Thanks for the info Dave, this was very helpful. I actually meant Category 6
not Category 5e in my last email for GigE purposes.

> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
> Behalf Of Dave Watkins
> Sent: Friday, June 10, 2005 10:39 AM
> To: 'CLUG General'
> Subject: RE: [clug-talk] voice & data on cat5 ( LONG)
> 
> Hi Kin,
> 
> Here are a few tidbits I have found. BTW, nobody mentioned Cat6 which if
> Gigabit capable (as is Cat5e - but maxed out)
> 
> 
> ............................................
> 
> Personally; unless you are required to have cabling that will last more
> than
> 7 years or so, I'd go Cat5e.
> 
> As others have mentioned, Cat6 is basically better quality and will
> hopefully support future enhancements better than Cat5e. However, at this
> point in time, there is no practical difference; both support 1000Base-T
> (Gigabit) up to 100M max (using all four pairs remember).
> 
> Yes, you should definitely use PoE. Remember, not using PoE can also be
> costly - you'll need lots more power sockets at desks. More importantly,
> how
> would you provide battery backup in times of power failure for all those
> sockets? (people still expect phones to work during power failures and
> this
> is probably more critical in a school.) Much easier to put a UPS in the
> wiring closet...
> 
> If you have recent edge switches then add mid-span power units to them.
> Otherwise, buy new PoE switches that support the 802.3af standard. Check
> that your IP handsets will be compatible. Check the power budget on each
> switch as some handsets consume more power than others and most switches
> do
> not have PSUs capable of handling the highest power devices on all ports.
> 
> .........................................
> 
> 
> 
> If you are looking for a long term solution, install everything CAT-6.
> If you plan to reconfigure work areas frequently, and need to save a few
> bucks, install everything CAT-5e.
> If you want a long term cabling solution, but still need to save a few
> bucks, mix it up a bit. You could install CAT-6 cabling and CAT-5e
> components (outlets, patch panels, patch cords, etc) You will save money
> now
> by installing cheaper components which can be replaced in the future when
> the need arises. When the time does come to upgrade to CAT-6 it will be
> much
> more cost effective (from a labor standpoint)to replace jacks and patch
> panels and test than it would be to remove all of the old cabling, install
> all new cabling, jack, terminate and test. Besides, if you check around
> and
> chose your cable wisely, you may find that CAT-6 cable is not much more
> expensive than CAT-5e
> 
> .....................
> 
> 
> Cat5e and Cat6 Comparison
> Category 6 Cabling System and Application
> 
> 
> Why do I need all the bandwidth of category 6? As far as I know, there is
> no
> application today that requires 200 MHz of bandwidth.
> 
> Bandwidth precedes data rates just as highways come before traffic.
> Doubling
> the bandwidth is like adding twice the number of lanes on a highway. The
> trends of the past and the predictions for the future indicate that data
> rates have been doubling every 18 months. Current applications running at
> 1
> Gb/s are really pushing the limits of category 5e cabling. As streaming
> media applications such as video and multi-media become commonplace, the
> demands for faster data rates will increase and spawn new applications
> that
> will benefit from the higher bandwidth offered by category 6. This is
> exactly what happened in the early 90's when the higher bandwidth of
> category 5 cabling compared to category 3 caused most LAN applications to
> choose the better media to allow simpler, cost effective, higher speed LAN
> applications, such as 100BASE-TX. Note: Bandwidth is defined as the
> highest
> frequency up to which positive power sum ACR (Attenuation to Crosstalk
> Ratio) is greater than zero.
> 
> What is the general difference between category 5e and category 6?
> 
> The general difference between category 5e and category 6 is in the
> transmission performance, and extension of the available bandwidth from
> 100
> MHz for category 5e to 200 MHz for category 6. This includes better
> insertion loss, near end crosstalk (NEXT), return loss, and equal level
> far
> end crosstalk (ELFEXT). These improvements provide a higher signal-to-
> noise
> ratio, allowing higher reliability for current applications and higher
> data
> rates for future applications.
> 
> Will category 6 supersede category 5e?
> 
> Yes, analyst predictions and independent polls indicate that 80 to 90
> percent of all new installations will be cabled with category 6. The fact
> that category 6 link and channel requirements are backward compatible to
> category 5e makes it very easy for customers to choose category 6 and
> supersede category 5e in their networks. Applications that worked over
> category 5e will work over category 6.
> 
> What does category 6 do for my current network vs. category 5e?
