Hi Iñigo,

happy you made quite some progress.

If you were asking yourself why for BYTE, WORD and DWORD the driver is 
returning a List ... these are considered Bit-Strings. If you want to 
read/write a single byte as an integer value, please use SINT instead.

So regarding one of your questions ... could you instead of doing: 
        builderWriter.addItem("mivariable", "%DB20:DBB06:BYTE", 127);
Please try:
        builderWriter.addItem("mivariable", "%DB20:DBB06:SINT", 127);

And if you're getting an INTERNAL_ERROR that's probably our fault. As I 
mentioned, we haven't done too much writing as no one ever uses that ;-)

Chris




Am 02.07.20, 15:56 schrieb "Iñigo Angulo" <[email protected]>:

    Hi,

    I have been doing further tests with the S7 driver. I would like to ask you 
some doubts, which i am not sure if relate to the PLC4X driver or the actual 
hardware (Siemens S7-300) i am using (pretty novice in PLC data access im 
afraid...)


    The "Read value" tests I have done work correctly for different datatypes, 
for example:

        builderReader.addItem("mivariable", "%DB20:DBX5.0:BOOL"); //Single 
boolean value
        builderReader.addItem("mivariable", "%DB20:DBB06:BYTE"); //returns a 
PlcList (Array of 8 boolean values)
        builderReader.addItem("mivariable", "%DB20:DBW06:WORD"); //returns a 
PlcList (Array of 16 boolean values)
        builderReader.addItem("mivariable", "%DB20:DBD06:DWORD"); //returns a 
PlcList (Array of 32 boolean values)
        builderReader.addItem("mivariable", "%DB20:DBW06:INT"); //returns a 
PlcInteger (16 bit integer (signed))
        builderReader.addItem("mivariable", "%DB20:DBD06:DINT"); //returns a 
PlcInteger (32 bit integer (signed))
        builderReader.addItem("mivariable", "%DB20:DBD06:REAL"); //returns a 
PlcFloat (32 bit IEEE 754 full precision floating point value (signed))


    In the "Write value" tests, write request for all datatype seem to work 
fine:

        builderWriter.addItem("mivariable", "%DB20:DBX6.1:BOOL", true); //write 
response code "OK"
        builderWriter.addItem("mivariable", "%DB20:DBB06:BYTE", 127); //write 
response code "OK"
        builderWriter.addItem("mivariable", "%DB20:DBW06:WORD", 7); //write 
response code "OK"
        builderWriter.addItem("mivariable", "%DB20:DBD06:DWORD", 1); //write 
response code "OK"


    Except for the 'INT' and 'DINT' datatypes, which return an INTERNAL_ERROR 
response code

        builderWriter.addItem("mivariable", "%DB20:DBW06:INT", 1); //write 
response code "INTERNAL_ERROR"
        builderWriter.addItem("mivariable", "%DB20:DBD06:DINT", 1); //write 
response code "INTERNAL_ERROR"


    Is the INTERNAL_ERROR code a hardware issue? (Maybe a device configuration 
problem?)

    ---

    Also, the other thing I found in the test:

    When I write a value different than BOOL, and then read the same memory 
address, I dont get the actual value but a 'false' filled array. TO give some 
examples,

    with BOOL values:

        builderWriter.addItem("mivariable", "%DB20:DBX6.1:BOOL", true); 
        builderReader.addItem("mivariable", "%DB20:DBX6.1:BOOL"); //return true

        builderWriter.addItem("mivariable", "%DB20:DBX6.1:BOOL", false); 
        builderReader.addItem("mivariable", "%DB20:DBX6.1:BOOL"); //return false

    The written value is "correctly updated" and read fine.

    with other datatypes:

        builderWriter.addItem("mivariable", "%DB20:DBB06:BYTE", 1);
        builderReader.addItem("mivariable", "%DB20:DBB06:BYTE"); //returns 
[false, false, false, false, false, false, false, false]

        builderWriter.addItem("mivariable", "%DB20:DBB06:BYTE", 127);
        builderReader.addItem("mivariable", "%DB20:DBB06:BYTE"); //returns 
[false, false, false, false, false, false, false, false]


    I have tried to combine write single bits and read other datatypes, which 
seem to work fine:

        builderWriter.addItem("mivariable", "%DB20:DBX6.1:BOOL", true);
            builderReader.addItem("mivariable", "%DB20:DBB06:BYTE"); //returns 
[false, false, false, false, false, false, true, false]
        builderReader.addItem("mivariable", "%DB20:DBW06:INT"); //return 512

