[Sprinklerforum] Re: Riser in a rated stair enclosure

2024-03-26 Thread Hinson, Ryan
Placement/coordination within the stairwell is also important since the riser location cannot encroach into the minimum egress width or height required through the stairwell. Ryan L. Hinson, PE*, SET** \ Burns & McDonnell Associate Fire Protection Engineer \ Upper Midwest Region O

[Sprinklerforum] Re: Fire Pump testing procedures

2024-01-29 Thread Hinson, Ryan
If these are electric pumps, power to the pumps must be sufficient such that both can operate as anticipated. Also, NFPA 20 has required the following for fire pump field acceptance flow testing since 2010: Where simultaneous operation of multiple pumps is possible or required

[Sprinklerforum] Re: LIGHT-WALL SCH 7 NFPA

2024-01-08 Thread Hinson, Ryan
If it is listed for FP use and appropriate for the pressure classification needed for your system, then yes. See below for additional relevant NFPA 13 (2022) requirements and considerations: 7.3 Aboveground Pipe and Tube. 7.3.1 General. 7 .3.1.1 Pipe or tube shall meet or exceed one of the

[Sprinklerforum] Re: Sprinkler system area determination

2023-12-19 Thread Hinson, Ryan
Still sounds like a mezzanine to me whereas Sections 4.5.2.2 and 4.5.2.3 allow for ignoring the mezzanine area that is within the footprint of the single floor sprinkler area. I guess it would depend on what you define as 'any one floor area' per Section 4.5.1. Ryan L. Hinson, PE*, SET** \

[Sprinklerforum] Re: Air venting

2023-10-09 Thread Hinson, Ryan
Hey Ken, As has already been stated by others, I believe the intent is to remove as much air from 'each wet system' as possible. 'System', in this case, is any piping network isolated from the rest of the upstream system by isolation valving be it a check valve or a shutoff valve. Support for

[Sprinklerforum] Re: Best fire protection solution for dirty environment

2023-09-18 Thread Hinson, Ryan
FYI Here is what the annex to the section below from NFPA 13 (2022) states: A.16.2.4.2 Plastic bags should not be used for this purpose due to the fact that shrinkage prior to development of temperatures needed to ensure sprinkler activation can interfere with proper sprinkler operation and

[Sprinklerforum] Re: Control/Sectioning Valves

2023-08-16 Thread Hinson, Ryan
This is the premise of yard system reliability per NFPA 24 where isolation of one section cannot shut down more than six appurtenances/systems at a time. Ryan L. Hinson, PE*, SET** \ Burns & McDonnell Associate Fire Protection Engineer O 612-900-3755 \ M 763-688-4045 \ F 952-229-2923

[Sprinklerforum] Re: Hangers on Seismic swing joint

2023-07-19 Thread Hinson, Ryan
man Center Drive, Suite 500 \ Minneapolis-St. Paul, MN 55437 *Registered in: AK, LA, MD, MN, PA, TX, & UT **NICET IV - Water-Based Systems Layout From: Hinson, Ryan Sent: Wednesday, July 19, 2023 4:20 PM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinkl

[Sprinklerforum] Re: Hangers on Seismic swing joint

2023-07-19 Thread Hinson, Ryan
Metraflex has a listed seismic breakaway hanger for just such a use: https://www.metraflex.com/seismic-applications/ Ryan L. Hinson, PE*, SET** \ Burns & McDonnell Associate Fire Protection Engineer O 612-900-3755 \ M 763-688-4045 \ F 952-229-2923

[Sprinklerforum] Re: Elbows in pump suction

2023-07-14 Thread Hinson, Ryan
Todd, Your proposed configuration is allowed per NFPA 20 (2016) Figure A.4.15.6 bottom row. Ryan L. Hinson, PE*, SET** \ Burns & McDonnell Associate Fire Protection Engineer O 612-900-3755 \ M 763-688-4045 \ F 952-229-2923 rhin...@burnsmcd.com \

[Sprinklerforum] Re: 2nd FDC Instead of a Hydrant ???

2023-07-12 Thread Hinson, Ryan
e building FP system to use in fore hoses for outside the building. "It's cheaper than adding a hydrant" Brian Harris, CET BVS Systems Inc. bvssytemsinc.com<http://bvssystemsinc.com/> From: Hinson, Ryan mailto:rhin...@burnsmcd.com>> Sent: Wednesday, July 12, 2023 2:25

[Sprinklerforum] Re: 2nd FDC Instead of a Hydrant ???

