I have anywhere from 2 to 8 x 100Ah AGM batteries at a bunch of sites.  That’s 
a lot of money.  They are not throwaways.  It does help somewhat that more 
expensive batteries tend to survive more discharge cycles.

But it seems to me from graphs that once you get down to 11 volts, it declines 
pretty rapidly from there.  I could be wrong, but I don’t think you’re getting 
that much extra runtime continuing to drain the batteries below let’s say 10.5 
volts.

I try to have at least 8 hours of runtime, some sites that are hard to get to 
in winter more like 2-4 days of runtime.  The idea is to bring out a portable 
generator before the batteries are dead.  If you have mountaintop sites, maybe 
that’s different.

Smaller sites we often see zero customers registered while running on batteries 
because none of them have power or generators.  It might make sense to have 
remote per-radio power control, to shut off the APs but keep the backhauls 
running for downstream towers.  But if they are licensed backhauls, they may 
consume most of the power anyway.


From: That One Guy /sarcasm 
Sent: Wednesday, December 02, 2015 1:56 PM
To: [email protected] 
Subject: Re: [AFMUG] Calculating battery bank size

so how dead does it make the battery for fully discharge, the rhetoric, is run 
em down, throw them away, is there a rule of thumb for damage?

On Wed, Dec 2, 2015 at 12:49 PM, Bill Prince <[email protected]> wrote:

  He didn't indicate how the 400 ah were configured. Is it one 12V 400 ah 
battery, or one 24v 400 ah battery, etc. But as you noted, once you convert the 
battery voltage and amp-hours to watts, it eliminates any confusion.

  If I had 4800 watt-hours of battery (assuming 12V X 4 at 100 amp-hours), I 
would estimate 9 hours of run time until the batteries are dead as a doornail. 
If you want to use them again (and most people do), then cut that time in half.

  On the other hand, if you have a 48 volt battery with a 400 amp-hour rating, 
then you actually have 19,200 watt-hours of capacity, and you could multiply 
the above by 4.

  If you configure the four 12V/100 ah batteries in series, then you don't have 
400 ah, you have 48V/100 ah. The watt-hours are the same.


bp
<part15sbs{at}gmail{dot}com>

On 12/2/2015 10:23 AM, Mathew Howard wrote:

    watt-hours stay the same - 200x24 and 100x48 both equal 4800 watt hours. In 
other words, unless you have some horribly inefficient voltage converters in 
the mix, it makes little difference.


    On Wed, Dec 2, 2015 at 12:05 PM, Bill Prince <[email protected]> wrote:

      wrong.

bp
<part15sbs{at}gmail{dot}com>

On 12/2/2015 10:04 AM, Josh Luthman wrote:

        If you do 4x 12v 100ah batteries and do 24v it's twice the time as 48v

        Josh Luthman
        Office: 937-552-2340
        Direct: 937-552-2343
        1100 Wayne St
        Suite 1337
        Troy, OH 45373

        On Dec 2, 2015 1:01 PM, "Bill Prince" <[email protected]> wrote:

          What voltage?

          bp
          <part15sbs{at}gmail{dot}com>

          On 12/2/2015 10:00 AM, TJ Trout wrote:


            How long will 500w load last on 400ah?













-- 

If you only see yourself as part of the team but you don't see your team as 
part of yourself you have already failed as part of the team.

Reply via email to