The battery charging current on the AD-155C is actually limited to 0.2A...
which is kind of a good thing, in that you won't have the situation Mark
mentioned where the system won't start because the batteries are drawing
too much current, but it is going to take a few weeks to completely
recharge a 100ah battery.

On Tue, Jun 19, 2018 at 1:29 PM, <ch...@wbmfg.com> wrote:

> Well, if the battery voltage eventually comes up to float voltage then you
> have enough current.
> There is a tiny amount of current needed to maintain the charge.
>
> *From:* Adam Moffett
> *Sent:* Tuesday, June 19, 2018 12:23 PM
> *To:* ch...@wbmfg.com
> *Subject:* Re: [AFMUG] Battery Charging
>
> Sorry, that was not supposed to be offlist.  Not used to the reply-all
> thing yet.
> -Adam
>
> On 6/19/2018 1:56 PM, Adam Moffett wrote:
>
> Something I've wondered about is whether there's a *minimum *charge
> current.  If you have something like a Meanwell AD-155C then you have a
> whopping 155Watts to work with.  If you have 100W of load then you have
> 1amp of charge current.  Then somebody maybe adds a couple of devices and
> now you have 125W of load and maybe 1/2 amp of charge current.
>
> I won't be concerned if the problem is that it took a month to fully
> charge, but is there a point where the charger is too weak and doesn't do
> anything?
>
> I'm also not currently using a charger that small on such a large battery,
> but in the past when I was doing everything on the cheap I've definitely
> put a Meanwell AD-155C on a 100ah 48v battery to power a few Canopy units.
> It worked fine, but I always wondered if I was hurting something by having
> such a small charger.
>
> I'll definitely keep that 10-20% range in mind for the future, and thanks
> for sharing.
>
> Thanks,
> Adam
>
>
> On 6/19/2018 1:11 PM, ch...@wbmfg.com wrote:
>
> OK, finally got that IEEE whitepaper to load.  Nothing really new to me
> but they did point out a few things I had not thought of for a long time.
> The main points to consider are as follows:
>
> You need to have a rectifier/charger large enough to carry the load plus
> produce no more than 20% of the battery capacity charge current.  For
> example, if you have a 100 Ah battery, you do not want to charge it more
> than 20 amps.  It is recommended that 10% or less be used to preserve
> battery life.
>
> Too high of a charge current will shorten the battery life in a variety of
> ways.  Sealed VLRA batts are much more susceptible due to a reduced amount
> of liquid electrolyte to serve as a heat sink.  They also outgas thus
> losing electrolyte and capacity during deep discharge.  Furthermore they
> have a chance of thermal runaway during heavy discharge or charge.  Flooded
> cells do not have this same problem.
>
> So, say you have a 48 volt system, your load current is 10 amps.  You want
> it to remain alive for 48 hours during a power outage.  You need 24*4*10 =
> 480 Ah of battery.  Pretty large battery.  $3500 or so.
>
> Now, after an outage you need to charge that battery and run your load.
> So, 10% of 480Ah is 48 amps of charging current plus 10 amps for your
> load.  58 amps of charger/rectifier.
>
> But wait, you really need to do N+1 for redundancy so two 60 amp
> rectifiers would be needed.  However then you have way too much recharge
> capacity after outages that could damage your batts.
>
> So, you need to have rectifiers that will limit the current.  The ones I
> use allow you to set the whole shelf to limit the current.  If you are
> paralleling units that do not talk to each other, set each one for load
> plus 5% of the battery.
>
> So in the above example, current limit the rectifiers to 34 amps each.  If
> one rectifier dies, the other can still pull the 10 amp load plus have 25
> amps for recharge.  That will bring the batts back to fully charged in
> about 19 hours.
>
> However if both are working, and there is an outage, when the power comes
> back on there will be 68 amps of total current available.  Take off 10 amps
> for the load and you have 58 amps going into the batts.
>
> 58/480=12%  You are golden.  No battery damage.  N+1 operation.  All is
> well.  And you will recharge in about 10 hours.
>
>
>
>
>
> --
> AF mailing list
> AF@af.afmug.com
> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
>
>
-- 
AF mailing list
AF@af.afmug.com
http://af.afmug.com/mailman/listinfo/af_af.afmug.com