2023-07-12 Thread Hinson, Ryan
FDC...as in injection into the system on the back side in the absence of fire hydrants nearby doesn't make sense to me. Do you mean to draw water off the FW piping in the building to serve portable equipment for the parking lot storage? Ryan L. Hinson, PE*, SET** \ Burns & McDonnell

[Sprinklerforum] Re: Storage Tank

2023-07-11 Thread Hinson, Ryan
Don't forget about backflow prevention requirements. If filling a FW tank from a potable source, put backflow prevention (1 ft air gap) above the overflow level as allowed per IPC. Whether the fill line is automatic or manual, that float- or manual fill valve must be appropriately

[Sprinklerforum] Re: 13D freeze protection for sprinkler protection of fuel fired equipment

2023-06-02 Thread Hinson, Ryan
Why not just use a dry sprinkler of proper length with boot/seal extending from a wet system in adjacent heated space per NFPA 13 (2022) Section 15.3? Ryan L. Hinson, PE*, SET** \ Burns & McDonnell Associate Fire Protection Engineer O 612-900-3755 \ M 763-688-4045 \ F 952-229-2923

[Sprinklerforum] Test

2023-04-25 Thread Hinson, Ryan
Have I been missing forum discussion? Ryan L. Hinson, PE*, SET** \ Burns & McDonnell Associate Fire Protection Engineer, Fire Protection Engineering Group O 612-900-3755 \ M 763-688-4045 \ F 952-229-2923 rhin...@burnsmcd.com \

[Sprinklerforum] Re: New foam systems

2023-02-27 Thread Hinson, Ryan
Who is requiring the foam system? What codes are adopted/enforced in the project state/municipality? What is the product/commodity you are protecting? Is this using foam-water deluge discharge via sprinklers, monitors, or a combination thereof? There are a ton of nuances out there including

[Sprinklerforum] Re: Spiral Blast Freezer

2023-02-22 Thread Hinson, Ryan
Not occupied doesn't mean not required to have sprinklers. Walk-in freezers routinely have suppression piping in them including penetration into a smaller separate enclosure inside a larger building. To get the full story, one would need to know the overarching building type, use, occupancy;

[Sprinklerforum] Re: 6" Pipe & Z-Purlins

2023-02-13 Thread Hinson, Ryan
How about a side beam bracket (listed to 8") with ½" thru-bolt, backing-nut, and washer with drilled bolt hole through the center 1/3 of the purlin spine; ½" bevel washer between the ½" ATR nut and the horizontal leg of the side beam bracket as required to counter sloped purlin deck; supporting

[Sprinklerforum] Re: Pipe Stands

2023-01-04 Thread Hinson, Ryan
you, On Tue, Jan 3, 2023 at 6:32 PM Hinson, Ryan mailto:rhin...@burnsmcd.com>> wrote: Ken, No worries, my friend. Together, we hopefully make everyone better. I need a little redirection now and then. I admittedly misread the initial email. I saw supporting the drops off the

[Sprinklerforum] Re: Pipe Stands

2023-01-03 Thread Hinson, Ryan
C59a2e8f00723473b61d208dae9ed78ad%7Cbfbb9a2b6d994e78b3c795005d555c8b%7C0%7C0%7C638079503413136871%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C=iOFTw%2BsPwk9us%2FUBz%2B3cNGRbTgjBaIK6ynwxtBLrgyY%3D=0> On 12/29/2022 3:20 PM, Hinson, Ryan wrote: Denn

[Sprinklerforum] Re: Pipe Stands

2022-12-29 Thread Hinson, Ryan
1BA0.3526E8C0] From: Hinson, Ryan Sent: Thursday, December 29, 2022 3:21 PM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: Pipe Stands Dennis, It appears that you have a 25-ft auxiliary system loop of 4" pipe from deck to grade and ba

[Sprinklerforum] Re: Pipe Stands

2022-12-29 Thread Hinson, Ryan
Dennis, It appears that you have a 25-ft auxiliary system loop of 4" pipe from deck to grade and back which must be properly supported. I think your reviewing engineer's concern may justified with how this pipe is supported as you are at the maximum 25-ft vertical distance between hangers on

[Sprinklerforum] Re: Underground FDC auto drain

2022-12-23 Thread Hinson, Ryan
Regardless of whose scope it is, an automatic drain is required per NFPA 13 (2022) Section 16.12.5 and NFPA 24 (2022) Section 5.9.4.1…unless waived by the AHJ per NFPA 24 Section 5.9.1.1. NFPA 13 Figures A.16.12.5.5(a & b) and NFPA 24 Figures A.5.9.3.2.1(a & b) specifically show the ball drip

[Sprinklerforum] Re: BFP on underground supply

2022-12-14 Thread Hinson, Ryan
NFPA 13 (2022) Section 16.4.5 with ‘enhanced content’ and some new standard language, discourages this practice. How will the requirement of Section 16.14.5.1.1 be achieved without additional calculation?: 16.14.5.1* Backflow Prevention Valves. A test connection shall be provided downstream

