Hi all,

to me "registerholder:34" isn't a valid Modbus address string (at least not for 
0.7.0)
Please have a look at the documentation for modbus connections here:
https://plc4x.apache.org/users/protocols/modbus.html

Chris

Am 27.05.20, 06:41 schrieb "venki hadoop" <[email protected]>:

    Thanks Cesar, will do the same. Not sure some one already tested Modbus
    driver to retrieve holding register data, if some one did plz let us know
    about this issue.        Regards,


    On Wednesday, May 27, 2020, Cesar Garcia <[email protected]> wrote:

    > Ok,
    >
    > For tomorrow I will take the time to test the new version and I will take 
a
    > step by step.
    >
    > Best regards,
    >
    > El mar., 26 may. 2020 a las 23:42, venki hadoop (<[email protected]>)
    > escribió:
    >
    > > Sure Cesar,
    > >                     was unable to attach my program due to size
    > > restrictions. But 1st am testing to retrieve holding resgister variable
    > > locally, then will in corporate into my logstash plugin I already
    > > implemented for OPC ua server signal simulator. Please find imp code:
    > > Builder.addItem("value","registerholder:34").
    > > Plcreadrequest req= builder.build().
    > >   plcreadresponse res=req.execute().get().
    > >  Val=res.getObject("value").
    > >  It's throwing me timeout exception while executing execute().get()
    > method.
    > > On Wednesday, May 27, 2020, Cesar Garcia <[email protected]>
    > wrote:
    > >
    > > > Hello,
    > > >
    > > > I'm glad it worked.
    > > >
    > > > Sure if you put your example code, we can help you test it.
    > > >
    > > > Best regards,
    > > >
    > > >
    > > > El mar., 26 may. 2020 a las 22:53, venki hadoop (<
    > [email protected]
    > > >)
    > > > escribió:
    > > >
    > > > > Hello Cesar,.
    > > > >                    Was able to configure device and signal function
    > > based
    > > > > on above instructions.
    > > > >  But am unable to retrieve value, am assuming due to version issue,
    > > today
    > > > > will update to 0.7.0 and test then will update you.
    > > > > Regards,
    > > > > On Tuesday, May 26, 2020, Cesar Garcia <[email protected]>
    > > wrote:
    > > > >
    > > > > > Hi,
    > > > > >
    > > > > > Please, you can use "karaf.bat" for startup.
    > > > > >
    > > > > > This way the console start.
    > > > > >
    > > > > > __  __                 _           _
    > > > > > |  \/  |   ___   _ __  | |   ___   | |_
    > > > > > | |\/| |  / _ \ | '__| | |  / _ \  | __|
    > > > > > | |  | | |  __/ | |    | | | (_) | | |_
    > > > > > |_|  |_|  \___| |_|    |_|  \___/   \__|
    > > > > >
    > > > > > Merlot Industrial Gateway (0.0.1-SNAPSHOT)
    > > > > >
    > > > > > Hit '<tab>' for a list of available commands
    > > > > > and '[cmd] --help' for help on a specific command.
    > > > > > Hit '<ctrl-d>' or type 'system:shutdown' or 'logout' to shutdown
    > > > Merlot.
    > > > > >
    > > > > > karaf@root()>
    > > > > >
    > > > > >
    > > > > > Karaf documentation can be found at https://karaf.apache.org
    > > > > >
    > > > > > If the console starts, the Modbus server is already active, so
    > Modbus
    > > > > > devices must be created.
    > > > > >
    > > > > > At the command line type
    > > > > >
    > > > > > karaf@root>modbus:new --help
    > > > > > karaf@root> modbus:new 10 test desc 1000 1000 1000 1000
    > > > > >
    > > > > > Then check the configuration file for the simulation of the 
records
    > > as
    > > > I
    > > > > > pointed out in the previous email.
    > > > > >
    > > > > > You must verify if the instance is active, since the option
    > > "start.bat"
    > > > > > starts as a service, which you must kill to avoid a problem with
    > the
    > > > > ports.