> 
> Because of its improved transmission performance and superior immunity
> from
> external noise, systems operating over category 6 cabling will have fewer
> errors vs. category 5e for current applications. This means fewer
> re-transmissions of lost or corrupted data packets under certain
> conditions,
> which translates into higher reliability for category 6 networks compared
> to
> category 5e networks.
> 
> When should I recommend or install category 6 vs. category 5e?
> 
> >From a future proofing perspective, it is always better to install the
> best
> cabling available. This is because it is so difficult to replace cabling
> inside walls, in ducts under floors and other difficult places to access.
> The rationale is that cabling will last at least 10 years and will support
> at least four to five generations of equipment during that time. If future
> equipment running at much higher data rates requires better cabling, it
> will
> be very expensive to pull out category 5e cabling at a later time to
> install
> category 6 cabling. So why not do it for a premium of about 20 percent
> over
> category 5e on an installed basis?
> 
> What is the shortest link that the standard will allow?
> 
> There is no short length limit. The standard is intended to work for all
> lengths up to 100 meters. There is a guideline in ANSI/TIA/EIA-568-B.1
> that
> says the consolidation point should be located at least 15 meters away
> from
> the telecommunications room to reduce the effect of connectors in close
> proximity. This recommendation is based upon worst-case performance
> calculations for short links with four mated connections in the channel.
> 
> What is a "tuned" system between cable and hardware? Is this really needed
> if product meets the standard?
> 
> The word "tuned" has been used by several manufacturers to describe
> products
> that deliver headroom to the category 6 standard. This is outside the
> scope
> of the category 6 standard. The component requirements of the standard
> have
> been carefully designed and analyzed to assure channel compliance and
> electrical/ mechanical interoperability.
> 
> What is impedance matching between cable and hardware? Is this really
> needed
> if product meets the standard?
> 
> The standard has no impedance matching requirements. These are addressed
> by
> having return loss requirements for cables, connectors, and patch cords.
> 
> Is there a use for category 6 in the residential market?
> 
> Yes, category 6 will be very effective in the residential market to
> support
> higher Internet access speeds while facilitating the more stringent Class
> B
> EMC requirements (see also the entire FCC Rules and Regulations, Title 47,
> Part 15). The better balance of category 6 will make it easier to meet the
> residential EMC requirements compared to category 5e cabling. Also, the
> growth of streaming media applications to the home will increase the need
> for higher data rates which are supported more easily and efficiently by
> category 6 cabling.
> 
> Why wouldn't I skip category 6 and go straight to optical fiber?
> 
> You can certainly do that but will find that a fiber system is still very
> expensive. Ultimately, economics drive customer decisions, and today
> optical
> fiber together with optical transceivers is about twice as expensive as an
> equivalent system built using category 6 and associated copper
> electronics.
> Installation of copper cabling is more craft-friendly and can be
> accomplished with simple tools and techniques. Additionally, copper
> cabling
> supports the emerging Data Terminal Equipment (DTE) power standard under
> development by IEEE (802.3af).
> 
> What is meant by the term "Electrically Balanced"?
> 
> A simple open wire circuit consisting of two wires is considered to be a
> uniform, balanced transmission line. A uniform transmission line is one
> which has substantially identical electrical properties throughout its
> length, while a balanced transmission line is one whose two conductors are
> electrically alike and symmetrical with respect to ground and other nearby
> conductors.* "Electrically balanced" relates to the physical geometry and
> the dielectric properties of a twisted pair of conductors. If two
> insulated
> conductors are physically identical to one another in diameter,
> concentricity, dielectric material and are uniformly twisted with equal
> length of conductor, then the pair is electrically balanced with respect
> to
> its surroundings. The degree of electrical balance depends on the design
> and
> manufacturing process. Category 6 cable requires a greater degree of
> precision in the manufacturing process. Likewise, a category 6 connector
> requires a more balanced circuit design. For balanced transmission, an
> equal
> voltage of opposite polarity is applied on each conductor of a pair. The
> electromagnetic fields created by one conductor cancel out the
> electromagnetic fields created by its "balanced" companion conductor,
> leading to very little radiation from the balanced twisted pair
> transmission
> line. The same concept applies to external noise that is induced on each
> conductor of a twisted pair. A noise signal from an external source, such
> as
> radiation from a radio transmitter antenna generates an equal voltage of
> the
> same polarity, or "common mode voltage," on each conductor of a pair. The
> difference in voltage between conductors of a pair from this radiated
> signal, the "differential voltage," is effectively zero. Since the desired
> signal on the pair is the differential signal, the interference does not
> affect balanced transmission. The degree of electrical balance is
> determined
> by measuring the "differential voltage" and comparing it to the "common
> mode
> voltage" expressed in decibels (dB). This measurement is called
> Longitudinal
> Conversion Loss "LCL" in the Category 6 standard. * The ABC's of the
> telephone Vol. 7
> Category 6 Cable Questions
> What is the difference between enhanced category 5e cable rated for 400
> MHz
> and category 6 cable rated for 250 MHz?
