How does a 44U cabinet need 208V 60A for storage arrays?

In a 4U chassis the max hard drives (front and rear) is about 60 x 3.5"...

Say each drive is 7.5W TDP, that's 450W of drives. Add another 200W for
controller/motherboard and fans. 650W in 4U.

44 / 4 = 11

Multply by 650

7150W

More realistically with a normal amount of drives (like 40 per 4U) a single
208 30A is sufficient,

208 x 30 = 6240W

Run at max 0.85 load on the circuit, so

6240 x 0.85 = 5304W

In a really dense 2.5" environment all of the above is of course invalid,
you could probably need up to 7900W per cabinet
Then there's 52U cabinets as well...
On May 13, 2016 6:16 PM, "Paul Stewart" <[email protected]> wrote:

Yup … general trends on new data centers are pushing those temperatures
higher for efficiency but also with better designs ..



One of our data centers runs at 78F and have no issues – each cabinet is
standard 208V 30A as you mention but can go per cabinet much higher if
needed (ie. 208V 60A for storage arrays)



*From:* Af [mailto:[email protected]] *On Behalf Of *Eric Kuhnke
*Sent:* May 11, 2016 5:15 PM

*To:* [email protected]
*Subject:* Re: [AFMUG] Data center temperatures



There have been some fairly large data set studies done shown that air
intake temperature for huge numbers of servers, at 77-78F does not
correlate with a statistically significant rate of failure.

http://www.datacenterknowledge.com/archives/2008/09/18/intel-servers-do-fine-with-outside-air/

http://www.datacenterknowledge.com/archives/2012/03/23/too-hot-for-humans-but-google-servers-keep-humming/

how/what you do for cooling is definitely dependent on the load. Designing
a colo facility to use a full 208V 30A circuit per cabinet (5.5kW) in a
hot/cold air separated configuration is very different than 'normal' older
facilities that are one large open room.



On Wed, May 11, 2016 at 1:58 PM, Ken Hohhof <[email protected]> wrote:

I’m not sure you can answer the question without knowing the max heat load
per cabinet and how you manage airflow in the cabinets.



AFAIK it used to be standard practice to keep data centers as cold as
possible without requiring people to wear parkas, but energy efficiency is
a consideration now.





*From:* That One Guy /sarcasm <[email protected]>

*Sent:* Wednesday, May 11, 2016 3:51 PM

*To:* [email protected]

*Subject:* Re: [AFMUG] Data center temperatures



apparently 72 is the the ideal for our noc, i set our thermostat to 60 and
it always gets turned back to 72, so i just say fuck it, I wanted new gear
in the racks anyway



On Wed, May 11, 2016 at 3:46 PM, Larry Smith <[email protected]> wrote:

On Wed May 11 2016 15:37, Josh Luthman wrote:
> Just curious what the ideal temp is for a data center.  Our really nice
> building that Sprint ditched ranges from 60 to 90F (on a site monitor).

I try to keep my NOC room at about 62F, that puts many of the CPU's
at 83 to 90F.  Many of the bigger places I visit will generally be 55 to
60F.
Loads of computers (data center type) are primarily groupings of little
heaters...

--
Larry Smith
[email protected]





-- 

If you only see yourself as part of the team but you don't see your team as
part of yourself you have already failed as part of the team.

Reply via email to