    > > > > >
    > > > > > Take a look at the concept here https://github.com/glcj/
    > Merlot/wiki,
    > > I
    > > > > > will
    > > > > > work on the documentation shortly.
    > > > > >
    > > > > > For tomorrow if you are online, we can use Google meet or other
    > tools
    > > > if
    > > > > > you follow the problems.
    > > > > >
    > > > > > Best regards,
    > > > > >
    > > > > >
    > > > > >
    > > > > >
    > > > > >
    > > > > > El mar., 26 may. 2020 a las 0:06, venki hadoop (<
    > > > [email protected]
    > > > > >)
    > > > > > escribió:
    > > > > >
    > > > > > > Hello Cesar,.
    > > > > > >                  Can you please provide me some information
    > > regarding
    > > > > how
    > > > > > > to start device, it's bit confusing.
    > > > >  I
    > > > > > > made necessary config changes in windows, then started using
    > > > start.bat
    > > > > > file
    > > > > > > from command line prompt. But nothing is happening. Please let 
me
    > > > know
    > > > > > what
    > > > > > > am doing is correct?
    > > > > > >                Thanks,
    > > > > > >
    > > > > > > On Tuesday, May 26, 2020, venki hadoop <[email protected]>
    > > > wrote:
    > > > > > >
    > > > > > > > Thanks Cesar, will test today, update status here.
    > > > > > > >
    > > > > > > > On Tuesday, May 26, 2020, Cesar Garcia <
    > [email protected]
    > > >
    > > > > > wrote:
    > > > > > > >
    > > > > > > >> Hi Venki,
    > > > > > > >>
    > > > > > > >> Sorry for the delay, the internet connection was spectacular,
    > > the
    > > > > ADSL
    > > > > > > >> very
    > > > > > > >> slow to download and very very & very slow to upload.
    > > > > > > >>
    > > > > > > >> Attach you will find the download links for the application,
    > the
    > > > > > version
    > > > > > > >> .zip (Windows) and .tar.gz (Linux)...
    > > > > > > >>
    > > > > > > >>
    > > > > > > https://mega.nz/file/nhVgxAQZ#M11oLJc-N5qDnbeF_
    > > > > > AhhsQk5ow9B3rPsIT2bt1ZORLc
    > > > > > > >>
    > > > > > > https://mega.nz/file/zocg0CyT#Pk5E9nRdM-
    > xdGNDSjAY9hl27pUpWgPDjdsO_
    > > > > > apCE6WQ
    > > > > > > >>
    > > > > > > >> 1.  You can add a Modbus device through the command line or
    > > > > > permanently
    > > > > > > in
    > > > > > > >> the configuration file *com.ceos.merlot.modbus.dev.cfg*. You
    > > can
    > > > > > > specify
    > > > > > > >> the number of elements you require (Coils, Input registers,
    > > etc.).
    > > > > > > >> 2. After creating the Modbus device, you can add the
    > simulation
    > > > > > > services,
    > > > > > > >> you have three:
    > > > > > > >> Random: Which simulates bits and scalars in a given range of
    > > > > > registers.
    > > > > > > >> Function: Perform simple math operations
    > > > > > > >> Signal: Generates continuous functions (Sinus, square,
    > > triangular
    > > > > and
    > > > > > > >> sawtooth).
    > > > > > > >> You can do this in the configuration file *
    > > > > > > com.ceos.merlot.modbus.sim.cf
    > > > > > > >> g*.
    > > > > > > >>
    > > > > > > >> The configuration files can be found in the 'etc' directory.
    > > > > > > >>
    > > > > > > >> In the case of the signals function, you can play with the
    > > > frequency
    > > > > > and
    > > > > > > >> phase registers, to adjust the signal to your sampling time.
    > > > Please
    > > > > > > don't
    > > > > > > >> forget our friend Nyquist.
    > > > > > > >>
    > > > > > > >> I'm going to spend some time on documentation.
    > > > > > > >>
    > > > > > > >> Chris, this is the tool I was telling you about to 
incorporate
    > > > into
    > > > > > the
    > > > > > > >> PLC4X project, if It meet the requirements of course.