    And the other way around, write a byte and read single bits

        builderWriter.addItem("mivariable", "%DB20:DBB06:BYTE", 127);
        builderReader.addItem("mivariable-0", "%DB20:DBX6.0:BOOL"); //returns 
false
        builderReader.addItem("mivariable-1", "%DB20:DBX6.1:BOOL"); //returns 
false
        builderReader.addItem("mivariable-2", "%DB20:DBX6.2:BOOL"); //returns 
false
        builderReader.addItem("mivariable-3", "%DB20:DBX6.3:BOOL"); //returns 
false
        builderReader.addItem("mivariable-4", "%DB20:DBX6.4:BOOL"); //returns 
false
        builderReader.addItem("mivariable-5", "%DB20:DBX6.5:BOOL"); //returns 
false
        builderReader.addItem("mivariable-6", "%DB20:DBX6.6:BOOL"); //returns 
false
        builderReader.addItem("mivariable-7", "%DB20:DBX6.7:BOOL"); //returns 
false

    Which leads me to think that could be a write issue, right?

    Again I understand that these issues could be an actual hardware 
configuration problem.. but any help or advice would be much appreciated

    Thank you in advance!

    iñigo 

    P.S. I attached the test classes if anyone wants to take a look.

    ----------------------------------------- 
    Iñigo Angulo 

    ZYLK.net :: consultoría.openSource 
    Ribera de Axpe, 11 
    Edificio A, modulo 201-203 
    48950 Erandio (Bizkaia) 
    +34 944272119 
    -----------------------------------------

    ----- Mensaje original -----
    De: "Iñigo Angulo Otegui" <[email protected]>
    Para: "dev" <[email protected]>
    Enviados: Jueves, 2 de Julio 2020 12:45:49
    Asunto: Re: S7 write test doubt

    Hi Julian,

    Yes, we saw the adopters page and were thinking to contribute there. We 
will prepare a short text describing the work we are doing with the project and 
send it to you soon.

    Thanks 
    iñigo

    ----------------------------------------- 
    Iñigo Angulo 

    ZYLK.net :: consultoría.openSource 
    Ribera de Axpe, 11 
    Edificio A, modulo 201-203 
    48950 Erandio (Bizkaia) 
    +34 944272119 
    -----------------------------------------

    ----- Mensaje original -----
    De: "Julian Feinauer" <[email protected]>
    Para: "dev" <[email protected]>
    Enviados: Jueves, 2 de Julio 2020 12:00:53
    Asunto: Re: S7 write test doubt

    And, as i shortly checked your company profile which looks pretty cool... 
if you like it, or use it, dont forget to enter your company on the adopters 
page : )

    https://plc4x.apache.org/users/adopters.html

    Julian

    Am 02.07.20, 10:31 schrieb "Iñigo Angulo" <[email protected]>:

        Hi Chris,

        Yes, using the 0.8.0-SNAPSHOT with the update you did the problem is 
solved now. 

        Thank you for the help and the fast solution!

        Iñigo

        ----------------------------------------- 
        Iñigo Angulo 

        ZYLK.net :: consultoría.openSource 
        Ribera de Axpe, 11 
        Edificio A, modulo 201-203 
        48950 Erandio (Bizkaia) 
        +34 944272119 
        -----------------------------------------

        ----- Mensaje original -----
        De: "Christofer Dutz" <[email protected]>
        Para: "dev" <[email protected]>
        Enviados: Miércoles, 1 de Julio 2020 13:18:34
        Asunto: Re: S7 write test doubt

        Hi all,

        build passed locall, pushed the changes, build on ci passed .... so you 
should be ready to give things a new try.

        However keep in mind, if you built with 0.8.0-SNAPSHOT once today, 
please be sure to do a "mvn -U install" build or you won't get the update today.

        Would be cool if you could reply if this helped.

        Chris



        Am 01.07.20, 12:30 schrieb "Julian Feinauer" 
<[email protected]>:

            Thanks both of you!
            As I just wrote in Slack we can only grow and improve if we get 
feedback, Bug reports and usage scenarios.
            And of course thanks Chris for that fast reply and fix <3

            Julian

            Am 01.07.20, 12:24 schrieb "Iñigo Angulo" <[email protected]>:

                Hi Chris,

                No problem. I will keep track of the issue in Jira, and use the 
0.8.0-SNAPSHOT version.

