The ePMP sync APs die right at 20 volts FYI.

In my case I use the regulator as a LVD - it will continue doing 24v until
something like 19 or 20v from the batteries.  I'd rather lose some
batteries than have the site go down.


Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373

On Wed, Dec 2, 2015 at 3:53 PM, Mathew Howard <[email protected]> wrote:

> I don't see that there's really a lot of value in running batteries below
> 10.5 volts or so, at that point the voltage is going to be low enough that
> a lot of radios aren't going to run anyway (for example, ePMPs will die
> just a little under 22v), which means your going to just be wearing out the
> batteries for nothing.
>
> One time I had a Mikrotik router lock up after a power outage -
> apparently, when the voltage dropped to low (and all the radios had long
> since died), the Mikrotik locked up, but it never actually got low enough
> for it to completely shut down, so when the power came back on, it stayed
> in it's locked up state until I went out there and unplugged it. it
> would've saved me a trip out there if there had been an LVD on the
> batteries.
>
> On Wed, Dec 2, 2015 at 2:12 PM, Ken Hohhof <[email protected]> wrote:
>
>> I have anywhere from 2 to 8 x 100Ah AGM batteries at a bunch of sites.
>> That’s a lot of money.  They are not throwaways.  It does help somewhat
>> that more expensive batteries tend to survive more discharge cycles.
>>
>> But it seems to me from graphs that once you get down to 11 volts, it
>> declines pretty rapidly from there.  I could be wrong, but I don’t think
>> you’re getting that much extra runtime continuing to drain the batteries
>> below let’s say 10.5 volts.
>>
>> I try to have at least 8 hours of runtime, some sites that are hard to
>> get to in winter more like 2-4 days of runtime.  The idea is to bring out a
>> portable generator before the batteries are dead.  If you have mountaintop
>> sites, maybe that’s different.
>>
>> Smaller sites we often see zero customers registered while running on
>> batteries because none of them have power or generators.  It might make
>> sense to have remote per-radio power control, to shut off the APs but keep
>> the backhauls running for downstream towers.  But if they are licensed
>> backhauls, they may consume most of the power anyway.
>>
>>
>> *From:* That One Guy /sarcasm <[email protected]>
>> *Sent:* Wednesday, December 02, 2015 1:56 PM
>> *To:* [email protected]
>> *Subject:* Re: [AFMUG] Calculating battery bank size
>>
>> so how dead does it make the battery for fully discharge, the rhetoric,
>> is run em down, throw them away, is there a rule of thumb for damage?
>>
>> On Wed, Dec 2, 2015 at 12:49 PM, Bill Prince <[email protected]> wrote:
>>
>>> He didn't indicate how the 400 ah were configured. Is it one 12V 400 ah
>>> battery, or one 24v 400 ah battery, etc. But as you noted, once you convert
>>> the battery voltage and amp-hours to watts, it eliminates any confusion.
>>>
>>> If I had 4800 watt-hours of battery (assuming 12V X 4 at 100 amp-hours),
>>> I would estimate 9 hours of run time until the batteries are dead as a
>>> doornail. If you want to use them again (and most people do), then cut that
>>> time in half.
>>>
>>> On the other hand, if you have a 48 volt battery with a 400 amp-hour
>>> rating, then you actually have 19,200 watt-hours of capacity, and you could
>>> multiply the above by 4.
>>>
>>> If you configure the four 12V/100 ah batteries in series, then you don't
>>> have 400 ah, you have 48V/100 ah. The watt-hours are the same.
>>>
>>> bp
>>> <part15sbs{at}gmail{dot}com>
>>>
>>>
>>> On 12/2/2015 10:23 AM, Mathew Howard wrote:
>>>
>>> watt-hours stay the same - 200x24 and 100x48 both equal 4800 watt hours.
>>> In other words, unless you have some horribly inefficient voltage
>>> converters in the mix, it makes little difference.
>>>
>>> On Wed, Dec 2, 2015 at 12:05 PM, Bill Prince <[email protected]>
>>> wrote:
>>>
>>>> wrong.
>>>>
>>>> bp
>>>> <part15sbs{at}gmail{dot}com>
>>>>
>>>>
>>>> On 12/2/2015 10:04 AM, Josh Luthman wrote:
>>>>
>>>> If you do 4x 12v 100ah batteries and do 24v it's twice the time as 48v
>>>>
>>>> Josh Luthman
>>>> Office: 937-552-2340
>>>> Direct: 937-552-2343
>>>> 1100 Wayne St
>>>> Suite 1337
>>>> Troy, OH 45373
>>>> On Dec 2, 2015 1:01 PM, "Bill Prince" <[email protected]> wrote:
>>>>
>>>>> What voltage?
>>>>>
>>>>> bp
>>>>> <part15sbs{at}gmail{dot}com>
>>>>>
>>>>> On 12/2/2015 10:00 AM, TJ Trout wrote:
>>>>>
>>>>>>
>>>>>> How long will 500w load last on 400ah?
>>>>>>
>>>>>>
>>>>>
>>>>
>>>
>>>
>>>
>>
>>
>> --
>> If you only see yourself as part of the team but you don't see your team
>> as part of yourself you have already failed as part of the team.
>>
>
>

Reply via email to