    > > > > > > >>
    > > > > > > >> I hope you find it useful in testing with Modbus
    > > > > > > >>
    > > > > > > >> Best regards,...
    > > > > > > >>
    > > > > > > >>
    > > > > > > >>
    > > > > > > >>
    > > > > > > >>
    > > > > > > >> El vie., 22 may. 2020 a las 2:27, venki hadoop (<
    > > > > > [email protected]
    > > > > > > >)
    > > > > > > >> escribió:
    > > > > > > >>
    > > > > > > >> > Thanks  Cesar,.
    > > > > > > >> >                 Sure, will try immediately once it is
    > > available
    > > > > and
    > > > > > > will
    > > > > > > >> > give me feedback.
    > > > > > > >> >          Regards,
    > > > > > > >> >
    > > > > > > >> > On Friday, May 22, 2020, Cesar Garcia <
    > > [email protected]
    > > > >
    > > > > > > wrote:
    > > > > > > >> >
    > > > > > > >> > > Hi,
    > > > > > > >> > >
    > > > > > > >> > > Sorry,
    > > > > > > >> > >
    > > > > > > >> > > I misunderstood your email.
    > > > > > > >> > >
    > > > > > > >> > > You already tried from an OPC server, excellent.
    > > > > > > >> > >
    > > > > > > >> > > Remember me next week, I am going to implement the signal
    > > > > > simulator
    > > > > > > in
    > > > > > > >> > > Modbus so you can do your tests with the PLC4X driver.
    > > > > > > >> > >
    > > > > > > >> > > The important thing is that you give us feedback, on any
    > > point
    > > > > of
    > > > > > > >> > > improvement of the driver.
    > > > > > > >> > >
    > > > > > > >> > > Best regards,
    > > > > > > >> > >
    > > > > > > >> > > El jue., 21 may. 2020 a las 12:59, venki hadoop (<
    > > > > > > >> [email protected]
    > > > > > > >> > >)
    > > > > > > >> > > escribió:
    > > > > > > >> > >
    > > > > > > >> > > > Hello  Cesar,
    > > > > > > >> > > >                    I already tested with Modbus, but
    > want
    > > to
    > > > > > test
    > > > > > > >> with
    > > > > > > >> > > > streaming data ( data updated continuously) like how I
    > > > tested
    > > > > > > using
    > > > > > > >> OPC
    > > > > > > >> > > UA
    > > > > > > >> > > > server.  Was unable to get streaming data using Modbus
    > > > > > simulator.
    > > > > > > >> > > >                    Regards,
    > > > > > > >> > > >
    > > > > > > >> > > > On Thursday, May 21, 2020, Cesar Garcia <
    > > > > > [email protected]
    > > > > > > >
    > > > > > > >> > > wrote:
    > > > > > > >> > > >
    > > > > > > >> > > > >  Hello,
    > > > > > > >> > > > >
    > > > > > > >> > > > > Why don't you try Modbus first to try out the
    > different
    > > > > PLC4X
    > > > > > > >> tools.
    > > > > > > >> > > > >
    > > > > > > >> > > > > It is one of the simplest and most widely used
    > > protocols.
    > > > > > > >> > Additionally,
    > > > > > > >> > > > > Chris has made excellent documentation of the tools.
    > > > > > > >> > > > >
    > > > > > > >> > > > >
    > > https://plc4x.apache.org/users/plc4j/virtual-modbus.html
    > > > > > > >> > > > >
    > > > > > > >> > > > > As for the Siemens Software, you can use it for 15
    > days
    > > by
    > > > > > > >> > downloading
    > > > > > > >> > > it
    > > > > > > >> > > > > from its pages.
    > > > > > > >> > > > >
    > > > > > > >> > > > > My grain of sand,
    > > > > > > >> > > > >
    > > > > > > >> > > > > Happiness,
    > > > > > > >> > > > >
    > > > > > > >> > > > > El mié., 20 may. 2020 a las 12:13, venki hadoop (<
    > > > > > > >> > > [email protected]
    > > > > > > >> > > > >)
    > > > > > > >> > > > > escribió:
    > > > > > > >> > > > >
    > > > > > > >> > > > > > Hi Lukas, went through the video mentioned. But I
    > > didn't
    > > > > get
    > > > > > > >> which
    > > > > > > >> > > > > siemens
    > > > > > > >> > > > > > simulator they used for demo? Can some one let me
    > know
    > > > > free
    > > > > > > >> siemens
    > > > > > > >> > > s7
    > > > > > > >> > > > > plc
    > > > > > > >> > > > > > simulator for poc purpose?
