https://codes.iccsafe.org/content/IFC2018/CHAPTER-56-EXPLOSIVES-AND-FIREWORKS?site_type=public

On Sat, Apr 6, 2024 at 1:20 PM Prahl, Craig <craig.pr...@jacobs.com> wrote:

> Munitions and explosives are typically protected via separation.  On
> military projects, storage areas such as these are either semi-subterranean
> (partially earthen covered bunker), or just physically separated from other
> structures by several hundred feet.
>
>
>
> I do hope the components are adequately separated.
>
>
>
> Fire is usually not an issue in these spaces since there should be very
> stringent controls on ignition sources.  So, we don’t waste money on
> sprinklers or other types of suppression systems.  They just aren’t going
> to stop an explosion event.  Once it’s done, it’s done.
>
>
>
> You can take a look at UFC 4-420-01, May 2015 for the way munitions and
> explosive storage is handled by the military.  UFC = Unified Facilities
> Criteria.  You can search for it on-line.  There are no restrictions for
> access.
>
>
>
> You’d also have to  deal with sprinkler run-off and being underground,
> that might be a big challenge.
>
>
>
> So, basically, this isn’t a sprinkler contractor project.
>
>
>
> Craig Prahl | Jacobs | Fire Protection SME – Special Hazards |
> craig.pr...@jacobs.com | www.jacobs.com
> <https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
>
> 1041 East Butler Road   Greenville, South Carolina  29606
>
> CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS
>
>
>
>
>
> *From:* Chris Dorn <chris.d...@dornfireprotection.com>
> *Sent:* Friday, April 5, 2024 4:05 PM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* [EXTERNAL] [Sprinklerforum] Protecting underground storage of
> explosives.
>
>
>
> Trying to help a friend of a friend. Has anyone ever provided any type of
> fire suppression system for underground storage of ANFO (Ammoniun Nitrate
> and fuel oil mixture)? The area in question is in a limestone mine
> underground. The space is pretty large and has 30’ ceilings so I’m guessing
> that chemical suppression is not going to be an option. I tend to believe
> that sprinklers may not be the route to go. Water will apparently render
> the ANFO inert but in case of a fire I’m not sure that the sprinklers could
> operate fast enough to provide any real protection. Additionally, the water
> supply is inadequate for almost any type of sprinkler system anyway.
>
>
>
> I’m not really finding much in NFPA except Annex C in NFPA 495 which
> refers to separation distances. I did find a reference to NFPA 490 2002
> Edition but cannot find a current code so I’m guessing it was folded into
> 495 at some point.
>
>
>
> Any direction at all would be appreciated to help me in my research.
>
>
>
> Chris Dorn
>
> Dorn Fire Protection LLC
>
>
>
> ------------------------------
>
> NOTICE - This communication may contain confidential and privileged
> information that is for the sole use of the intended recipient. Any
> viewing, copying or distribution of, or reliance on this message by
> unintended recipients is strictly prohibited. If you have received this
> message in error, please notify us immediately by replying to the message
> and deleting it from your computer.
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> sprinklerforum-le...@lists.firesprinkler.org
>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to