Hey Ray,
Good posting on ground fault interrupters.  Maybe you could find something
on arc fault interrupters.  In the last few years they have become a new
code requirement for protecting outlets in sleeping areas.  Last time I
cheched some time ago information was pretty sketchy on how they worked.
Thanks,
Ron
----- Original Message ----- 
From: "Ray Boyce" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Sunday, July 30, 2006 11:11 PM
Subject: [BlindHandyMan] Ground Fault Circuit Interrupter


> Hi
>   What is a GFCI?
>
> A Ground Fault Circuit Interrupter (GFCI) is a device to protect against
> electric shock should someone come in contact with a live (Hot) wire and
> a path to ground which would result in a current through his/her body.
The
> GFCI operates by sensing the difference between the currents in the Hot
and
> Neutral conductors.  Under normal conditions, these should be equal.
> However,
> if someone touches the Hot and a Ground such as a plumbing fixture or
> they are standing in water, these currents will not be equal as the path
is
> to Ground - a ground fault - and not to the Neutral.  This might occur
> if a short circuit developed inside an ungrounded appliance or if someone
> was working on a live circuit and accidentally touched a live wire.
>
> The GFCI will trip in a fraction of a second at currents (a few mA) well
> below those that are considered dangerous.  Note that a GFCI is NOT a
> substitute for a fuse or circuit breaker as these devices are still
> required to protect equipment and property from overloads or short
> circuits that can result in fire or other damage.
>
> GFCIs can be installed in place of ordinary outlets in which case they
> protect that outlet as well as any downstream from it.  There are also
> GFCIs that install in the main service panel.
>
> Note that it may be safe and legal to install a GFCI rated at 15 A on a
> 20 A circuit since it will have a 20 A feed-through.  Of course, the GFCI
> outlet itself can then only be used for appliances rated 15 A or less.
>
> Many (if not most) GFCIs also test for a grounded neutral condition where
a
> low resistance path exists downstream between the N and G conductors.  If
> such
> a situation exists, the GFCI will trip immediately when power is applied
> even
> with nothing connected to the protected outlets.
>
>    GFCIs, overloads, and fire safety
>
> A GFCI is NOT a substitute for a fuse or circuit breaker (unless it is a
> combined unit - available to replace circuit breakers at the service
panel).
>
> Therefore, advice like "use a GFCI in place of the normal outlet to
prevent
> appliance fires" is not really valid.
>
> There may be some benefit if a fault developed between Hot and Ground but
> that
> should blow a fuse or trip a circuit breaker if the outlet is properly
> wired.
> If the outlet is ungrounded, nothing would happen until someone touched
the
> metal cabinet and an earth ground simultaneously in which case the GFCI
> would
> trip and provide its safety function.  See the section: "
> Why a GFCI should not
> be used with major appliances"
> for reasons why this is not generally
> desirable as long as the appliance or outlet is properly grounded.
>
> However, if a fault occurs between Hot and Neutral - a short in the motor,
> for
> example - a GFCI will be perfectly happy passing almost any sort of
overload
> current until the GFCI, wiring, and appliance melts down or burns up - a
> GFCI
> is not designed to be a fuse or circuit breaker!  That function must be
> provided separately.
>
>   How does a GFCI work
>
> GFCIs typically test for the following condition:
>
> 1. A Hot to Ground (safety/earth) fault.  Current flows from the Hot wire
to
> Ground bypassing the Neutral.  This is the test that is most critical for
> safety.
>
> 2. A grounded neutral fault.  Due to miswiring or a short circuit, the N
and
> G
> wires are connected by a low resistance path downstream of the GFCI.  In
> this case, the GFCI will trip as soon as power is applied even if nothing
> is connected to its protected (load) circuit.
>
> To detect a Hot to Ground fault, both current carrying wires pass through
> the
> core of a sense coil (transformer).  When the currents are equal and
> opposite,
> there is no output from its multiturn sense voltage winding.  When an
> imbalance
> occurs, an output signal is produced.  When this exceeds a threshold, a
> circuit
> breaker inside the GFCI is tripped.
>
> GFCIs for 220 VAC applications need to monitor both Hots as well as the
> Neutral.  The principles are basically the same: the sum of the currents
in
> Hot1 + Hot2 + Neutral should be zero unless a fault exists.
>
> To detect a grounded neutral fault, a separate drive coil is continuously
> energized and injects a small 120 Hz signal into the current carrying
> conductors.  If a low resistance path exists between N and G downstream
> of the GFCI, this completes a loop (in conjunction with the normal
> connection
> between N and G at the service panel) and enough current flows to again
> trip the GFCI's internal circuit breaker.
>
> GFCIs use toroidal coils (actually transformers to be more accurate) where
> the
> core is shaped like a ring (i.e., toroid or doughnut).  These are
convenient
> and efficient for certain applications.  For all practical purposes, they
> are
> just another kind of transformer.  If you look inside a GFCI, you will
find
> a
> pair of toroidal transformers (one for H-N faults and the other for N-G
> faults
> as described above).  They look like 1/2" diameter rings with the main
> current
> carrying conductors passing once through the center and many fine turns of
> wire (the sense or drive winding) wound around the toroid.
>
> All in all, quite clever technology.  The active component in the Leviton
> GFCI is a single chip - probably a National Semiconductor LM1851 Ground
> Fault
> Interrupter.  For more info, check out the specs at National'a web site
at:
> http://www.national.com/pf/LM/LM1851.html.
>
>
>   More on how the GFCI detects a N-G short
>
> To detect a Neutral to Ground fault there is a second transformer placed
