As has been said by others.  This is not an FDC and would result in monitoring 
issues within the building.  What they are looking for is a wall hydrant which 
needs to be connected to the lead-in upstream of any building suppression 
systems.

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
Associate Fire Protection Engineer
O 612-900-3755 \  M 763-688-4045 \  F 952-229-2923
rhin...@burnsmcd.com<mailto:rhin...@burnsmcd.com>  \  
burnsmcd.com<http://www.burnsmcd.com/>
8201 Norman Center Drive, Suite 500  \  Minneapolis-St. Paul, MN 55437
*Registered in: AK, LA, MD, MN, PA, TX, & UT
**NICET IV - Water-Based Systems Layout

From: Brian Harris <bhar...@bvssystemsinc.com>
Sent: Wednesday, July 12, 2023 1:29 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Re: 2nd FDC Instead of a Hydrant ???

Ryan-
Yes. They want to draw water from inside the building FP system to use in fore 
hoses for outside the building. "It's cheaper than adding a hydrant...."

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>


From: Hinson, Ryan <rhin...@burnsmcd.com<mailto:rhin...@burnsmcd.com>>
Sent: Wednesday, July 12, 2023 2:25 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: 2nd FDC Instead of a Hydrant ???

FDC...as in injection into the system on the back side in the absence of fire 
hydrants nearby doesn't make sense to me.  Do you mean to draw water off the FW 
piping in the building to serve portable equipment for the parking lot storage?

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
Associate Fire Protection Engineer
O 612-900-3755 \  M 763-688-4045 \  F 952-229-2923
rhin...@burnsmcd.com<mailto:rhin...@burnsmcd.com>  \  
burnsmcd.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.burnsmcd.com%2f&c=E,1,7VFuIwuxPjOttrVgynPolVOTgN3v6mT-V6g87jq-Q2EvwrY7AAFdS1ToF0kt5EBG9OYlkVkYa2frZoY5Yh2qLTkFn5Iw7WH7j4mnGlxT9GuOLxsUbhhdyw,,&typo=1>
8201 Norman Center Drive, Suite 500  \  Minneapolis-St. Paul, MN 55437
*Registered in: AK, LA, MD, MN, PA, TX, & UT
**NICET IV - Water-Based Systems Layout

From: matthew.will...@ferguson.com<mailto:matthew.will...@ferguson.com> 
<matthew.will...@ferguson.com<mailto:matthew.will...@ferguson.com>>
Sent: Wednesday, July 12, 2023 1:22 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Re: 2nd FDC Instead of a Hydrant ???

Nope. Exterior fire operations are as or more important than internal.

Seen this many times for different applications.

R/
Matt

Please rate our customer 
service<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fsurvey.medallia.com%2f%3femailsignature%26fc%3d3539%26bg%3dFire%2520and%2520Fabrication&c=E,1,srwSq8YdVmazH4zsAgasid0nRVIUZrVEzSqa9212B7ULLYAOtDti9oRFL0FjT0h5WKOorJZ6qJIa5p6Gp_6TcG1lKeSP72YRuaYIZwVkZ_cXaQPdrmPfCLoFFjZa&typo=1>

Matthew J. Willis, CWBSP, CET
Engineering Designer IV
FERGUSON FIRE DESIGN, LLC
A Wholly Owned Subsidiary of Ferguson Fire & Fabrication, LLC
401 N 5th Street
Suite 448
Wausau, WI 54403
C: 307-236-8249
matthew.will...@ferguson.com<mailto:matthew.will...@ferguson.com>
www.FergusonFire.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.fergusonfire.com%2f&c=E,1,t2kkU6GiN48ipjo2cUguayf2olg-9ggZNBHGg4GIUPquGYTwa57Bsl6HIod0TTUnlD6KAmZOf15WFvAedioRCYUOHkT_leEbTXykFA5lKZCQPB2yTNYoJIyI&typo=1>

From: Brian Harris <bhar...@bvssystemsinc.com<mailto:bhar...@bvssystemsinc.com>>
Sent: Wednesday, July 12, 2023 2:19 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] 2nd FDC Instead of a Hydrant ???

This is a first. We recently did a sprinkler system for a 2-story storage 
building. The owner is now putting storage containers in the back parking lot 
and the AHJ wants him to add a 2nd FDC on the back of the building, there's 
already one on the front, and use it to "supply" fire hoses if there's a fire 
outside since there's not a hydrant in the back.... Tell me I'm crazy.

Brian Harris, CET
BVS Systems Inc.
bvssystemsinc.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f&c=E,1,KvUcJKwR1-VMeJ08pas56fB1FbmRf44mocNWawMpPEDp7swm7LB7aN-PQwe7ORb0mBUyEoXrzXuPAFliI6m20_hR6VaomNnzFc--WU3fuFARFdI,&typo=1>
Phone: 704.896.9989
Fax: 704.896.1935


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to