    > > > > > > >> > > > > >
    > > > > > > >> > > > > > On Monday, May 18, 2020, Lukas Ott <
    > > > > [email protected]>
    > > > > > > >> wrote:
    > > > > > > >> > > > > >
    > > > > > > >> > > > > > > Hi Venki welcome to the PLC4X community,
    > > > > > > >> > > > > > >
    > > > > > > >> > > > > > > First direction we can point you to is the 
webinar
    > > > from
    > > > > > > >> Julian:
    > > > > > > >> > > > > > > https://youtu.be/MIp_0OcDTr4 There he shows in
    > > detail
    > > > > how
    > > > > > > to
    > > > > > > >> > > connect
    > > > > > > >> > > > > > > Siemens PLCs to PLC4X.
    > > > > > > >> > > > > > > Additionally he shows you how to connect to a
    > > > simulated
    > > > > > PLC
    > > > > > > >> > server
    > > > > > > >> > > > > which
    > > > > > > >> > > > > > is
    > > > > > > >> > > > > > > maybe what you are looking for to test and 
develop
    > > > your
    > > > > > > >> > application
    > > > > > > >> > > > > with
    > > > > > > >> > > > > > > the Kafka connector.
    > > > > > > >> > > > > > >
    > > > > > > >> > > > > > > Best regards,
    > > > > > > >> > > > > > > Lukas
    > > > > > > >> > > > > > >
    > > > > > > >> > > > > > > Am Mo., 18. Mai 2020 um 16:04 Uhr schrieb venki
    > > > hadoop <
    > > > > > > >> > > > > > > [email protected]>:
    > > > > > > >> > > > > > >
    > > > > > > >> > > > > > > > ---------- Forwarded message ----------
    > > > > > > >> > > > > > > > From: *venki hadoop* <[email protected]>
    > > > > > > >> > > > > > > > Date: Saturday, May 16, 2020
    > > > > > > >> > > > > > > > Subject: Exploring Plc4x
    > > > > > > >> > > > > > > > To: [email protected]
    > > > > > > >> > > > > > > > Cc: [email protected]
    > > > > > > >> > > > > > > >
    > > > > > > >> > > > > > > >
    > > > > > > >> > > > > > > > Hello Everyone,
    > > > > > > >> > > > > > > >                  Am a big data/cloud architect
    > > > working
    > > > > > on
    > > > > > > >> > > analytics
    > > > > > > >> > > > > > from
    > > > > > > >> > > > > > > > India. Was working in IOT industry since 2 
years
    > > > with
    > > > > > > >> different
    > > > > > > >> > > > > clients
    > > > > > > >> > > > > > > but
    > > > > > > >> > > > > > > > mostly on analytics side than machine side.
    > > Recently
    > > > > > when
    > > > > > > >> > > exploring
    > > > > > > >> > > > > > about
    > > > > > > >> > > > > > > > IIOT got to know about plc4x tool. Since then
    > > trying
    > > > > to
    > > > > > > >> explore
    > > > > > > >> > > and
    > > > > > > >> > > > > > > present
    > > > > > > >> > > > > > > > to larger audience in my company if it suits 
our
    > > > > > > >> requirements.
    > > > > > > >> > > > > > > >
    > > > > > > >> > So
    > > > > > > >> > > > > what
    > > > > > > >> > > > > > am
    > > > > > > >> > > > > > > > planning right now is :
    > > > > > > >> > > > Read
    > > > > > > >> > > > > > > > streaming data from siemens device and push it
    > > Kafka
    > > > > > from
    > > > > > > >> there
    > > > > > > >> > > > > > > dashboard.
