Yes. Use a connector that is rated for both. I like the figure 8 type that
Copper goes on one side and aluminum on the other.

On Thu, Jul 21, 2016, 7:46 PM That One Guy /sarcasm <
[email protected]> wrote:

> I was always under the impression the aluminum romex had something to do
> with expansion/contraction creating a disconnect, part of the reason for
> this post
>
> On Thu, Jul 21, 2016 at 9:29 PM, Chuck McCown <[email protected]> wrote:
>
>> or noalox (brand names)
>>
>> http://www.homedepot.com/p/Ideal-NOALOX-4-oz-Anti-Oxidant-Compound-30-026/202276208
>>
>> Back in the 60s, mobile homes, modular homes and some stick built homes
>> were wired up with aluminum romex.  The aluminum would oxidize at screw
>> terminals on receptacles, get hot and catch fire.  So, in a typical
>> overreaction it was banned.  Homes were fixed by using a crimp sleeve to
>> put copper tails on all the aluminum in the walls.  Appraisers and
>> insurance companies were and probably still are on the  lookout for
>> aluminum romex.
>>
>> But if the aluminum is terminated to something that is designed for
>> aluminum wires you will be fine.
>>
>>
>> *From:* Bill Prince <[email protected]>
>> *Sent:* Thursday, July 21, 2016 8:17 PM
>> *To:* [email protected]
>> *Subject:* Re: [AFMUG] is it bad to mix aluminum and copper in bonding?
>>
>>
>> The aluminum will oxidize. It's recommended to use No-ox to prevent it.
>>
>> http://www.sanchem.com/electrical-contact-lubricant.html
>>
>> bp
>>
>> On 7/21/2016 6:52 PM, That One Guy /sarcasm wrote:
>>
>> Im generating the parts list for some upper cross connect boxes, the
>> BBDGE will strip when it comes in with the shield bonded to bus bars. The
>> shield is copper, the recomended grounding thingamajig that slips under the
>> shield and clamps to it is aluminum(or steel, not sure) the mechanical lug
>> on that is copper, the #6 stranded is copper, the bus bar is aluminum, and
>> the connections between the bus bars are the #6 copper
>>
>> am i creating some unknowm lightning magnet here?
>>
>> --
>> If you only see yourself as part of the team but you don't see your team
>> as part of yourself you have already failed as part of the team.
>>
>>
>>
>
>
> --
> If you only see yourself as part of the team but you don't see your team
> as part of yourself you have already failed as part of the team.
>