[Sprinklerforum] Re: Steel pipe failure rates

2022-11-23 Thread Hinson, Ryan
Was the desire for Sch. 40 known prior to bidding? If yes, then you should price accordingly and move on. If the Sch. 40 desired was known and you assumed it was incorrect and instead that you would be able to install Sch. 10, that's on you. If the Sch. 40 was not known prior to bidding,

[Sprinklerforum] Re: FDC Serving Multiple Buildings

2022-08-31 Thread Hinson, Ryan
olis-St. Paul, MN 55437 *Registered in: AK, LA, MD, MN, PA, TX, & UT **NICET IV - Water-Based Systems Layout -Original Message- From: Hinson, Ryan Sent: Wednesday, August 31, 2022 4:18 PM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum]

[Sprinklerforum] Re: FDC Serving Multiple Buildings

2022-08-31 Thread Hinson, Ryan
NFPA 24 (2022) Section 5.9.1.2 states the following: N 5.9.1.2 A single fire department connection shall be permitted to supply multiple buildings where acceptable to the AHJ. Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell Senior Fire Protection Engineer O 612-900-3755 \ M 763-688-4045 \  F

[Sprinklerforum] Re: [EXTERNAL] Hydrant flow tests

2022-08-31 Thread Hinson, Ryan
FWIW, Joe Meyer provides a nice explanation of the potential for error from flowing smaller amounts of water versus higher flows (which this discussion is about) in the following YouTube vid: https://www.youtube.com/watch?v=8YpogorxFSc We recently performed refinery-sized firewater flow

RE: Joining black carbon steel with stainless steel piping

2022-02-28 Thread Hinson, Ryan via Sprinklerforum
Craig, >From literature I have, SS has an anodic index of approximately 0.60 V while >plain CS has that of 0.85 V. If the environment in which the joint is located is 'normal' or 'controlled', you shouldn't have a galvanic compatibility issue. If the environment is considered 'harsh', the

RE: 8 inch sprinkler pipe fall from factory ceiling

2022-02-24 Thread Hinson, Ryan via Sprinklerforum
Gary, Some initial questions that come to my mind follow: 1. What was the size of the main? 2. What was the spacing of hangers? 3. Were all roll grooves of proper depth? 4. Was there any structural movement before or during this recorded event? 5. Was the hanger failure

RE: Thread connection holding on one thread only

2022-01-05 Thread Hinson, Ryan via Sprinklerforum
I seem to recall single thread calculations back in college, however, I could not find anything other than what is in ASME B.1-20-1 (2013) - Pipe threads, General Purpose. Among other things, this standard discusses 'hand-tight engagement', 'wrench makeup length', effective thread length', and

RE: Best Common Practices

2021-11-08 Thread Hinson, Ryan via Sprinklerforum
In my experience, it boils down to whether you need relatively few trapezes for your XMs and/or BRs as opposed to greater potential numbers of trapezed BLs. Certainly, each design is likely going to be unique; pipe size/schedule-dependent; and roof structure: direction-, member max-loading-,

SR EC OH fusible-link SDWL

2021-11-01 Thread Hinson, Ryan via Sprinklerforum
Happy Monday, Does a standard response, extended coverage, fusible-link, sidewall sprinkler exist which is listed for ordinary hazard occupancies? Thanks, Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell Senior Fire Protection Engineer, Fire Protection Engineering Group O 612-900-3755 \  M

RE: Mixing of K-Factors in self-storage facilities

2021-10-29 Thread Hinson, Ryan via Sprinklerforum
...and response time within the compartment is the same per NFPA 13 (2019) Section 9.4.3.3 and as otherwise stipulated in specific chapters. Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell Senior Fire Protection Engineer O 612-900-3755 \ M 763-688-4045 \  F 952-229-2923 rhin...@burnsmcd.com  \ 

RE: Seismic joint detail

2021-10-19 Thread Hinson, Ryan via Sprinklerforum
While I see allowable offsetting in all directions via rotation within those couplings necessary, it would appear that before some couplings will rotate, a moment arm must be created into which the strain can be transferred or it may manifest itself into a coupling in a prying fashion

RE: [EXTERNAL] Re: Stub-up Material

2021-08-19 Thread Hinson, Ryan via Sprinklerforum
I agree with others' assertions here that this is poor design. I have further taken NFPA 24 (2019) Section 10.1.4's specific wording to mean that this nonmetallic stub is only allowable INSIDE a building. If the manufacturer says no, so do I in this regard. I have also received photos from

RE: Dry head boot retrofit

2021-07-01 Thread Hinson, Ryan via Sprinklerforum
5437 *Registered in: AK, LA, MD, MN, PA, TX, & UT **NICET IV - Water-Based Systems Layout -Original Message- From: Hinson, Ryan Sent: Thursday, July 1, 2021 10:11 AM To: sprinklerforum@lists.firesprinkler.org; Mark Longtin Cc: Mark Phillips Subject: RE: Dry head boot retrofit I t

