I saw an ad recently from someone offering a redundant input DC power device 
using MOSFETs rather than diodes for almost zero voltage drop.  I think it was 
ICT.

http://www.ict-power.com/products/display_isolationmodule.php?id=1408


From: Chuck McCown 
Sent: Friday, April 24, 2015 10:48 AM
To: af@afmug.com 
Subject: Re: [AFMUG] Power supply back feed loss?

Generally.  Some  power supplies will slowly drain your battery when off.  Most 
don’t.  You  would want to verify with an ammeter. 

From: TJ Trout 
Sent: Friday, April 24, 2015 9:46 AM
To: af@afmug.com 
Subject: Re: [AFMUG] Power supply back feed loss?

Sorry this was completely wisp unrelated, I only plan on connecting the 
batteries once and awhile and don't need them to be floated, etc. 

So I'm guessing it's safe to parallel a power supply and a battery when the 
power supply is turned off?

On Fri, Apr 24, 2015 at 6:20 AM, Mark Radabaugh <m...@amplex.net> wrote:

  On the subject Lewis brings up...

  There are a variety of battery charging schemes:

  Single Stage, Two Stage, and Three Stage.

  The very short version of this:

  Single Stage - usually a float charger, low amperage, fixed voltage.  Not 
intended to supply current to a load.  Very slow to recharge batteries.  When 
used to power a load as well as charge batteries will usually leave batteries 
undercharged.  May also cause poor equipment operation when AC is restored 
after an extended outage as the DC voltage will rise slowly - this can cause 
unpredictable operation of attached network equipment.

  Two Stage - High(er) voltage and current to charge battery, float voltage 
after fully charging battery.  Usually dangerous to your batteries when also 
powering a load - the charger can't tell the difference between the current 
going into the batteries versus into the load.  The charger always thinks the 
batteries are still bulk charging and leaves the voltage too high and will cook 
the batteries.

  Three Stage - Similar to two stage but also includes a boost voltage above 
the bulk charge to equalize the voltage in all of the batteries.   Can also 
cook batteries when trying to supply load current.

  Best version - a 3 stage charger with separate current sensing for the load 
and battery current, along with temperature monitoring of the batteries.   This 
allows the charger to know how much current the batteries are consuming so that 
it can determine charge state accurately.  Temperature compensation is to 
adjust the float voltage for temperature.

  Mark 


  On 4/24/15 9:06 AM, Lewis Bergman wrote:

    And as a side note, you should be worried about the opposite issue. Every 
supply is built to handle a load all the time. You need a supply that is 
designed to both handle a load and float batteries. A standard PS has a good 
chance of cooking your batteries if you constant load is much lower than your 
PS rating.

    On Fri, Apr 24, 2015 at 7:46 AM, Mark Radabaugh <m...@amplex.net> wrote:

      DC power supplies rarely care if there is another source of voltage that 
the power supply sees on it's input.    It is not unusual for a AC/DC supply to 
have to power up into an existing potential.   Many DC loads, on a brief power 
interruption, still have significant voltage that the power supply is going to 
see when AC returns.

      * This comment is general and may not apply to every power supply *

      From experience the only supply I know that won't deal with power on the 
output is one of the larger MeanWell AC/DC 48V supplies. The internal voltage 
regulator is too slow to respond and ramps the voltage up over the high voltage 
limit and shuts the power supply down if it's powered up when there is already 
a battery voltage on the output.   If you power up the supply and then add the 
battery it's fine - but not very practical.

      Every other AC/DC supply I have tried has worked fine doing what you are 
asking to do.

      Mark 


      On 4/24/15 1:34 AM, TJ Trout wrote:


        I have a dc load that I need to power using a switching ac to dc power 
supply but I also occasionally need to power the load from batteries, I was 
planning to put the load, power supply and battery clamps in parallel, is that 
a acceptable solution ? Can I power the load from battery and back feed DC into 
the supply without damaging it? Would there be a significant drain back into 
the supply?

        If this isn't ok, what's better solution? Diode ? SPDT switch ?

        The load is 50V 100A so that makes diodes and switches a challenge to 
find. ..







Reply via email to