Arc Fault Circuit Interrupter (AFCI) FACT SHEET 
THE AFCI

The "AFCI" is an arc fault circuit  interrupter. AFCIs are
newly-developed  electrical devices designed to protect  against fires
caused by arcing faults in the  home electrical wiring.

THE FIRE PROBLEM

Annually, over 40,000 fires are attributed  to home electrical wiring.
These fires  result in over 350 deaths and over 1,400  injuries each
year

1

. Arcing faults are one  of the major causes of these fires. When
unwanted arcing occurs, it generates high  temperatures that can ignite
nearby  combustibles such as wood, paper, and  carpets.

Arcing faults often occur in damaged or  deteriorated wires and cords.
Some causes  of damaged and deteriorated wiring include  puncturing of
wire insulation from picture  hanging or cable staples, poorly installed
outlets or switches, cords caught in doors  or under furniture,
furniture pushed against  plugs in an outlet, natural aging, and cord
exposure to heat vents and sunlight.  
HOW THE AFCI WORKS

Conventional circuit breakers only respond to overloads and short
circuits; so they do not  protect against arcing conditions that produce
erratic current flow. An AFCI is selective  so that normal arcs do not
cause it to trip.

The AFCI circuitry continuously monitors current flow through the AFCI.
AFCIs use  unique current sensing circuitry to discriminate between
normal and unwanted arcing  conditions. Once an unwanted arcing
condition is detected, the control circuitry in the  
Ault, Singh, and Smith, "
1996 Residential Fire Loss Estimates", October 1998, U.S. Consumer

Product Safety Commission, Directorate for Epidemiology and Health
Sciences.

AFCI trips the internal contacts, thus de-energizing the circuit and
reducing the potential  for a fire to occur. An AFCI should not trip
during normal arcing conditions, which can  occur when a switch is
opened or a plug is pulled from a receptacle.  
Presently, AFCIs are designed into conventional circuit breakers
combining traditional  overload and short-circuit protection with arc
fault protection. AFCI circuit breakers  (AFCIs) have a test button and
look similar to ground fault circuit interrupter (GFCI)  circuit
breakers. Some designs combine GFCI and AFCI protection. Additional AFCI
design configurations are anticipated in the near future.  
It is important to note that AFCIs are designed to mitigate the effects
of arcing faults but  cannot eliminate them completely. In some cases,
the initial arc may cause ignition prior  to detection and circuit
interruption by the AFCI.  
The AFCI circuit breaker serves a dual purpose - not only will it shut
off electricity in the  event of an "arcing fault", but it will also
trip when a short circuit or an overload occurs.  The AFCI circuit
breaker provides protection for the branch circuit wiring and limited
protection for power cords and extension cords. Single-pole, 15- and 20-
ampere AFCI  circuit breakers are presently available.  
WHERE AFCIs SHOULD BE USED

The 1999 edition of the National Electrical Code, the model code for
electrical wiring  adopted by many local jurisdictions, requires AFCIs
for receptacle outlets in bedrooms,  effective January 1, 2002. Although
the requirement is limited to only certain circuits in  new residential
construction, AFCIs should be considered for added protection in other
circuits and for existing homes as well. Older homes with aging and
deteriorating wiring  systems can especially benefit from the added
protection of AFCIs. AFCIs should also  be considered whenever adding or
upgrading a panel box while using existing branch  circuit conductors.

INSTALLING AFCIs

AFCI circuit breakers should be installed by a qualified electrician.
The installer should  follow the instructions accompanying the device
and the panel box.

In homes equipped with conventional circuit breakers rather than fuses,
an AFCI circuit  breaker may be installed in the panel box in place of
the conventional circuit breaker to  add arc protection to a branch
circuit. Homes with fuses are limited to receptacle or  portable-type
AFCIs, which are expected to be available in the near future, or AFCI
circuit breakers can be added in separate panel boxes next to the fuse
panel box.  
TESTING AN AFCI

AFCIs should be tested after installation to make sure they are working
properly and  protecting the circuit. Subsequently, AFCIs should be
tested once a month to make sure  they are working properly and
providing protection from fires initiated by arcing faults.

A test button is located on the front of the device. The user should
follow the instructions  accompanying the device. If the device does not
trip when tested, the AFCI is defective  and should be replaced.  
AFCIs vs. GFCIs

The AFCI should not be confused with the GFCI or ground fault circuit
interrupter. The  GFCI is designed to protect people from severe or
fatal electric shocks while the AFCI  protects against fires caused by
arcing faults. The GFCI also can protect against some  electrical fires
by detecting arcing and other faults to ground but cannot detect
hazardous  across-the-line arcing faults that can cause fires.