RE: Dry head boot retrofit

2021-07-01 Thread Hinson, Ryan via Sprinklerforum
I think you are thinking of the Tyco DSB-2 Sprinkler boot which included one boot, two strap ties, and 1/3 oz. of adhesive. This component is/was found on Tyco's Dry Sprinkler cuts...at least on the old cutsheets TFP500 and TFP550. Not sure if it is still available. Ryan L. Hinson, PE*,

Re: [EXTERNAL] Re: Available Pressure from Fire Water Storage Tank

2021-05-07 Thread Hinson, Ryan via Sprinklerforum
Don’t forget that, along with your pump(s) churn, the high water level in the tank must be used to determine maximum downstream system pressure. Sent from my iPhone > On May 7, 2021, at 4:06 PM, Mark.Phelps via Sprinklerforum > wrote: > > So, if this same tank and pump were at the same

RE: Same size orifice in a room

2021-04-19 Thread Hinson, Ryan via Sprinklerforum
Same orifice, no. Limits on orifice, yes...in several places such as NFPA 13 (2019) Sections 9.4.4, Chapter 21, Chapter 25, Section 27.2.4.9.2, or word search 'factor'. Same response time per compartment, yes per Section 9.4.3.2. Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell Senior Fire

RE: Does a remote free standing FDC require a valve pit?

2021-03-10 Thread Hinson, Ryan via Sprinklerforum
Ball drip is required at the lowpoint of the upstream piping of FDC checks per NFPA 13 (2019) Sections 16.12.1, 16.12.7, and Figure 16.12.1 (in areas subject to freezing...TX) unless an FDC is not required per Section 16.12.2. (Here it is called out as an automatic drip) It should be noted

RE: potential freezing in ESFR system

2020-12-22 Thread Hinson, Ryan via Sprinklerforum
Hopefully, your sprinklers are not already installed. Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell Senior Fire Protection Engineer O 612-900-3755 NEW \ M 763-688-4045 \  F 952-229-2923 rhin...@burnsmcd.com  \  burnsmcd.com 8201 Norman Center Drive, Suite 500  \  Minneapolis-St. Paul, MN

Lonergan Fire Pump Pressure Relief Valve

2020-11-17 Thread Hinson, Ryan via Sprinklerforum
Does anyone out there have a cutsheet for the J.E. Lonergan Model HU FM Approved Fire Pump Relief Valve from circa 1970? I have one needing reorientation due to revising relief piping and am looking for allowable installation orientation. Not finding anything online. Ryan L. Hinson, PE*,

RE: Domestic Demands 13R

2020-11-12 Thread Hinson, Ryan via Sprinklerforum
ok.com/?url=http%3A%2F%2Ffergu > soncommunications.us.newsweaver.com%2Fhq7bgesq7f%2Fn1gewi5ud95byeftyuo > y12%2Fexternal%3Femail%3Dtrue%26a%3D6%26p%3D2591775%26t%3D517003** > ;data=04%7C01%7Crhinson%40burnsmcd.com%7C9c91628183a8418eca7e08d8872f1 > f06%7Cbfbb9a2b6d994e78b3c795005d555c8b%7C0%7C1

RE: Domestic Demands 13R

2020-11-12 Thread Hinson, Ryan via Sprinklerforum
Is this entire complex brand new or existing? Your answer will determine mine: 1. Taking a water flow test on an existing looped water main supplying both FW and domestic demands already accounts for the domestic demands of the other buildings, no? On the single main feeding all the way

RE: Obstruction Clarification

2020-11-11 Thread Hinson, Ryan via Sprinklerforum
Since you are using EC heads, presumably you are protecting LH or OH areas wherein, if you were using standard uprights or pendents in the space, you could ignore minimum spacing from nonstructural members per Section 10.2.7.2.1.4. Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell Senior Fire

RE: [EXTERNAL] Re: Submittal Packages

2020-10-08 Thread Hinson, Ryan via Sprinklerforum
It's very difficult to efficiently review a project when submittals come in piecemeal. Inevitably, things get missed and resubmittals of such partial submittals only complicate matters. Though there are always exceptions, we require complete (re)submittals with shop drawings complying with

Code requiring inclusion of possible concurrent flow

2020-09-10 Thread Hinson, Ryan via Sprinklerforum
We have run into a dock FW system design where multiple automatic flushing valves are being provided on the system to prevent freezing by automatically flowing water at temps below 40°F to the order of 300 gpm. Though this flow should absolutely be included in the system demand flow, I am

