Neat :)

Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373
On May 15, 2016 12:26 AM, "Faisal Imtiaz" <[email protected]> wrote:

> nothing special, dell C2100's.... looks like these settings are getting to
> be more common in stuff designed for high density data center install.
>
> Regards.
>
> Faisal Imtiaz
> Snappy Internet & Telecom
> 7266 SW 48 Street
> Miami, FL 33155
> Tel: 305 663 5518 x 232
>
> Help-desk: (305)663-5518 Option 2 or Email: [email protected]
>
> ------------------------------
>
> *From: *"Josh Luthman" <[email protected]>
> *To: *[email protected]
> *Sent: *Sunday, May 15, 2016 12:14:49 AM
> *Subject: *Re: [AFMUG] Data center temperatures
>
> Wow that's cool!  What kind of hardware are they?
>
>
> Josh Luthman
> Office: 937-552-2340
> Direct: 937-552-2343
> 1100 Wayne St
> Suite 1337
> Troy, OH 45373
>
> On Sun, May 15, 2016 at 12:13 AM, Faisal Imtiaz <[email protected]>
> wrote:
>
>> It would be interesting to note that, we are putting in some new servers,
>> and in the bios these have a setting that delays a random amount of time
>> between 50 - 120seconds, before returning to power on state after a power
>> loss   .....
>>
>> :)
>>
>> Faisal Imtiaz
>> Snappy Internet & Telecom
>> 7266 SW 48 Street
>> Miami, FL 33155
>> Tel: 305 663 5518 x 232
>>
>> Help-desk: (305)663-5518 Option 2 or Email: [email protected]
>>
>> ------------------------------
>>
>> *From: *"Chuck McCown" <[email protected]>
>> *To: *[email protected]
>> *Sent: *Saturday, May 14, 2016 11:40:09 PM
>>
>> *Subject: *Re: [AFMUG] Data center temperatures
>>
>> I remembering being at a data center on a hot summer day.   Power went
>> out, generator started.  Things were fine... then all the air conditioners
>> switched on at the same time.  Actually stalled the generator.  We  had to
>> put sequencers on the AC.
>>
>> *From:* Faisal Imtiaz <[email protected]>
>> *Sent:* Saturday, May 14, 2016 9:20 PM
>> *To:* [email protected]
>> *Subject:* Re: [AFMUG] Data center temperatures
>>
>> FYI, Electrical Code (NECA) and most datacenters require the power not to
>> be loaded beyond 80% of breaker capacity... i.e. 16amp draw on a 20amp
>> circuit.
>>
>> Additionally, one also has to have head room on the power circuit to deal
>> with start up draw (current rush). It's not pretty when you have a crap
>> load of servers starting up all together
>>
>>
>> :)
>>
>> Faisal Imtiaz
>> Snappy Internet & Telecom
>> 7266 SW 48 Street
>> Miami, FL 33155
>> Tel: 305 663 5518 x 232
>>
>> Help-desk: (305)663-5518 Option 2 or Email: [email protected]
>>
>> ------------------------------
>>
>> *From: *"Eric Kuhnke" <[email protected]>
>> *To: *[email protected]
>> *Sent: *Saturday, May 14, 2016 7:50:22 PM
>> *Subject: *Re: [AFMUG] Data center temperatures
>>
>> How does a 44U cabinet need 208V 60A for storage arrays?
>>
>> In a 4U chassis the max hard drives (front and rear) is about 60 x 3.5"...
>>
>> Say each drive is 7.5W TDP, that's 450W of drives. Add another 200W for
>> controller/motherboard and fans. 650W in 4U.
>>
>> 44 / 4 = 11
>>
>> Multply by 650
>>
>> 7150W
>>
>> More realistically with a normal amount of drives (like 40 per 4U) a
>> single 208 30A is sufficient,
>>
>> 208 x 30 = 6240W
>>
>> Run at max 0.85 load on the circuit, so
>>
>> 6240 x 0.85 = 5304W
>>
>> In a really dense 2.5" environment all of the above is of course invalid,
>> you could probably need up to 7900W per cabinet
>> Then there's 52U cabinets as well...
>> On May 13, 2016 6:16 PM, "Paul Stewart" <[email protected]> wrote:
>>
>> Yup … general trends on new data centers are pushing those temperatures
>> higher for efficiency but also with better designs ..
>>
>>
>>
>> One of our data centers runs at 78F and have no issues – each cabinet is
>> standard 208V 30A as you mention but can go per cabinet much higher if
>> needed (ie. 208V 60A for storage arrays)
>>
>>
>>
>> *From:* Af [mailto:[email protected]] *On Behalf Of *Eric Kuhnke
>> *Sent:* May 11, 2016 5:15 PM
>>
>> *To:* [email protected]
>> *Subject:* Re: [AFMUG] Data center temperatures
>>
>>
>>
>> There have been some fairly large data set studies done shown that air
>> intake temperature for huge numbers of servers, at 77-78F does not
>> correlate with a statistically significant rate of failure.
>>
>>
>> http://www.datacenterknowledge.com/archives/2008/09/18/intel-servers-do-fine-with-outside-air/
>>
>>
>> http://www.datacenterknowledge.com/archives/2012/03/23/too-hot-for-humans-but-google-servers-keep-humming/
>>
>> how/what you do for cooling is definitely dependent on the load.
>> Designing a colo facility to use a full 208V 30A circuit per cabinet
>> (5.5kW) in a hot/cold air separated configuration is very different than
>> 'normal' older facilities that are one large open room.
>>
>>
>>
>> On Wed, May 11, 2016 at 1:58 PM, Ken Hohhof <[email protected]> wrote:
>>
>> I’m not sure you can answer the question without knowing the max heat
>> load per cabinet and how you manage airflow in the cabinets.
>>
>>
>>
>> AFAIK it used to be standard practice to keep data centers as cold as
>> possible without requiring people to wear parkas, but energy efficiency is
>> a consideration now.
>>
>>
>>
>>
>>
>> *From:* That One Guy /sarcasm <[email protected]>
>>
>> *Sent:* Wednesday, May 11, 2016 3:51 PM
>>
>> *To:* [email protected]
>>
>> *Subject:* Re: [AFMUG] Data center temperatures
>>
>>
>>
>> apparently 72 is the the ideal for our noc, i set our thermostat to 60
>> and it always gets turned back to 72, so i just say fuck it, I wanted new
>> gear in the racks anyway
>>
>>
>>
>> On Wed, May 11, 2016 at 3:46 PM, Larry Smith <[email protected]> wrote:
>>
>> On Wed May 11 2016 15:37, Josh Luthman wrote:
>> > Just curious what the ideal temp is for a data center.  Our really nice
>> > building that Sprint ditched ranges from 60 to 90F (on a site monitor).
>>
>> I try to keep my NOC room at about 62F, that puts many of the CPU's
>> at 83 to 90F.  Many of the bigger places I visit will generally be 55 to
>> 60F.
>> Loads of computers (data center type) are primarily groupings of little
>> heaters...
>>
>> --
>> Larry Smith
>> [email protected]
>>
>>
>>
>>
>>
>> --
>>
>> If you only see yourself as part of the team but you don't see your team
>> as part of yourself you have already failed as part of the team.
>>
>>
>>
>>
>>
>

Reply via email to