I remembering being at a data center on a hot summer day.   Power went out, 
generator started.  Things were fine... then all the air conditioners switched 
on at the same time.  Actually stalled the generator.  We  had to put 
sequencers on the AC.  

From: Faisal Imtiaz 
Sent: Saturday, May 14, 2016 9:20 PM
To: [email protected] 
Subject: Re: [AFMUG] Data center temperatures

FYI, Electrical Code (NECA) and most datacenters require the power not to be 
loaded beyond 80% of breaker capacity... i.e. 16amp draw on a 20amp circuit.

Additionally, one also has to have head room on the power circuit to deal with 
start up draw (current rush). It's not pretty when you have a crap load of 
servers starting up all together 


:)

Faisal Imtiaz
Snappy Internet & Telecom
7266 SW 48 Street
Miami, FL 33155
Tel: 305 663 5518 x 232

Help-desk: (305)663-5518 Option 2 or Email: [email protected]


--------------------------------------------------------------------------------

  From: "Eric Kuhnke" <[email protected]>
  To: [email protected]
  Sent: Saturday, May 14, 2016 7:50:22 PM
  Subject: Re: [AFMUG] Data center temperatures

  How does a 44U cabinet need 208V 60A for storage arrays?

  In a 4U chassis the max hard drives (front and rear) is about 60 x 3.5"...

  Say each drive is 7.5W TDP, that's 450W of drives. Add another 200W for 
controller/motherboard and fans. 650W in 4U.

  44 / 4 = 11

  Multply by 650

  7150W

  More realistically with a normal amount of drives (like 40 per 4U) a single 
208 30A is sufficient,

  208 x 30 = 6240W

  Run at max 0.85 load on the circuit, so

  6240 x 0.85 = 5304W


  In a really dense 2.5" environment all of the above is of course invalid, you 
could probably need up to 7900W per cabinet
  Then there's 52U cabinets as well...

  On May 13, 2016 6:16 PM, "Paul Stewart" <[email protected]> wrote:

    Yup … general trends on new data centers are pushing those temperatures 
higher for efficiency but also with better designs ..



    One of our data centers runs at 78F and have no issues – each cabinet is 
standard 208V 30A as you mention but can go per cabinet much higher if needed 
(ie. 208V 60A for storage arrays)



    From: Af [mailto:[email protected]] On Behalf Of Eric Kuhnke
    Sent: May 11, 2016 5:15 PM


    To: [email protected]
    Subject: Re: [AFMUG] Data center temperatures


    There have been some fairly large data set studies done shown that air 
intake temperature for huge numbers of servers, at 77-78F does not correlate 
with a statistically significant rate of failure.  

    
http://www.datacenterknowledge.com/archives/2008/09/18/intel-servers-do-fine-with-outside-air/

    
http://www.datacenterknowledge.com/archives/2012/03/23/too-hot-for-humans-but-google-servers-keep-humming/



    how/what you do for cooling is definitely dependent on the load. Designing 
a colo facility to use a full 208V 30A circuit per cabinet (5.5kW) in a 
hot/cold air separated configuration is very different than 'normal' older 
facilities that are one large open room.





    On Wed, May 11, 2016 at 1:58 PM, Ken Hohhof <[email protected]> wrote:

      I’m not sure you can answer the question without knowing the max heat 
load per cabinet and how you manage airflow in the cabinets.



      AFAIK it used to be standard practice to keep data centers as cold as 
possible without requiring people to wear parkas, but energy efficiency is a 
consideration now.





      From: That One Guy /sarcasm 

      Sent: Wednesday, May 11, 2016 3:51 PM

      To: [email protected] 

      Subject: Re: [AFMUG] Data center temperatures



      apparently 72 is the the ideal for our noc, i set our thermostat to 60 
and it always gets turned back to 72, so i just say fuck it, I wanted new gear 
in the racks anyway



      On Wed, May 11, 2016 at 3:46 PM, Larry Smith <[email protected]> wrote:

        On Wed May 11 2016 15:37, Josh Luthman wrote:
        > Just curious what the ideal temp is for a data center.  Our really 
nice
        > building that Sprint ditched ranges from 60 to 90F (on a site 
monitor).

        I try to keep my NOC room at about 62F, that puts many of the CPU's
        at 83 to 90F.  Many of the bigger places I visit will generally be 55 
to 60F.
        Loads of computers (data center type) are primarily groupings of little
        heaters...

        --
        Larry Smith
        [email protected]







      -- 

      If you only see yourself as part of the team but you don't see your team 
as part of yourself you have already failed as part of the team.




Reply via email to