RE: Ethanol unloading exposure protection

2020-09-02 Thread Hinson, Ryan via Sprinklerforum
Your scenario, which sounds like exposure protection, is likely not going to be achieved using closed sprinklers and should instead be using deluge. Why not provide a fixed water spray exposure system using open spray nozzles in accordance with NFPA 15, FM 4-1N,...or API RP 2030 Sections 7.2.2

RE: C-Clamp Hangers

2020-08-26 Thread Hinson, Ryan via Sprinklerforum
Hanger attachments are being confused with bracing attachments. - NFPA 13 (2019) Section 18.5.11.10 explicitly DOES NOT allow C-clamps used for seismic bracing structural attachments with orwithout restraining straps unless specifically listed for such use. - Section 18.7.1

Re: [EXTERNAL] RE: Floor area less than required

2020-06-17 Thread Hinson, Ryan via Sprinklerforum
I would caution throwing all us engineers into the same stereotypical group...kind of like saying all Americans are racist. Sent from my iPhone On Jun 17, 2020, at 8:35 AM, Dennis Wilson via Sprinklerforum wrote:  Don’t you just love them engineers!!! From: Sprinklerforum On Behalf Of

Re: Flammable liquid tanks in a garage

2020-02-26 Thread Hinson, Ryan via Sprinklerforum
Is NFPA 37 applicable? Sent from my iPhone On Feb 26, 2020, at 5:24 AM, Fpdcdesign via Sprinklerforum wrote:  Could you give a few more details? What is in the tanks? Why are they there? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (ofc) 860-554-7054

NFPA 14 Air supervision requirement

2020-01-24 Thread Hinson, Ryan via Sprinklerforum
Got a question with the 'apparently' all-encompassing dry standpipe air supervision requirement of NFPA 14 Section 6.1.1?: * 2013: [cid:image009.png@01D5D2C2.A4A39510] * 2016: [cid:image008.png@01D5D2C2.2A144EC0] * 2019: [cid:image010.png@01D5D2C3.2F6A77E0] Since it's illogical

RE: Looking for a 6" hanger for sloped roof

2020-01-02 Thread Hinson, Ryan via Sprinklerforum
Assuming you have done your homework regarding whether and at what hanger spacing the structure can support the weight of the water-filled pipe in accordance with NFPA 13; in my experience, one still cannot hang from the bottom lip of exposed Z-purlins and must instead hang with something like

RE: Table 22.4.2.1 NFPA 30

2019-12-20 Thread Hinson, Ryan via Sprinklerforum
Tim, Keep in mind the fact that each pair of tanks is independently evaluated for spacing purposes per the note at the bottom of NFPA 30 (2015) Table 22.4.2.1 as further explained in Section A.22.4.2.1 and that there are exceptions in the subsequent subsections. There are other documents out

RE: [EXTERNAL] Trying to determine hydrant locations per IFC, wondering how sprinkler coverage omissions will affect distances.

2019-10-24 Thread Hinson, Ryan via Sprinklerforum
James, From IBC 2018 commentary: Section 202 DEFINITIONS [F] AUTOMATIC SPRINKLER SYSTEM. An automatic sprinkler system, for fire protection purposes, is an integrated system of underground and overhead piping designed in accordance with fire protection engineering standards. The system

RE: [EXTERNAL] FW: Dry Pipe Valve to Wet

2019-09-24 Thread Hinson, Ryan via Sprinklerforum
IFC 2012 Section 901.4.5 Ryan L. Hinson, PE*, SET** \ Burns & McDonnell Senior Fire Protection Engineer O 952-656-3662 \ M 320-250-5404 \ F 952-229-2923 rhin...@burnsmcd.com \ burnsmcd.com 8201 Norman Center Drive, Suite 300 \

RE: 30' diameter and 30' high storage tank

2019-08-09 Thread Hinson, Ryan via Sprinklerforum
Tim, All manufacturers' cutsheets I've used walk you through how to determine this. In addition to the axial distance, the spray profile for your proposed nozzle needs to be known (typically shown on the cutsheets), as well as the nozzle's fixed angle of orientation. Dependent upon these

RE: 30' diameter and 30' high storage tank

2019-08-08 Thread Hinson, Ryan via Sprinklerforum
Keep in mind that 12 ft is the maximum distance measured along the surface of the protected asset per NFPA 15. "Net rate" in NFPA 15 (2017) Section 7.4.2.1 means that one has to include necessary flow to achieve an overall average of 0.25 gpm/sq ft of all exposed vessel surface. If your

RE: Determining seismic design category.