A ground fault is an unintentional electric path diverting current to
ground. Ground  faults occur when current leaks from a circuit. How the
current leaks is very important.  If a person's body provides a path to
ground for this leakage, the person could be injured,  burned, severely
shocked, or electrocuted.  
The National Electrical Code requires GFCI protection for receptacles
located outdoors;  in bathrooms, garages, kitchens, crawl spaces and
unfinished basements; and at certain  locations such as near swimming
pools. A combination AFCI and GFCI can be used to  satisfy the NEC
requirement for GFCI protection only if specifically marked as a
combination device.  Drag
Page Menu

8.5 x 11 in
Status

Bookmarks
Single Page
Continuous
Continuous - Facing
Facing
Zoom Out
Zoom In
Next Page
Last Page

File
Save a Copy
Print
Email
Search

Basic
Hand Tool

Select
Snapshot Tool

Select

Select

Zoom

ZoomIn
Actual Size
Fit Page
Fit Width
Zoom Out
Zoom Menu
Zoom In

Edit

Rotate View
Rotate Clockwise
Rotate Clockwise

Tasks

Add-on Tools
Adobe PDF Document End 

-----Original Message-----
From: blindhandyman@yahoogroups.com
[mailto:[EMAIL PROTECTED] On Behalf Of R & S Enterprises
Sent: Monday, 31 July 2006 10:28
To: blindhandyman@yahoogroups.com
Subject: Re: [BlindHandyMan] Ground Fault Circuit Interrupter

Hey Ray,
Good posting on ground fault interrupters.  Maybe you could find
something on arc fault interrupters.  In the last few years they have
become a new code requirement for protecting outlets in sleeping areas.
Last time I cheched some time ago information was pretty sketchy on how
they worked.
Thanks,
Ron
----- Original Message -----
From: "Ray Boyce" <[EMAIL PROTECTED]>
To: <blindhandyman@yahoogroups.com>
Sent: Sunday, July 30, 2006 11:11 PM
Subject: [BlindHandyMan] Ground Fault Circuit Interrupter


