We recently had a site where an electrician installed a panel and his own
ground (rod) for the electrical/AC ground.  We then installed our equipment
at the bottom of the tower and bonded everything in the cabinet to the
tower ground.  This site took a pretty bad strike and it was my
understanding that this may have happened because the surge traveled
through our equipment and out of the AC/electrical ground since it was the
path of least resistance.

I am admittedly stupid when it comes to grounding, so, was this actually
the proper way to ground this site?

Josh

On Wed, Apr 15, 2015 at 9:44 PM, Mark Radabaugh <[email protected]> wrote:

> For electrical service purposes the ground wire you have is fine.  The
> tower itself obviously needs to be well grounded.
>
> Where is your equipment?  I'm assuming it's at the tower since you talk
> about driving the battery charger.  All of the equipment at the tower needs
> to be bonded together with the tower ground and the electrical ground.
>
> A good 120V surge suppressor at the tower, grounded to the tower ground,
> will help avoid damage from coming in over the power lines.
>
> You are not trying to protect equipment back at the breaker panel.   The
> ground wire size back to the panel is pretty irrelevant as long as it can
> carry enough current to trip the breaker in a short circuit condition.
> Other than that it doesn't serve much purpose.
>
>
> Mark
>
> On Apr 15, 2015, at 3:41 PM, Paul McCall <[email protected]> wrote:
>
>  In my continued disposition of acknowledging that I am not a electrical
> grounding expert, I lay out this scenario for review, a new tower we just
> built.
>
>
>
> We installed a new tower, approximately 200ft. from the service panel that
> feeds it.  We will be on our own breaker (kinda irrelevant here).
>
>
>
> In the past, we had run 10 gauge wire (x3) out to the tower with 110vac.
> Voltage drop is relatively negligible, certainly within the bounds of
> working properly to drive our 24v charger for the battery array.
>
>
>
> I was told, by a grounding “expert” that all my equipment electrical
> grounds need to homerun to a bus bar that ride the ground back to the
> service panel directly, that nothing else is acceptable.
>
>
>
> AND, and this is the big part…  that I needed to seriously upgrade the
> 200ft. ground wire only that rides back to the panel to something
> significantly bigger.  How much bigger I am not sure.
>
>
>
> So, I figured I would ask the crowd for an answer J
>
>
>
> Thanks!
>
>
>
>
>
>
>
> Paul McCall, Pres.
>
> PDMNet / Florida Broadband
>
> 658 Old Dixie Highway
>
> Vero Beach, FL 32962
>
> 772-564-6800 office
>
> 772-473-0352 cell
>
> www.pdmnet.com
>
> [email protected]
>
>
>
>