2018-12-03 Thread Hinson, Ryan
Ss is only one of several factors necessary to determine seismic requirements. Both IBC (2015) Sections 202 and 1613.1 and NFPA 13 (2016) Sections 3.11.1, and 9.3.5.9.4 refer to ASCE-7. ASCE-7 (2016) Chapters 11 and 13 provide this determination as I’ve learned from my friend Ken Wagoner. To

UL listed/FM approved MOV

2018-09-27 Thread Hinson, Ryan
Forum, Is there a UL listed/FM approved valve assembly having motor-operation? I have looked many times and am unaware of any. Projects touting such components always turn out to be using process controls-MOV equipment which is not listed for fire protection such as Emerson's M2CP. Have I

RE: buried fdc ball drip?

2018-09-20 Thread Hinson, Ryan
For remote FDC’s NFPA 24 (2013) Section 5.9.4.2 requires the automatic drip to be located in a location that permits inspection and testing as required by NFPA 25. In industrial applications, ball drips not used on FDC’s are routinely used to drain daylighted FW piping that extends above grade

RE: Reaming of pipe

2018-08-10 Thread Hinson, Ryan
r.com<mailto:m...@knssprinkler.com> From: Sprinklerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org>> On Behalf Of Hinson, Ryan Sent: Thursday, August 9, 2018 8:46 PM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Cc: Schoenecker,

Reaming of pipe

2018-08-09 Thread Hinson, Ryan
What is the forum consensus on why threaded sprinkler piping is reamed. I always did it as a fitter. We have always required it in our specifications. I have never really thought about the ‘why’ though. Is it as simple as removing the burr created when the pipe is cut and any potential

RE: HDPE's PE 4710 resin for FP use

2018-04-26 Thread Hinson, Ryan
.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Subject: RE: HDPE's PE 4710 resin for FP use Have you been running into AHJ/contractor push-back on specifying PE4710? Matt From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists

HDPE's PE 4710 resin for FP use

2018-04-26 Thread Hinson, Ryan
UG FW forumites, Not sure if any of you are aware of this but NFPA 24 (2016) edition requires HDPE piping materials to be selected from AWWA C906 per Table 10.1.1. NFPA 24 Section 2.3.3 specifically references the 2007 edition of AWWA C906. In AWAA C906 (2007), PE 4710 is not available. The

RE: Playpipe Pitot Pressures - Fire Pump Annual Tests

2018-03-29 Thread Hinson, Ryan
I’ve never seen them all identical. Ryan L. Hinson, PE*, SET** \ Burns & McDonnell Senior Fire Protection Engineer O 952-656-3662 \ M 320-250-5404 \ F 952-229-2923 rhin...@burnsmcd.com \ burnsmcd.com 8201 Norman Center Drive, Suite 300 \ Bloomington, MN 55437

RE: Case 00201286: Differing k-factors [ ref:_00D5077Vx._5005013w8og:ref ]

2018-03-28 Thread Hinson, Ryan
Travis, I think your situation may fall under NFPA 13 (2016) Section 23.4.4.9.3: 23.4.4.9.3 Sprinklers with different K-factors shall be acceptable for special use such as exposure protection, small rooms or enclosures, or directional discharge. (See 3.3.22 for definition of small rooms.)

RE: fixed site industrial hose monitor

2018-03-01 Thread Hinson, Ryan
Right-o on what's being protected. Is NFPA 400 applicable in this jurisdiction? If so, fertilizer (ammonium nitrate per Section 11.1.2 of the 2013 edition) and the protection thereof are required in accordance with Section 6.2.1.1 as required by Section 11.2.6. Section 6.2.1.1 requires all

RE: Schedule 10 vs Schedule 40 pipe

2017-10-03 Thread Hinson, Ryan
I would say to use nitrogen in lieu of shop air and then use schedule 10 for sizes larger than 2". Ryan L. Hinson, PE*, SET** \ Burns & McDonnell Senior Fire Protection Engineer O 952-656-3662 \ M 320-250-5404 \ F 952-229-2923 rhin...@burnsmcd.com \ burnsmcd.com

RE: Pipe life predictability

2017-08-04 Thread Hinson, Ryan
ECS (Engineered Corrosion Solutions) at www.ECSCorrosion.com is good as well. Ryan L. Hinson, PE*, SET** \ Burns & McDonnell Senior Fire Protection Engineer O 952-656-3662 \ M 320-250-5404 \ F 952-229-2923 rhin...@burnsmcd.com \

RE: Bluebeam Revu 2017 eXtreme fire sprinkler symbols

2017-08-03 Thread Hinson, Ryan
everyone for your input. -Kyle M From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Hinson, Ryan Sent: Tuesday, August 01, 2017 2:19 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Longitudinal Bracing Question Ken, I will respectfully disagree with you on t

RE: Longitudinal Bracing Question

2017-08-01 Thread Hinson, Ryan
Ken, I will respectfully disagree with you on this point in that I believe the ‘straight line to avoid eccentric loading on fittings and fasteners’ of Section 9.3.5.11.5 is in fact a line running through the center of the braced pipe’s long axis and acting in a coaxial line along the long axis

