Tower ground wasn't sufficient? 

Also, fiber would help keep the surge out of your data path, if only the 
equipment vendors supported it. 




----- 
Mike Hammett 
Intelligent Computing Solutions 
http://www.ics-il.com 



----- Original Message -----

From: "Paul McCall" <[email protected]> 
To: [email protected] 
Sent: Thursday, April 16, 2015 7:26:29 AM 
Subject: Re: [AFMUG] Electrical - Grounding question - long run 



That’s a great answer in theory, but both buildings that we had to be 
disconnected from were thoroughly checked out by a reputable and thorough 
electrician. 

If the tower gets physically hit, the concept is… why induce that surge into 
your electrical ground as well for it to have to deal with? 






From: Af [mailto:[email protected]] On Behalf Of Mike Hammett 
Sent: Thursday, April 16, 2015 8:09 AM 
To: [email protected] 
Subject: Re: [AFMUG] Electrical - Grounding question - long run 


If your grounding is failing, it is because some piece somewhere isn't big 
enough or connected properly. 



----- 
Mike Hammett 
Intelligent Computing Solutions 
http://www.ics-il.com 




----- Original Message -----


From: "Paul McCall" < [email protected] > 
To: [email protected] 
Sent: Thursday, April 16, 2015 6:49:24 AM 
Subject: Re: [AFMUG] Electrical - Grounding question - long run 
Mark, 

Proposing to bond electrical ground with tower ground at the tower is the 
opposite of what they are saying to do. I know, I know … we have done that 
pretty regularly in the past. We had a coupe towers that got total equipment 
losses a several different times… sometimes multiple times in one lightning 
season. All the potentials were within a couple ohms of each other … 
everywhere. We double, triple checked everything. Still got pounded. 

At the expert’s sugg4estion of not bonding everything together at those 2 
towers, we separated the grounds, and guess what… no more damages (almost 2 
years now) And I understand the concept, but the grey area for me is… What 
about shielded Ethernet cables going up the tower… I mean your APs are grounded 
(450s, ePMPs, sectors to the tower, yet they would plug into your electronics 
at the bottom of the tower…seemingly linking the two systems together 
regardless of intent. 

I have lots of thoughts on that.. from shield kits on each Cat5 wire …to 
isolating antennas with rubber from the tower…. Which we have tried too, LOL. 

It all starts to get a bit cloudy in understanding… over the years we have had 
both paid and unpaid “experts” say…absolutely THIS is the way to do it, yet the 
next guy contradicts the former guy more frequently than makes me feel 
comfortable. 

Forrest, I hadn’t thought about backing the breaker size down to 15A…. that 
makes sense. I will definitely try that & the bigger ground cable to see if 
that helps at this site. 




From: Af [ mailto:[email protected] ] On Behalf Of Mark Radabaugh 
Sent: Wednesday, April 15, 2015 9:44 PM 
To: [email protected] 
Subject: Re: [AFMUG] Electrical - Grounding question - long run 


For electrical service purposes the ground wire you have is fine. The tower 
itself obviously needs to be well grounded. 



Where is your equipment? I'm assuming it's at the tower since you talk about 
driving the battery charger. All of the equipment at the tower needs to be 
bonded together with the tower ground and the electrical ground. 



A good 120V surge suppressor at the tower, grounded to the tower ground, will 
help avoid damage from coming in over the power lines. 



You are not trying to protect equipment back at the breaker panel. The ground 
wire size back to the panel is pretty irrelevant as long as it can carry enough 
current to trip the breaker in a short circuit condition. Other than that it 
doesn't serve much purpose. 





Mark 


On Apr 15, 2015, at 3:41 PM, Paul McCall < [email protected] > wrote: 



In my continued disposition of acknowledging that I am not a electrical 
grounding expert, I lay out this scenario for review, a new tower we just 
built. 

We installed a new tower, approximately 200ft. from the service panel that 
feeds it. We will be on our own breaker (kinda irrelevant here). 

In the past, we had run 10 gauge wire (x3) out to the tower with 110vac. 
Voltage drop is relatively negligible, certainly within the bounds of working 
properly to drive our 24v charger for the battery array. 

I was told, by a grounding “expert” that all my equipment electrical grounds 
need to homerun to a bus bar that ride the ground back to the service panel 
directly, that nothing else is acceptable. 

AND, and this is the big part… that I needed to seriously upgrade the 200ft. 
ground wire only that rides back to the panel to something significantly 
bigger. How much bigger I am not sure. 

So, I figured I would ask the crowd for an answer J 

Thanks! 



Paul McCall, Pres. 
PDMNet / Florida Broadband 
658 Old Dixie Highway 
Vero Beach, FL 32962 
772-564-6800 office 
772-473-0352 cell 
www.pdmnet.com 
[email protected] 




Reply via email to