> 
> Category 5e requirements are specified up to 100 MHz. Cables can be tested
> up to any frequency that is supported by the test equipment, but such
> measurements are meaningless without the context of applications and
> cabling
> standards. The category 6 standard sets minimum requirements up to 250 MHz
> for cables, connecting hardware, patch cords, channels and permanent
> links,
> and therefore guarantees reasonable performance that can be utilized by
> applications.
> 
> Why did all category 6 cable used to have a spline, and now is offered
> without one?
> 
> Some category 6 cable designs have a spline to increase the separation
> between pairs and also to maintain the pair geometry. This additional
> separation improves NEXT performance and allows category 6 compliance to
> be
> achieved. With advances in technology, manufacturers have found other ways
> of meeting category 6 requirements. The bottom line is the internal
> construction of the cable does not matter, so long as it meets all the
> transmission and physical requirements of category 6. The standard does
> not
> dictate any particular method of cable construction.
> 
> Is there a limitation on the size of bundles one can have with category 6?
> Can you have 200-300 and still pass category 6?
> 
> There is no limit imposed by the standards on the maximum number of
> category
> 6 cables in a bundle. This is a matter for the market and the industry to
> determine based on practical considerations. It should be pointed out that
> after six or eight cables, the performance in any cable will not change
> significantly since the cables will be too far away to add any additional
> external (or alien) NEXT.
> Category 6 Patch Cord Questions
> Will contractors be able to make their own patch cords?
> 
> Category 6 patch cords are precision products, just like the cables and
> the
> connectors. They are best manufactured and tested in a controlled
> environment to ensure consistent, reliable performance. This will ensure
> interoperability and backward compatibility. All this supports patch cords
> as a factory-assembled product rather than a field-assembled product.
> 
> Do you have to use the manufacturer's patch cords to get category 6
> performance?
> 
> The category 6 standard has specifications for patch cords and connectors
> that are intended to assure interoperable category 6 performance. If
> manufacturers can demonstrate that each component meets the requirements
> in
> the standard, minimum category 6 performance will be achieved. However,
> manufacturers may also design their products to perform better than the
> minimum category 6 requirements, and in these cases compatible patch cords
> and connectors may lead to performance above the minimum category 6
> requirements.
> 
> Category 6 Testing Questions Why do field tester manufacturers offer many
> different link adapters if everyone meets the standard?
> 
> This was an interim solution while the standard was still being developed
> and the interoperability requirements were not yet established. It is
> likely
> that soon one or more adapters will work for testing of cabling from all
> vendors.
> 
> Would you get passing test results if you used a link adapter not
> recommended by a manufacturer?
> 
> You should expect to get passing results if both the link adapter
> interface
> and the mating jack that is part of the link are both compliant to
> category
> 6 requirements.
> Category 6 Connecting Hardware Questions
> Are the connectors for category 5e and category 6 different? Why are they
> more expensive?
> 
> Although category 6 and category 5e connectors may look alike, category 6
> connectors have much better transmission performance. For example, at 100
> MHz, NEXT of a category 5e connector is 43 decibels (dB), while NEXT of a
> category 6 connector is 54 dB. This means that a cat6 connector couples
> about 1/12 of the power that a cat5e connector couples from one pair to
> another pair. Conversely, one can say that a category 6 connector is 12
> times less "noisy" compared to a category 5e connector. This vast
> improvement in performance was achieved with new technology, new
> processes,
> better materials and significant R&D resources, leading to higher costs
> for
> manufacturers.
> 
> What will happen if I mix and match different manufacturers' hardware
> together?
> 
> If the components are category 6 compliant, then you will be assured of
> category 6 performance.


_______________________________________________
clug-talk mailing list
[email protected]
http://clug.ca/mailman/listinfo/clug-talk_clug.ca