> Hi
>   What is a GFCI?
>
> A Ground Fault Circuit Interrupter (GFCI) is a device to protect
against
> electric shock should someone come in contact with a live (Hot) wire
and
> a path to ground which would result in a current through his/her body.
The
> GFCI operates by sensing the difference between the currents in the
Hot
and
> Neutral conductors.  Under normal conditions, these should be equal.
> However,
> if someone touches the Hot and a Ground such as a plumbing fixture or
> they are standing in water, these currents will not be equal as the
path
is
> to Ground - a ground fault - and not to the Neutral.  This might occur
> if a short circuit developed inside an ungrounded appliance or if
someone
> was working on a live circuit and accidentally touched a live wire.
>
> The GFCI will trip in a fraction of a second at currents (a few mA)
well
> below those that are considered dangerous.  Note that a GFCI is NOT a
> substitute for a fuse or circuit breaker as these devices are still
> required to protect equipment and property from overloads or short
> circuits that can result in fire or other damage.
>
> GFCIs can be installed in place of ordinary outlets in which case they
> protect that outlet as well as any downstream from it.  There are also
> GFCIs that install in the main service panel.
>
> Note that it may be safe and legal to install a GFCI rated at 15 A on
a
> 20 A circuit since it will have a 20 A feed-through.  Of course, the
GFCI
> outlet itself can then only be used for appliances rated 15 A or less.
>
> Many (if not most) GFCIs also test for a grounded neutral condition
where
a
> low resistance path exists downstream between the N and G conductors.
If
> such
> a situation exists, the GFCI will trip immediately when power is
applied
> even
> with nothing connected to the protected outlets.
>
>    GFCIs, overloads, and fire safety
>
> A GFCI is NOT a substitute for a fuse or circuit breaker (unless it is
a
> combined unit - available to replace circuit breakers at the service
panel).
>
> Therefore, advice like "use a GFCI in place of the normal outlet to
prevent
> appliance fires" is not really valid.
>
> There may be some benefit if a fault developed between Hot and Ground
but
> that
> should blow a fuse or trip a circuit breaker if the outlet is properly
> wired.
> If the outlet is ungrounded, nothing would happen until someone
touched
the
> metal cabinet and an earth ground simultaneously in which case the
GFCI
> would
> trip and provide its safety function.  See the section: "
> Why a GFCI should not
> be used with major appliances"
> for reasons why this is not generally
> desirable as long as the appliance or outlet is properly grounded.
>
> However, if a fault occurs between Hot and Neutral - a short in the
motor,
> for
> example - a GFCI will be perfectly happy passing almost any sort of
overload
> current until the GFCI, wiring, and appliance melts down or burns up -
a
> GFCI
> is not designed to be a fuse or circuit breaker!  That function must
be
> provided separately.
>
>   How does a GFCI work
>
> GFCIs typically test for the following condition:
>
> 1. A Hot to Ground (safety/earth) fault.  Current flows from the Hot
wire
to
> Ground bypassing the Neutral.  This is the test that is most critical
for
> safety.
>
> 2. A grounded neutral fault.  Due to miswiring or a short circuit, the
N
and
> G
> wires are connected by a low resistance path downstream of the GFCI.
In
> this case, the GFCI will trip as soon as power is applied even if
nothing
> is connected to its protected (load) circuit.
>
> To detect a Hot to Ground fault, both current carrying wires pass
through
> the
> core of a sense coil (transformer).  When the currents are equal and
> opposite,
> there is no output from its multiturn sense voltage winding.  When an
> imbalance
> occurs, an output signal is produced.  When this exceeds a threshold,
a
> circuit
> breaker inside the GFCI is tripped.
>
> GFCIs for 220 VAC applications need to monitor both Hots as well as
the
> Neutral.  The principles are basically the same: the sum of the
currents
in
> Hot1 + Hot2 + Neutral should be zero unless a fault exists.
>
> To detect a grounded neutral fault, a separate drive coil is
continuously
> energized and injects a small 120 Hz signal into the current carrying
> conductors.  If a low resistance path exists between N and G
downstream
> of the GFCI, this completes a loop (in conjunction with the normal
> connection
> between N and G at the service panel) and enough current flows to
again
> trip the GFCI's internal circuit breaker.
>
> GFCIs use toroidal coils (actually transformers to be more accurate)
where
> the
> core is shaped like a ring (i.e., toroid or doughnut).  These are
convenient
> and efficient for certain applications.  For all practical purposes,
they
> are
> just another kind of transformer.  If you look inside a GFCI, you will
find
> a
> pair of toroidal transformers (one for H-N faults and the other for
N-G
> faults
> as described above).  They look like 1/2" diameter rings with the main
> current
> carrying conductors passing once through the center and many fine
turns of
> wire (the sense or drive winding) wound around the toroid.
>
> All in all, quite clever technology.  The active component in the
Leviton
> GFCI is a single chip - probably a National Semiconductor LM1851
Ground
> Fault
> Interrupter.  For more info, check out the specs at National'a web
site
at:
> http://www.national.com/pf/LM/LM1851.html.
>
>
>   More on how the GFCI detects a N-G short
>
> To detect a Neutral to Ground fault there is a second transformer
placed
> upstream of the H-G sense transformer (see the illustration of the
internal
> circuitry of the GFCI at:
> http://www.national.com/pf/LM/LM1851.html).
> A small
> drive signal is continuously injected via the 200 T winding which
induces
> equal voltages on the H and N wires passing through its core.
>
> * If N and G are separate downstream (as they should be), no current
will
be
> flow in either wire and the GFCI will not trip.  (No current will flow
in
> the H wire as a result of this stimulus because the voltage induced on
both
> H and N is equal and cancels.)
>
> * If there is a N-G short downstream, a current will flow through the
N
> wire,
> to the G wire via the short, and back to the N wire via the normal N-G
> connection at the service panel.  Since there will be NO similar
current
in
> the H wire, this represents a current unbalance and will trip the GFCI
in
> the same manner as the usual H-G short.
>
> * Interestingly, this scheme automatically detects a H-H fault as
well.
> This
> unlikely situation could occur if the Hots from two separate branch
circuits
> were accidentally tied together in a junction box downstream of the
GFCI.
> It works the same way except that the unbalance in current that trips
the
> GFCI flows through the H wire, through the H-H fault, and back around
via
> the Hot busbar at the service panel.  Of course if the two Hots are
not on
> the same phase, there may be fireworks as well :-).
>
>    GFCIs and safety ground
>
> Despite the fact that a Ground Fault Circuit Interrupter (GFCI) may be
> installed in a 2 wire circuit, the GFCI does not create a safety
ground.
> In fact, shorting between the Hot and Ground holes in the GFCI outlet
> will do absolutely nothing if the GFCI is not connected to a grounded
> circuit (at least for the typical GFCI made by Leviton sold at
hardware
> stores and home centers). It will trip only if a fault occurs such
that
> current flows to a true ground.  If the original circuit did not have
a
> safety ground, the third hole is not connected.  What this means is
that
> an appliance with a 3 prong plug can develop a short between Hot and
the
> (supposedly) grounded case but the GFCI will not trip until someone
> touches the case and an earth ground (e.g., water pipe, ground from
> some other circuit, etc.) at the same time.
>
> Note that even though this is acceptable by the NEC, I do not consider
it
> desirable.  Your safety now depends on the proper functioning of the
GFCI
> which is considerable more complex and failure prone than a simple
fuse or
> circuit breaker.  Therefore, if at all possible, provide a proper Code
> compliant ground connection to all outlets feeding appliances with 3
wire
> plugs.
>
>   Where are 3 wire grounded outlets required?
>
> If you move into a house or apartment where some or all of the outlets
are
> the
> old 2 prong ungrounded type, don't panic.  There is no reason to call
an
> electrician at 2:00 AM in the morning to upgrade them all at great
expense.
>
> You don't need grounded outlets for two wire appliances, lamps, etc.
They
> do essentially nothing if the third hole isn't occupied :-).  A GFCI
will
> provide much more protection!
>
> You should have grounded outlets for the following:
>
> * Computers in order for the line filters and surge suppressors to be
most
> effective.
>
> * High-end entertainment gear if it uses 3 prong plugs for similar
reasons.
>
> * Microwave ovens.  For safety, these really should be on a grounded
> circuit.
> (A GFCI will not protect against a fault on the high voltage side of a
> microwave oven, though this sort of fault is extremely unlikely).
>
> * Large appliances including refrigerators, clothes washers and
dryers,
> dehumidifiers, window air conditioners, etc.
>
> In most cases, there will only be a few circuits where this is needed
and
> only
> these need to be upgraded.  To what extent the wiring plan of your
residence
> separates lighting type circuits from those with outlets that will be
used
> for
> 3 wire equipment will determine how easy it is to upgrade only those
outlets
> that are affected.  It may be cheaper to just add new branch circuits
for
> specific equipment needs.
>
>
>
> To listen to the show archives go to link
>  http://acbradio.org/handyman.html
> or
> ftp://ftp.acbradio.org/acbradio-archives/handyman/
>
> The Pod Cast address for the Blind Handy Man Show is.
> http://www.acbradio.org/news/xml/podcast.php?pgm=saturday
>
> The Pod Cast address for the Cooking In The Dark Show is.
> http://www.gcast.com/u/cookingindark/main.xml
>
> Visit The New Blind Handy Man Files Page To Review Contributions From
Various List Members At The Following Address:
> http://www.jaws-users.com/handyman/
> Visit the new archives page at the following address
> http://www.mail-archive.com/blindhandyman@yahoogroups.com/
> For a complete list of email commands pertaining to the Blind Handy
Man
list just send a blank message to:
> [EMAIL PROTECTED]
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
> -- 
> No virus found in this incoming message.
> Checked by AVG Free Edition.
> Version: 7.1.394 / Virus Database: 268.10.5/403 - Release Date:
7/28/06
>