> upstream of the H-G sense transformer (see the illustration of the
internal
> circuitry of the GFCI at:
> http://www.national.com/pf/LM/LM1851.html).
> A small
> drive signal is continuously injected via the 200 T winding which induces
> equal voltages on the H and N wires passing through its core.
>
> * If N and G are separate downstream (as they should be), no current will
be
> flow in either wire and the GFCI will not trip.  (No current will flow in
> the H wire as a result of this stimulus because the voltage induced on
both
> H and N is equal and cancels.)
>
> * If there is a N-G short downstream, a current will flow through the N
> wire,
> to the G wire via the short, and back to the N wire via the normal N-G
> connection at the service panel.  Since there will be NO similar current
in
> the H wire, this represents a current unbalance and will trip the GFCI in
> the same manner as the usual H-G short.
>
> * Interestingly, this scheme automatically detects a H-H fault as well.
> This
> unlikely situation could occur if the Hots from two separate branch
circuits
> were accidentally tied together in a junction box downstream of the GFCI.
> It works the same way except that the unbalance in current that trips the
> GFCI flows through the H wire, through the H-H fault, and back around via
> the Hot busbar at the service panel.  Of course if the two Hots are not on
> the same phase, there may be fireworks as well :-).
>
>    GFCIs and safety ground
>
> Despite the fact that a Ground Fault Circuit Interrupter (GFCI) may be
> installed in a 2 wire circuit, the GFCI does not create a safety ground.
> In fact, shorting between the Hot and Ground holes in the GFCI outlet
> will do absolutely nothing if the GFCI is not connected to a grounded
> circuit (at least for the typical GFCI made by Leviton sold at hardware
> stores and home centers). It will trip only if a fault occurs such that
> current flows to a true ground.  If the original circuit did not have a
> safety ground, the third hole is not connected.  What this means is that
> an appliance with a 3 prong plug can develop a short between Hot and the
> (supposedly) grounded case but the GFCI will not trip until someone
> touches the case and an earth ground (e.g., water pipe, ground from
> some other circuit, etc.) at the same time.
>
> Note that even though this is acceptable by the NEC, I do not consider it
> desirable.  Your safety now depends on the proper functioning of the GFCI
> which is considerable more complex and failure prone than a simple fuse or
> circuit breaker.  Therefore, if at all possible, provide a proper Code
> compliant ground connection to all outlets feeding appliances with 3 wire
> plugs.
>
>   Where are 3 wire grounded outlets required?
>
> If you move into a house or apartment where some or all of the outlets are
> the
> old 2 prong ungrounded type, don't panic.  There is no reason to call an
> electrician at 2:00 AM in the morning to upgrade them all at great
expense.
>
> You don't need grounded outlets for two wire appliances, lamps, etc.  They
> do essentially nothing if the third hole isn't occupied :-).  A GFCI will
> provide much more protection!
>
> You should have grounded outlets for the following:
>
> * Computers in order for the line filters and surge suppressors to be most
> effective.
>
> * High-end entertainment gear if it uses 3 prong plugs for similar
reasons.
>
> * Microwave ovens.  For safety, these really should be on a grounded
> circuit.
> (A GFCI will not protect against a fault on the high voltage side of a
> microwave oven, though this sort of fault is extremely unlikely).
>
> * Large appliances including refrigerators, clothes washers and dryers,
> dehumidifiers, window air conditioners, etc.
>
> In most cases, there will only be a few circuits where this is needed and
> only
> these need to be upgraded.  To what extent the wiring plan of your
residence
> separates lighting type circuits from those with outlets that will be used
> for
> 3 wire equipment will determine how easy it is to upgrade only those
outlets
> that are affected.  It may be cheaper to just add new branch circuits for
> specific equipment needs.
>
>
>
> To listen to the show archives go to link
>  http://acbradio.org/handyman.html
> or
> ftp://ftp.acbradio.org/acbradio-archives/handyman/
>
> The Pod Cast address for the Blind Handy Man Show is.
> http://www.acbradio.org/news/xml/podcast.php?pgm=saturday
>
> The Pod Cast address for the Cooking In The Dark Show is.
> http://www.gcast.com/u/cookingindark/main.xml
>
> Visit The New Blind Handy Man Files Page To Review Contributions From
Various List Members At The Following Address:
> http://www.jaws-users.com/handyman/
> Visit the new archives page at the following address
> http://www.mail-archive.com/[email protected]/
> For a complete list of email commands pertaining to the Blind Handy Man
list just send a blank message to:
> [EMAIL PROTECTED]
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
> -- 
> No virus found in this incoming message.
> Checked by AVG Free Edition.
> Version: 7.1.394 / Virus Database: 268.10.5/403 - Release Date: 7/28/06
>


To listen to the show archives go to link
 http://acbradio.org/handyman.html
or
ftp://ftp.acbradio.org/acbradio-archives/handyman/

The Pod Cast address for the Blind Handy Man Show is.
http://www.acbradio.org/news/xml/podcast.php?pgm=saturday

The Pod Cast address for the Cooking In The Dark Show is.
http://www.gcast.com/u/cookingindark/main.xml

Visit The New Blind Handy Man Files Page To Review Contributions From Various 
List Members At The Following Address:
http://www.jaws-users.com/handyman/
Visit the new archives page at the following address
http://www.mail-archive.com/[email protected]/  
For a complete list of email commands pertaining to the Blind Handy Man list 
just send a blank message to:
[EMAIL PROTECTED] 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/blindhandyman/

<*> To unsubscribe from this group, send an email to:
    [EMAIL PROTECTED]

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/
 


Reply via email to