    > > > > > > >> > > > > > > > From examples provided in documentation was 
able
    > > to
    > > > > > easily
    > > > > > > >> > > > correlate
    > > > > > > >> > > > > > > > pushing data into Kafka and afterwards.  But as
    > I
    > > > > don't
    > > > > > > have
    > > > > > > >> > any
    > > > > > > >> > > > > > > experience
    > > > > > > >> > > > > > > > it's hard to understand for me about the device
    > > > > > > >> configuration
    > > > > > > >> > and
    > > > > > > >> > > > > > > > integrating with plc4x( I know this are basic
    > plc
    > > > > > > questions,
    > > > > > > >> > > please
    > > > > > > >> > > > > > bear
    > > > > > > >> > > > > > > me
    > > > > > > >> > > > > > > > with me for some time). Now in order to start 
my
    > > > poc,
    > > > > I
    > > > > > > need
    > > > > > > >> > > > > fallowing
    > > > > > > >> > > > > > > > information. Can someone help me on this.
    > > > 1.
    > > > > > Any
    > > > > > > >> > siemens
    > > > > > > >> > > > plc
    > > > > > > >> > > > > > > > device simulator for poc?
    >  2.
    > > > > What
    > > > > > > >> > > > configuration
    > > > > > > >> > > > > > we
    > > > > > > >> > > > > > > > need and we have to check from plc side(
    > assuming
    > > I
    > > > > have
    > > > > > > >> some
    > > > > > > >> > > > > > temperature
    > > > > > > >> > > > > > > > kind of sensor).
    > > > > > > >> > > > > > > >                       3. How to point to plc
    > > output
    > > > > data
    > > > > > > >> from
    > > > > > > >> > > Kafka
    > > > > > > >> > > > > > > > connect?( Was confused with memory blocks,
    > fields,
    > > > etc
    > > > > > in
    > > > > > > >> the
    > > > > > > >> > > > code).
    > > > > > > >> > > > > > > >
    > > > > > > >> > > > > > > >      I know this are very basic questions from
    > plc
    > > > > side,
    > > > > > > >> but my
    > > > > > > >> > > no
    > > > > > > >> > > > > > > > experience with plc side make me hard to
    > > understand
    > > > > > using
    > > > > > > >> > Google.
    > > > > > > >> > > > > > > >
    > > Last
    > > > > but
    > > > > > > not
    > > > > > > >> > > least,
    > > > > > > >> > > > > > thanks
    > > > > > > >> > > > > > > > Christofer for introducing me for this platform
    > > and
    > > > > > plc4x
    > > > > > > >> tool.
    > > > > > > >> > > > > > > >                                    Best 
Regards,
    > > > > > > >> > > > > > > >
    > > > > > > >> > > > > > >
    > > > > > > >> > > > > >
    > > > > > > >> > > > >
    > > > > > > >> > > > >
    > > > > > > >> > > > > --
    > > > > > > >> > > > > *CEOS Automatización, C.A.*
    > > > > > > >> > > > > *GALPON SERVICIO INDUSTRIALES Y NAVALES FA, C.A.,*
    > > > > > > >> > > > > *PISO 1, OFICINA 2, AV. RAUL LEONI, SECTOR
    > GUAMACHITO,*
    > > > > > > >> > > > >
    > > > > > > >> > > > > *FRENTE A LA ASOCIACION DE GANADEROS,BARCELONA,EDO.
    > > > > > ANZOATEGUI*
    > > > > > > >> > > > > *Ing. César García*
    > > > > > > >> > > > >
    > > > > > > >> > > > > *Cel: +58 414-760.98.95*
    > > > > > > >> > > > >
    > > > > > > >> > > > > *Hotline Técnica SIEMENS: 0800 1005080*
    > > > > > > >> > > > >
    > > > > > > >> > > > > *Email: [email protected]
    > > > > > > >> > > > > <[email protected]>*
    > > > > > > >> > > > >
    > > > > > > >> > > >
    > > > > > > >> > >
    > > > > > > >> > >
    > > > > > > >> > > --
    > > > > > > >> > > *CEOS Automatización, C.A.*
    > > > > > > >> > > *GALPON SERVICIO INDUSTRIALES Y NAVALES FA, C.A.,*
    > > > > > > >> > > *PISO 1, OFICINA 2, AV. RAUL LEONI, SECTOR GUAMACHITO,*
    > > > > > > >> > >
    > > > > > > >> > > *FRENTE A LA ASOCIACION DE GANADEROS,BARCELONA,EDO.
