On 5/27/25 12:34, Adam Moffett wrote:
Does anyone here monitor air conditioners?  If so, how do you do it?

Up until now, I would find out about an A/C failure by getting temperature alarms from equipment.  When I look at the chart of temperature over time it usually looks the A/C fail happened hours (sometimes many hours) before the temperature got critical.  It'd be nice to respond sooner.


One simple thing to start with is take two temperature sensors and place one in the air stream before the coil and one after the coil. If the air temperature drop is less than 20 degrees F while it's running in cooling mode, you are going to have a problem soon.

Getting a little fancier: tap all of the thermostat wires and contactors so you can read all of the control wiring states. i.e. if the tstat is calling for cooling but the compressor contactor is still de-energezed, you have a problem.

Adding a differential pressure switch across the blower can detect blower motor failures and/or weak airflow depending how sensitive it is.

~Seth

--
AF mailing list
[email protected]
http://af.afmug.com/mailman/listinfo/af_af.afmug.com

Reply via email to