So, you are hanging a receptacle on a tower.  30 amp  10 gauge.  
You want a 4 gauge ground?  I understanding bonding the tower to a common bond 
point with a large gauge wire.  But the three wires run in some liquidtite or 
conduit can be smaller.  How about only hot and neutral inside EMT.  If the 
only goal is to get a safe receptacle at the top of the tower I would thing 
that would suffice as long as the tower itself is bonded properly.  No?

From: Mike Hammett 
Sent: Wednesday, April 15, 2015 2:03 PM
To: [email protected] 
Subject: Re: [AFMUG] Electrical - Grounding question - long run

Amperage is irrelevant, well, unless it's larger than the gauge I recommended. 
It's not an inside-home outlet, but bonding the ground between the electrical 
service and the equipment\tower. You don't want your tower ground to be better 
than your electrical service ground and have a surge decide the best path is 
through the electric (+ or neutral) and thus your equipment.




-----
Mike Hammett
Intelligent Computing Solutions
http://www.ics-il.com





--------------------------------------------------------------------------------

From: "Chuck McCown" <[email protected]>
To: [email protected]
Sent: Wednesday, April 15, 2015 3:01:06 PM
Subject: Re: [AFMUG] Electrical - Grounding question - long run


For a 30 amp circuit?

From: Mike Hammett 
Sent: Wednesday, April 15, 2015 1:58 PM
To: [email protected] 
Subject: Re: [AFMUG] Electrical - Grounding question - long run

Your ground should be at least 4 gauge, maybe even larger than that. One of the 
0/x gauges is in my mind for some reason. That should bond the electrical 
ground with all tower and equipment grounds.




-----
Mike Hammett
Intelligent Computing Solutions
http://www.ics-il.com





--------------------------------------------------------------------------------

From: "Paul McCall" <[email protected]>
To: [email protected]
Sent: Wednesday, April 15, 2015 2:41:15 PM
Subject: [AFMUG] Electrical - Grounding question - long run


In my continued disposition of acknowledging that I am not a electrical 
grounding expert, I lay out this scenario for review, a new tower we just built.



We installed a new tower, approximately 200ft. from the service panel that 
feeds it.  We will be on our own breaker (kinda irrelevant here).



In the past, we had run 10 gauge wire (x3) out to the tower with 110vac.  
Voltage drop is relatively negligible, certainly within the bounds of working 
properly to drive our 24v charger for the battery array.



I was told, by a grounding “expert” that all my equipment electrical grounds 
need to homerun to a bus bar that ride the ground back to the service panel 
directly, that nothing else is acceptable.



AND, and this is the big part…  that I needed to seriously upgrade the 200ft. 
ground wire only that rides back to the panel to something significantly 
bigger.  How much bigger I am not sure.



So, I figured I would ask the crowd for an answer J



Thanks!







Paul McCall, Pres.

PDMNet / Florida Broadband 

658 Old Dixie Highway

Vero Beach, FL 32962

772-564-6800 office

772-473-0352 cell

www.pdmnet.com