How would staggered drive start up work?  Or is the array not available
until the timer is done?

Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373
On May 15, 2016 1:01 AM, "Josh Reynolds" <[email protected]> wrote:

> A lot of the dell servers I use, as well as a lot of the supermicro
> servers have that as well. Thankfully many of the RAID JBOD cards I
> use (softraid ftw, and zfs doesn't like it either) can also stagger
> drive startup.
>
> On Sat, May 14, 2016 at 11:13 PM, Faisal Imtiaz
> <[email protected]> wrote:
> > It would be interesting to note that, we are putting in some new servers,
> > and in the bios these have a setting that delays a random amount of time
> > between 50 - 120seconds, before returning to power on state after a power
> > loss   .....
> >
> > :)
> >
> > Faisal Imtiaz
> > Snappy Internet & Telecom
> > 7266 SW 48 Street
> > Miami, FL 33155
> > Tel: 305 663 5518 x 232
> >
> > Help-desk: (305)663-5518 Option 2 or Email: [email protected]
> >
> > ________________________________
> >
> > From: "Chuck McCown" <[email protected]>
> > To: [email protected]
> > Sent: Saturday, May 14, 2016 11:40:09 PM
> >
> > Subject: Re: [AFMUG] Data center temperatures
> >
> > I remembering being at a data center on a hot summer day.   Power went
> out,
> > generator started.  Things were fine... then all the air conditioners
> > switched on at the same time.  Actually stalled the generator.  We  had
> to
> > put sequencers on the AC.
> >
> > From: Faisal Imtiaz
> > Sent: Saturday, May 14, 2016 9:20 PM
> > To: [email protected]
> > Subject: Re: [AFMUG] Data center temperatures
> >
> > FYI, Electrical Code (NECA) and most datacenters require the power not
> to be
> > loaded beyond 80% of breaker capacity... i.e. 16amp draw on a 20amp
> circuit.
> >
> > Additionally, one also has to have head room on the power circuit to deal
> > with start up draw (current rush). It's not pretty when you have a crap
> load
> > of servers starting up all together
> >
> >
> > :)
> >
> > Faisal Imtiaz
> > Snappy Internet & Telecom
> > 7266 SW 48 Street
> > Miami, FL 33155
> > Tel: 305 663 5518 x 232
> >
> > Help-desk: (305)663-5518 Option 2 or Email: [email protected]
> >
> > ________________________________
> >
> > From: "Eric Kuhnke" <[email protected]>
> > To: [email protected]
> > Sent: Saturday, May 14, 2016 7:50:22 PM
> > Subject: Re: [AFMUG] Data center temperatures
> >
> > How does a 44U cabinet need 208V 60A for storage arrays?
> >
> > In a 4U chassis the max hard drives (front and rear) is about 60 x
> 3.5"...
> >
> > Say each drive is 7.5W TDP, that's 450W of drives. Add another 200W for
> > controller/motherboard and fans. 650W in 4U.
> >
> > 44 / 4 = 11
> >
> > Multply by 650
> >
> > 7150W
> >
> > More realistically with a normal amount of drives (like 40 per 4U) a
> single
> > 208 30A is sufficient,
> >
> > 208 x 30 = 6240W
> >
> > Run at max 0.85 load on the circuit, so
> >
> > 6240 x 0.85 = 5304W
> >
> > In a really dense 2.5" environment all of the above is of course invalid,
> > you could probably need up to 7900W per cabinet
> > Then there's 52U cabinets as well...
> >
> > On May 13, 2016 6:16 PM, "Paul Stewart" <[email protected]> wrote:
> >
> > Yup … general trends on new data centers are pushing those temperatures
> > higher for efficiency but also with better designs ..
> >
> >
> >
> > One of our data centers runs at 78F and have no issues – each cabinet is
> > standard 208V 30A as you mention but can go per cabinet much higher if
> > needed (ie. 208V 60A for storage arrays)
> >
> >
> >
> > From: Af [mailto:[email protected]] On Behalf Of Eric Kuhnke
> > Sent: May 11, 2016 5:15 PM
> >
> >
> > To: [email protected]
> > Subject: Re: [AFMUG] Data center temperatures
> >
> >
> >
> > There have been some fairly large data set studies done shown that air
> > intake temperature for huge numbers of servers, at 77-78F does not
> correlate
> > with a statistically significant rate of failure.
> >
> >
> http://www.datacenterknowledge.com/archives/2008/09/18/intel-servers-do-fine-with-outside-air/
> >
> >
> http://www.datacenterknowledge.com/archives/2012/03/23/too-hot-for-humans-but-google-servers-keep-humming/
> >
> > how/what you do for cooling is definitely dependent on the load.
> Designing a
> > colo facility to use a full 208V 30A circuit per cabinet (5.5kW) in a
> > hot/cold air separated configuration is very different than 'normal'
> older
> > facilities that are one large open room.
> >
> >
> >
> > On Wed, May 11, 2016 at 1:58 PM, Ken Hohhof <[email protected]> wrote:
> >
> > I’m not sure you can answer the question without knowing the max heat
> load
> > per cabinet and how you manage airflow in the cabinets.
> >
> >
> >
> > AFAIK it used to be standard practice to keep data centers as cold as
> > possible without requiring people to wear parkas, but energy efficiency
> is a
> > consideration now.
> >
> >
> >
> >
> >
> > From: That One Guy /sarcasm
> >
> > Sent: Wednesday, May 11, 2016 3:51 PM
> >
> > To: [email protected]
> >
> > Subject: Re: [AFMUG] Data center temperatures
> >
> >
> >
> > apparently 72 is the the ideal for our noc, i set our thermostat to 60
> and
> > it always gets turned back to 72, so i just say fuck it, I wanted new
> gear
> > in the racks anyway
> >
> >
> >
> > On Wed, May 11, 2016 at 3:46 PM, Larry Smith <[email protected]> wrote:
> >
> > On Wed May 11 2016 15:37, Josh Luthman wrote:
> >> Just curious what the ideal temp is for a data center.  Our really nice
> >> building that Sprint ditched ranges from 60 to 90F (on a site monitor).
> >
> > I try to keep my NOC room at about 62F, that puts many of the CPU's
> > at 83 to 90F.  Many of the bigger places I visit will generally be 55 to
> > 60F.
> > Loads of computers (data center type) are primarily groupings of little
> > heaters...
> >
> > --
> > Larry Smith
> > [email protected]
> >
> >
> >
> >
> >
> > --
> >
> > If you only see yourself as part of the team but you don't see your team
> as
> > part of yourself you have already failed as part of the team.
> >
> >
> >
> >
>