Thank you Mark and Chuck for the math. The scary part is I am actually 
understanding it. Before the solar site we did I was lost on this stuff.

 

 

From: AF [mailto:[email protected]] On Behalf Of Mark Radabaugh
Sent: Tuesday, June 19, 2018 12:31 PM
To: [email protected]
Subject: Re: [AFMUG] Battery Charging

 

Two more important items to keep in mind 

 

That 68amp of power for recharge  + load = (68A * 56V) = 3800W / .85 
(efficiency) = ~4500W of power.

 

Your 120V supply needs to be able to put out  ~37A or ~18A at 240VAC.    It’s 
easy to miss that when installing the system since the current draw with new 
charged batteries is going to be about 5A at 120V.   Hook it up to a 15A 
circuit and everything seems fine until the power comes back on after an 
extended outage and the circuit breaker trips 2 minutes later.  Now you are 
really screwed - the batteries are about dead and you have to scramble to get 
out there and figure out how to get the system to restart (hint - disconnect 
the batteries…)

 

Good rectifier shelves have a input current limit setting in addition to the 
battery current limit setting.   Both are important.

 

Another item - that rectifier shelf putting out 68A, if it’s 85% efficient (a 
reasonable number) is going to be dumping over 600W of heat into the cabinet.  
Make sure your cooling system can take the heat load without baking equipment 
to death.

 

Mark

 

 

 

On Jun 19, 2018, at 1:11 PM, [email protected] wrote:

 

OK, finally got that IEEE whitepaper to load.  Nothing really new to me but 
they did point out a few things I had not thought of for a long time.  The main 
points to consider are as follows:

 

You need to have a rectifier/charger large enough to carry the load plus 
produce no more than 20% of the battery capacity charge current.  For example, 
if you have a 100 Ah battery, you do not want to charge it more than 20 amps.  
It is recommended that 10% or less be used to preserve battery life.  

 

Too high of a charge current will shorten the battery life in a variety of 
ways.  Sealed VLRA batts are much more susceptible due to a reduced amount of 
liquid electrolyte to serve as a heat sink.  They also outgas thus losing 
electrolyte and capacity during deep discharge.  Furthermore they have a chance 
of thermal runaway during heavy discharge or charge.  Flooded cells do not have 
this same problem.  

 

So, say you have a 48 volt system, your load current is 10 amps.  You want it 
to remain alive for 48 hours during a power outage.  You need 24*4*10 = 480 Ah 
of battery.  Pretty large battery.  $3500 or so.

 

Now, after an outage you need to charge that battery and run your load.  So, 
10% of 480Ah is 48 amps of charging current plus 10 amps for your load.  58 
amps of charger/rectifier.  

 

But wait, you really need to do N+1 for redundancy so two 60 amp rectifiers 
would be needed.  However then you have way too much recharge capacity after 
outages that could damage your batts.

 

So, you need to have rectifiers that will limit the current.  The ones I use 
allow you to set the whole shelf to limit the current.  If you are paralleling 
units that do not talk to each other, set each one for load plus 5% of the 
battery.  

 

So in the above example, current limit the rectifiers to 34 amps each.  If one 
rectifier dies, the other can still pull the 10 amp load plus have 25 amps for 
recharge.  That will bring the batts back to fully charged in about 19 hours.  

 

However if both are working, and there is an outage, when the power comes back 
on there will be 68 amps of total current available.  Take off 10 amps for the 
load and you have 58 amps going into the batts.

 

58/480=12%  You are golden.  No battery damage.  N+1 operation.  All is well.  
And you will recharge in about 10 hours.  

-- 