Isn't the 200SS about 10 years old.

I'd replace it with something newer



On Friday, February 19, 2016, Adam Moffett <[email protected]> wrote:

> I would have assumed they weren't supposed to short the + and - wires when
> clamped.  That would be the opposite of protection lol. I also don't get
> why the short to stay there with the power shut off.  I spent a good 15-20
> minutes checking things with the power shut off, and the short didn't go
> away until I disconnected and reconnected wires on the SS.  I would have
> guessed the clamping would stop when the over current or over voltage
> condition went away.
>
> I did eventually find literature saying that the 200SS can take up to
> 6.5amps.  This BS uses 90 watts on bootup, and maybe 60 watts in normal
> operation.  The spec sheet says 125 Watt max.  So somewhere from 1.5 to 2.5
> amps.
>
> Maybe that particular SS is just broken in some way?  If so, it's a
> dangerous mode of failure.
>
> On 2/19/2016 2:30 PM, George Skorup wrote:
>
>> Definitely sounds like the SS was clamping. Maybe the SS thought a surge
>> occurred at initial startup of the power supply? And FYI, I have used Traco
>> TSP 48v supplies with -48 radios just fine, output is floating.
>>
>> On 2/19/2016 10:40 AM, Adam Moffett wrote:
>>
>>> ...my first thought of course was maybe it was hooked up wrong the first
>>> time.  The four 16ga wires hold their shape pretty well and I didn't have
>>> to re-bend them to fit, so I'm pretty sure they were on there correctly.
>>>
>>> People talk about SS's "clamping" or "clamping to ground". Could that
>>> cause a short?  I never tested the power wires against ground.
>>>
>>> If you're thinking +48 and -48 mixed on the tower, there are only two
>>> devices on the tower right now.  One base station and one backhaul, and
>>> they're both -48.  There's some 24v stuff in the enclosure at the bottom
>>> (switch, site monitor), but none of those have a ground referenced to power
>>> and they're isolated from the other stuff by a 48v to 24v converter.
>>>
>>>
>>> On 2/19/2016 11:27 AM, Adam Moffett wrote:
>>>
>>>> So I went out to a new location yesterday afternoon just to turn the
>>>> breakers on.  The power co had just plugged in the meter a few days prior.
>>>>
>>>> The Traco 48v power supply there immediately went into an alarm state.
>>>> After some troubleshooting I found a dead short on the -48v power bus
>>>> (terminal blocks with jumpers actually).  The short ended up being on the
>>>> power cable to a Wimax base station, I read 0 ohms between + and - on that
>>>> cable.
>>>>
>>>> There's a Motorola 200SS surge suppressor within 5' of the power bus,
>>>> and then about 80' of wire to the base station.  I checked resistance
>>>> between + and - on each side of the SS and read 0 ohms both ways.  There
>>>> are actually 4x 16ga wires going to the top, so two were screwed down to +
>>>> on the load side of the SS and two on the - side.
>>>>
>>>> That whole part was backstory.  This is where the mystery starts.
>>>>
>>>> I pulled all 4 wires off the load side of the SS to see if I could
>>>> narrow down which pair was shorted, and I couldn't find a short. I checked
>>>> the load side and the supply side of the SS and it was open on both sides.
>>>> So then I reconnected the wires to the SS and checked again - no short.  I
>>>> plugged the BTS back into the bus...powered up just fine.
>>>>
>>>> So where did the short circuit come from and where did it go? In
>>>> hindsight it seems like it had to be in the SS or before it. If it was
>>>> shorted at the top there would have been > 0 ohms of resistance with the
>>>> 80' of wire.
>>>>
>>>>
>>>>
>>>
>>
>

Reply via email to