 1/2"
perator
> www.AutonomousEnergies.com <http://www.autonomousenergies.com>
> (518) 567-1468
>
>
>
>
> On Thu, Jun 8, 2023 at 2:33 PM Dave Tedeyan via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> Also being in NYS, I have been familiar with this
Hi William,
I recently installed these connected to an FM100, and also on a couple grid
tied systems in the past year. I think that as long as you are getting the
expected 0.6V per module you know that everything is connected as it should
be. Unfortunately I do not think that you will be able to
It was a bunch of years ago, but I had seen many of these "snail trails" on
some modules. I actually took a curve tracer to them, and they functioned
essentially the same as the other modules there that did not have the snail
trails. Maybe these will be sources of premature failure in the future,
Also being in NYS, I have been familiar with this requirement for a long
time. I believe the idea is that just like how any metal part in a system
needs to be grounded, metal roof panels under solar panels are kind of part
of the system. What if a wire comes loose and touches the roof? You would
Sam,
Thanks for pointing me in that direction. It looks like you can update some
of the grid protection settings, although I am not sure if that will allow
for freq-watt control. My LG rep told me to use CA rule 21 grid profile,
but I am not sure if there is something like that on the old A series
Hi all,
Does anyone know if you can make the SolarEdge inverters (the A series,
before the HD wave inverters) respond to frequency control? I cannot find a
way to update the grid settings, and was wondering if anyone else has AC
coupled these inverters to a non-SolarEdge battery system. If not,
William,
If you swap strings, does the fault stay with the string, or with the
input? and if you do run without the string for a while can you determine
that the arc faults stop? Just figure it is worth making 100% sure the
fault is actually in the DC side of that one string you have isolated, and
If a customer wants to use some of their own parts, I'll need to add some
amount of hours for managing them and their purchase list, and make it
clear in the contract that issues arising from incomplete or incorrect
parts is on them.
Or you can do what I saw at my mechanic shop the other day:
I also have been having some issues with reported SOC through the Guardian
with Fortress. Fortress is generally responsive, although no one has
specifically addressed my concern yet. What I have seen with two recent
eFlex installations (replacing an existing battery bank on an off-grid
system) is
Kirk,
That site looks specifically for the Envy inverters. Do you know if the
Guardian site is working? My credentials will not get me in at this time.
www.app.fortresspower.io
My sites have no comms between the batteries and the inverter, since it is
an Outback system.
And yes, there is
9:07 AM Jay via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> I think that using a megger etc to test the panels and wires is what I’d
>> do before I yanked out all the
>> Wires.
>>
>> They are not that expensive anymore and maybe possi
Hi All,
I am curious to hear if anyone else has run into this:
This is the system I posted about a little while ago that had the
SolarWorld modules and all the module to module connectors were swollen and
melted. One of the inverters was giving an insulation resistance error, and
so after seeing
We also stopped using the -41's in 2023 due to the -SB requirement in NY.
We moved to Enphase for grid tied systems. I am hearing from Greentech that
the new Sunny Boy units, up to 7.7kw, should be available very soon. These
will have a secure power supply capability. But the larger KW units and
Jeremy,
It is my understanding that if the generator wakes up the grid tied
inverter and loads are more than the solar then maybe nothing bad would
happen. Although I would never do that because you don't have any control
over the loads. And if the solar production is more than the loads, then
Kirk,
I know that with the Guardian Battery monitor the app is working, but they
are doing a major overhaul on the website. My login info does not work on
the website right now, and I am told that it will not be available until
the new year. The website is:
https://app.fortresspower.io/
Cheers,
Interesting on the "mesh" wifi. That is good to know.
And yes, the site I linked is for the Guardian data. I don't know if there
is a separate site for the Envy data, but I'll find out in a couple weeks
when I install my first Envy inverter system. For what it's worth, their
tech support has been
Hi All,
I have an AC coupled Radian that is used to back up certain loads when the
grid is down. It is paired with the Northstar Blue (Outback) batteries. The
system sits in float nearly all the time. During a recent grid outage, the
batteries had less than half the capacity that I would have
t;> instead of zero AC loads.
>>>
>>> The third choice is to program something called FlexTime where you set
>>> the schedule of the AC input mode from grid tide to red zero or off grid,
>>> etc.
>>>
>>> It’s the system is on OpticsRE, you can
t;> Maverick Solar Enterprises, Inc.
>> • Solar Commander Remote Power
>> • SunFlow Systems Cathodic Protection
>> maver...@mavericksolar.com
>> 512-460-9825
>>
>>
>>
>> On Apr 25, 2024, at 5:57 PM, Dave Tedeyan via RE-wrenches <
>>
gt;> years and most of them are still viable.
>>
>> As a precaution, For AC coupling, I also install a high battery AUX port
>> controlled relay that drops the AC coupling input circuit.
>>
>> Thank you,
>>
>> Maverick
>>
>> Maverick Brown
&g
Hi All,
I have an insurance question and am very curious about how others deal with
this, or don't. People will sometimes ask us to either do some design work
for a system that we will not be installing, or to inspect a system and
give my professional opinion about it. These are two separate work
Another one out there that is worth looking at is MT Solar.
Cheers,
Dave
On Fri, Mar 8, 2024, 5:51 PM Kent via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Jeremy,
>
> I think the Solar RacksWorks TPMs are virtually identical to the DPW TPMs.
> My go to TPM is General Specialties
>
> around is a good one. NABECP I THINK, has some leads on firms for this.
>
>
> Chris
> On 3/10/2024 6:23 PM, Dave Tedeyan via RE-wrenches wrote:
>
> Hi All,
>
> I have an insurance question and am very curious about how others deal
> with this, or don't. People will so
Hi William,
Thinking out loud here, and I am guessing that there are reasons why not to
do this. But what about putting a voltage tester across each battery and
running a quick test?
I mention this because just a couple days ago, I went to check on a grid
tied battery backup system where capacity
I may be wrong, but I was under the impression that most inverter/chargers
are either being an inverter or a charger at any given time, but not both.
So, once the inverter sees the AC voltage from the generator, then it will
switch to being a charger and use the generator AC power to charge the
If anyone in the Maryland region is interested in lots of used solar panels
in the 235-300w range, send me a direct message. Sounds like they are
upgrading some older sites. Here is a message I received from an old friend:
As part of some of our upcoming portfolios there are old panels that we
This winter we were fixing up a system with a fronius primo inverter and
adding rapid shutdown. Fronius very much recommended against using Tigo.
They recommended we use Fire Raptors. They have been working fine.
Cheers,
Dave
On Thu, May 23, 2024, 8:27 PM Chris Sparadeo via RE-wrenches <
John,
Just an FYI, the new SBSE inverters are available in the up to 7.7kw
models. I believe the SPS is possible with them right now, but the more
involved backup options are not yet available.
Cheers,
Dave
On Tue, May 28, 2024 at 1:50 PM John Blittersdorf via RE-wrenches <
50 matches