    > > > ANZOATEGUI*
    > > > > > > >> > > *Ing. César García*
    > > > > > > >> > >
    > > > > > > >> > > *Cel: +58 414-760.98.95*
    > > > > > > >> > >
    > > > > > > >> > > *Hotline Técnica SIEMENS: 0800 1005080*
    > > > > > > >> > >
    > > > > > > >> > > *Email: [email protected]
    > > > > > > >> > > <[email protected]>*
    > > > > > > >> > >
    > > > > > > >> >
    > > > > > > >>
    > > > > > > >>
    > > > > > > >> --
    > > > > > > >> *CEOS Automatización, C.A.*
    > > > > > > >> *GALPON SERVICIO INDUSTRIALES Y NAVALES FA, C.A.,*
    > > > > > > >> *PISO 1, OFICINA 2, AV. RAUL LEONI, SECTOR GUAMACHITO,*
    > > > > > > >>
    > > > > > > >> *FRENTE A LA ASOCIACION DE GANADEROS,BARCELONA,EDO.
    > ANZOATEGUI*
    > > > > > > >> *Ing. César García*
    > > > > > > >>
    > > > > > > >> *Cel: +58 414-760.98.95*
    > > > > > > >>
    > > > > > > >> *Hotline Técnica SIEMENS: 0800 1005080*
    > > > > > > >>
    > > > > > > >> *Email: [email protected]
    > > > > > > >> <[email protected]>*
    > > > > > > >>
    > > > > > > >
    > > > > > >
    > > > > >
    > > > > >
    > > > > > --
    > > > > > *CEOS Automatización, C.A.*
    > > > > > *GALPON SERVICIO INDUSTRIALES Y NAVALES FA, C.A.,*
    > > > > > *PISO 1, OFICINA 2, AV. RAUL LEONI, SECTOR GUAMACHITO,*
    > > > > >
    > > > > > *FRENTE A LA ASOCIACION DE GANADEROS,BARCELONA,EDO. ANZOATEGUI*
    > > > > > *Ing. César García*
    > > > > >
    > > > > > *Cel: +58 414-760.98.95*
    > > > > >
    > > > > > *Hotline Técnica SIEMENS: 0800 1005080*
    > > > > >
    > > > > > *Email: [email protected]
    > > > > > <[email protected]>*
    > > > > >
    > > > >
    > > >
    > > >
    > > > --
    > > > *CEOS Automatización, C.A.*
    > > > *GALPON SERVICIO INDUSTRIALES Y NAVALES FA, C.A.,*
    > > > *PISO 1, OFICINA 2, AV. RAUL LEONI, SECTOR GUAMACHITO,*
    > > >
    > > > *FRENTE A LA ASOCIACION DE GANADEROS,BARCELONA,EDO. ANZOATEGUI*
    > > > *Ing. César García*
    > > >
    > > > *Cel: +58 414-760.98.95*
    > > >
    > > > *Hotline Técnica SIEMENS: 0800 1005080*
    > > >
    > > > *Email: [email protected]
    > > > <[email protected]>*
    > > >
    > >
    >
    >
    > --
    > *CEOS Automatización, C.A.*
    > *GALPON SERVICIO INDUSTRIALES Y NAVALES FA, C.A.,*
    > *PISO 1, OFICINA 2, AV. RAUL LEONI, SECTOR GUAMACHITO,*
    >
    > *FRENTE A LA ASOCIACION DE GANADEROS,BARCELONA,EDO. ANZOATEGUI*
    > *Ing. César García*
    >
    > *Cel: +58 414-760.98.95*
    >
    > *Hotline Técnica SIEMENS: 0800 1005080*
    >
    > *Email: [email protected]
    > <[email protected]>*
    >

Reply via email to