RE: CPVC Piping

2017-06-09 Thread Hinson, Ryan
..@lists.firesprinkler.org] On Behalf Of Hinson, Ryan Sent: Friday, June 9, 2017 1:43 PM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Subject: RE: CPVC Piping What is your expected temperature delta? Since CPVC is installed in heated spaces, is th

RE: CPVC Piping

2017-06-09 Thread Hinson, Ryan
What is your expected temperature delta? Since CPVC is installed in heated spaces, is there going to be that significant of a change in temperature? Where is the water supply coming from? In a conditioned space, CPVC piping system with no flow is going to have negligible thermal expansion

RE: Fire Pump Test Header Valve Location

2017-05-09 Thread Hinson, Ryan
Reed, Rhetorically, what is the definition of ‘close’ in this instance? I think you are fine to put that valve where appropriate in the configuration anywhere between the tee of the suction piping to within 4 ft along the pipe measured upstream of the exterior wall in an accessible location

RE: In Building Riser -- Restraints

2017-04-27 Thread Hinson, Ryan
I also would be interested in the their response. NFPA 24’s joint restraint section (10.8.3 – ’10 & ’13 and 10.6.2 – ’16) is quite clear in that “restrained joint systems shall include one or more of the following”: (1) Locking mechanical or push-on joints (2) Mechanical joints utilizing

RE: Sketching software

2017-04-10 Thread Hinson, Ryan
Bluebeam Ryan L. Hinson, PE*, SET** \ Burns & McDonnell Senior Fire Protection Engineer O 952-656-3662 \ M 320-250-5404 \ F 952-229-2923 rhin...@burnsmcd.com \ burnsmcd.com 8201 Norman Center Drive, Suite 300 \ Bloomington, MN 55437 *Registered in: MN, PA, & TX

RE: Fire dept. connection

2017-03-29 Thread Hinson, Ryan
The inquiry was about FDC orientation, not location. Cutsheets will usually provide allowed orientations of various components. In this case, it would likely be tied to how the clappers in your specific siamese operate and if they are spring-loaded or not such that the clappers are maintained

RE: Floating Dock

2017-02-16 Thread Hinson, Ryan
HDPE is only listed for underground suppression piping application. Are you suspending HDPE in air below docks? What about: - Poisson’s ratio of exposed plastic piping being significant due to temperature deltas in ambient air as well as pressure/expansion relationships between

RE: Foam - FDC

2017-02-09 Thread Hinson, Ryan
Add a separate, dedicated, AND CLEARLY LABELED foam FDC feeding ONLY the helipad appurtenances. Ryan L. Hinson, PE*, SET** \ Burns & McDonnell Senior Fire Protection Engineer O 952-656-3662 \ M 320-250-5404 \ F 952-229-2923 rhin...@burnsmcd.com \ burnsmcd.com

RE: Ammunition Manufacturer

2017-01-20 Thread Hinson, Ryan
How much DOT Class Division 1.1 (primer) and 1.3 (gunpowder)explosives will be located inside the building at any one time...and where? What blast resistance requirements are required between said explosives and the rest of the building? Where are explosives stored? Have venting

RE: Uprights on 3" pipe

2017-01-13 Thread Hinson, Ryan
You did not say you could not raise the 3” pipe. Couldn’t you raise it and put pendants in? Since the piping is obviously exposed, is there any reason you can’t comply with deflector-to-deck distances if you do that? If the pendants extending below the piping is a height or

RE: sealing sprinkler head penetrations

2016-12-14 Thread Hinson, Ryan
This ‘seal’ you speak of would not actually seal anything IMO as many inner escutcheons have a hole through them as well as the bent teeth for a friction fit for the outer escutcheon around it creating multiple ‘non-sealed’ voids. Can you use the rubber boot for the backside of dry pendants to

RE: Seismic Requirements for Risk Category IV (Essential Facility)

2016-12-07 Thread Hinson, Ryan
Risk Category determination out of ASCE-07 (2010) Table 1.5-1 drives the Seismic Design Category (SDC) based on Ss and S1 to a more severe designation in Tables 11.6-1 and 11.6-2. As Craig said, SDC should be provided for sprinkler contractors where this 'severity' has already been determined

RE: Bracing on vertical sprinkler drops - 15 ft long

2016-11-14 Thread Hinson, Ryan
16: 9.2.1.3.3 for suspended ceilings and flex hose fittings, 16: 9.3.2.4(3) IF seismic bracing was required, otherwise,…not required IMO. Ryan L. Hinson, PE*, SET** \ Burns & McDonnell Senior Fire Protection Engineer O 952-656-3662 \ M 320-250-5404 \ F 952-229-2923 rhin...@burnsmcd.com \