To listen to the show archives go to link
 http://acbradio.org/handyman.html
or
ftp://ftp.acbradio.org/acbradio-archives/handyman/

The Pod Cast address for the Blind Handy Man Show is.
http://www.acbradio.org/news/xml/podcast.php?pgm=saturday

The Pod Cast address for the Cooking In The Dark Show is.
http://www.gcast.com/u/cookingindark/main.xml

Visit The New Blind Handy Man Files Page To Review Contributions From
Various List Members At The Following Address:
http://www.jaws-users.com/handyman/
Visit the new archives page at the following address
http://www.mail-archive.com/blindhandyman@yahoogroups.com/  
For a complete list of email commands pertaining to the Blind Handy Man
list just send a blank message to:
[EMAIL PROTECTED] 
Yahoo! Groups Links



 



**********************************************************************
This message and its attachments may contain legally
privileged or confidential information. If you are not the
intended recipient, you must not disclose or use the
information contained in it. If you have received this e-mail
in error, please notify the sender immediately by return
e-mail and delete the e-mail.

Any content of this message and its attachments which
does not relate to the official business of Eraring Energy
must be taken not to have been sent or endorsed by
Eraring Energy. No warranty is made that the e-mail or
attachment(s) are free from computer virus or other defect.
**********************************************************************



To listen to the show archives go to link
 http://acbradio.org/handyman.html
or
ftp://ftp.acbradio.org/acbradio-archives/handyman/

The Pod Cast address for the Blind Handy Man Show is.
http://www.acbradio.org/news/xml/podcast.php?pgm=saturday

The Pod Cast address for the Cooking In The Dark Show is.
http://www.gcast.com/u/cookingindark/main.xml

Visit The New Blind Handy Man Files Page To Review Contributions From Various 
List Members At The Following Address:
http://www.jaws-users.com/handyman/
Visit the new archives page at the following address
http://www.mail-archive.com/blindhandyman@yahoogroups.com/  
For a complete list of email commands pertaining to the Blind Handy Man list 
just send a blank message to:
[EMAIL PROTECTED] 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/blindhandyman/

<*> To unsubscribe from this group, send an email to:
    [EMAIL PROTECTED]

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/
 


Reply via email to