RE: Visual Inspection of CPVC System

2016-07-13 Thread Hinson, Ryan
Did you provide new heads then? Ryan L. Hinson, PE*, SET** \ Burns & McDonnell Senior Fire Protection Engineer O 952-656-3662 \ M 320-250-5404 \ F 952-229-2923 rhin...@burnsmcd.com \ burnsmcd.com 8201 Norman Center Drive, Suite 300 \ Bloomington, MN 55437

RE: Fire Flow

2016-05-19 Thread Hinson, Ryan
- Original message ---- From: "Hinson, Ryan" <rhin...@burnsmcd.com<mailto:rhin...@burnsmcd.com>> Date: 5/19/16 7:30 AM (GMT-08:00) To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Subject: RE: Fire Flow Your building spri

RE: Fire Flow

2016-05-19 Thread Hinson, Ryan
Your building sprinkler feed is just that...a sprinkler feed which should be hydraulically calculated if minimum sizing is desired. Otherwise, A fire flow does not ONLY come through this line, it cumulative in the vicinity. Fire flows are for overall requirements of all adjacent hydrants off

RE: temperature monitoring system

2016-03-21 Thread Hinson, Ryan
Bruce, I believe Tim is referring to a reference in UFC 4-211-01 that has been out for some time in draft form which states, "Where wet pipe systems are installed in areas with a 99.6% dry bulb temperature less than 30°F (-1.0°C) per UFC 3-400-02 Engineering Weather Data, temperature

RE: Piping of radiator discharge line

2016-03-04 Thread Hinson, Ryan
Presuming you are talking about fire pump cooling operation, is this really a radiator-cooled pump or is it a heat exchanger cooled pump? Heat exchangers use the pumping medium to cool the pump and this piping cannot stagnate or cooling system will not function. Piping back to the main header

RE: Army Corp of Engineer Safety

2016-02-10 Thread Hinson, Ryan
How each piece of said pipe loaded into the lift cradle from grade? Do have a dedicated Lull rental to load each piece? Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell Senior Fire Protection Engineer O 952-656-3662 \  M 320-250-5404  \  F 952-229-2923 rhin...@burnsmcd.com  \  burnsmcd.com 8201

Dots and bars

2015-11-13 Thread Hinson, Ryan
Is there a reason the bars along new standard text and dots next to sections that have been removed...have been omitted from NFPA 13 (2016) and other standards...NFPA 11(2016), etc.? I for one found these to be helpful in the past when multiple editions needed to be researched to determine

RE: Dots and bars

2015-11-13 Thread Hinson, Ryan
d Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/> > On Nov 13, 2015, at 12:52 PM, Hinson, Ryan <rhin...@burnsmcd.com> wrote: > > Is there a

RE: AWWA classifications

2015-10-14 Thread Hinson, Ryan
C900-07 is a revision of C900-97; the last two numbers being the year of effective date and is for 4" through 12" only. Included is the following from C900-97 Section IV. Major Revisions: 1. The factor of safety was revised from 2.5 to 2.0. 2. The built-in surge allowance was

RE: PVC (C900) for spigot through floor

2015-10-02 Thread Hinson, Ryan
I'll play devil's advocate: It may be allowed up to 24" as indicated in NFPA 13 (2013) Section 6.3.1.1.1* which states " Underground pipe shall be permitted to extend into the building through the slab or wall not more than 24 in. (0.6 m)." The annex for this section states "Extending the

RE: Column Protection

2015-07-06 Thread Hinson, Ryan
In this case, for column protection, we want full 'obstruction'. NFPA 13 (2013) Sections 12.12.2.2.4.1(5), 16.1.4.1(2), 17.1.4.1(2), and 18.2.1(1) all give very nearly identical prescriptions of how to protect these structural components in that they are 'pointed toward one side' of the

RE: Using Rod as brace material

2015-01-27 Thread Hinson, Ryan
As a sometimes acting AHJ I generally do not allow rod to be used in compression. ATR should not be axially loaded in compression since this can introduce the tendency to bend thus creating a lateral load which is not allowed as described in the Annex of NFPA 13 (2013) in Section A.9.1.2.3(1).

RE: Frozen open PIV

2014-11-25 Thread Hinson, Ryan
This may be more of an issue with the Indicator post not being calibrated to indicate that the valve below is open when it is in fact partially or nearly fully closed. Ran into this before. PIV installation must indicate valve to be fully open when fully open. Ryan L. Hinson, PE*, SET Fire

RE: Protecting a fire water tank

2014-11-20 Thread Hinson, Ryan
IFC Section 312 Vehicle Impact Protection Ryan L. Hinson, PE*, SET Fire Protection Engineering Group Burns McDonnell Direct: 952-656-3662 Mobile: 320-250-5404 *Registered in: MN -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of