                Thank you for your help

                iñigo

                ----------------------------------------- 
                Iñigo Angulo 

                ZYLK.net :: consultoría.openSource 
                Ribera de Axpe, 11 
                Edificio A, modulo 201-203 
                48950 Erandio (Bizkaia) 
                +34 944272119 
                -----------------------------------------

                ----- Mensaje original -----
                De: "Christofer Dutz" <[email protected]>
                Para: "dev" <[email protected]>
                Enviados: Miércoles, 1 de Julio 2020 12:06:28
                Asunto: Re: S7 write test doubt

                Hi Iñigo,

                I will have to ask you to wait for a little while as you 
stumbled over a problem which goes a little deeper and is related to a major 
refactoring we did just before Christmas. I am pretty puzzled that no one ever 
noticed this, but I'll immediately start working on fixing this.

                I'm tracking progress here: 
                https://issues.apache.org/jira/browse/PLC4X-206


                If that's done I would like to ask you to use the 
0.8.0-SNAPSHOT till we've released the next version of PLC4X.

                Chris


                Am 01.07.20, 12:00 schrieb "Iñigo Angulo" <[email protected]>:

                    Hi Chris,

                    Thanks for the fast answer!

                    I will keep your advice about not adding the cast to the 
values, and letting the driver do its work.

                    If you want me to try to reproduce any other test just let 
me know.

                    Iñigo


                    ----------------------------------------- 
                    Iñigo Angulo 

                    ZYLK.net :: consultoría.openSource 
                    Ribera de Axpe, 11 
                    Edificio A, modulo 201-203 
                    48950 Erandio (Bizkaia) 
                    +34 944272119 
                    -----------------------------------------

                    ----- Mensaje original -----
                    De: "Christofer Dutz" <[email protected]>
                    Para: "dev" <[email protected]>
                    Enviados: Miércoles, 1 de Julio 2020 11:48:48
                    Asunto: Re: S7 write test doubt

                    And let me give you a little more context ... with the INT 
type in S7 you happen to know that there an INT is a 16 Bit signed integer.

                    We wanted to abstract from that. Cause another PLC could 
define INT as 32 bit integer ... So you can generally just work with any 
numeric type and pass that in. The driver will inspect the value ranges for 
that particular protocol and give some sensible error messages (At least it 
should ;-) ).

                    But ... I just noticed that indeed I am seeing the same 
problems you are seeing and that my suggestion just causes a different error 
... I'll get working on fixing this right away.

                    I'm really a bit confused about this ... but it does prove 
that most people just care about reading ;-)

                    Will keep you and the others posted on any progress.

                    Chris



                    Am 01.07.20, 11:33 schrieb "Christofer Dutz" 
<[email protected]>:

                        Hi Iñigo,

                        welcome to the party ... I really hope we'll be able to 
get you started asap ...

                        I just had a look at the code and PlcInteger does have 
the constructor ...

                            public PlcInteger(Short value) {
                                super(value.intValue(), true);
                            }

                        So I'll try to reproduce the problem ... but for now 
... could you just remove the cast from your items?

                            builderWriter.addItem("mivariable-1", 
"%DB20:DBX6.7:BOOL", true); 
                            builderWriter.addItem("mivariable-4", 
"%DB20:DBW06.0:INT", 2);
                            builderWriter.addItem("mivariable-2", 
"%DB20:DBB06:BYTE", 0);

                        Cause PLC4X internally already ensures everything fits 
into the bounds and internally PLC4X handles the "(short) 2" as an "(int) 2" 
anyway ;-)


                        Chris




                        Am 01.07.20, 11:19 schrieb "Iñigo Angulo" 
<[email protected]>:

                            Hi, 

                            I started doing some basic tests with the S7 
protocol using a Siemens S7-300, and the latest 0.7.0 release. The tests 
consist of reading and writing several DB variables. I was able to read 
different datatypes, for instance: 

                            builder.addItem("mivariable-1", 
"%DB20:DBX05.0:BOOL"); 
                            builder.addItem("mivariable-4", "%DB20:DBW06:INT"); 

                            However, when I try to write the same memory 
addresses I only manage to write BOOL values, for example 

                            builderWriter.addItem("mivariable-1", 
"%DB20:DBX6.7:BOOL", true); //WORKS OK 
                            builderWriter.addItem("mivariable-4", 
"%DB20:DBW06.0:INT", (short)2); // FAILS 
                            builderWriter.addItem("mivariable-2", 
"%DB20:DBB06:BYTE", (byte)0); // FAILS 

                            I am unable to write any datatype different than 
BOOL. 

                            I am facing the following Error message: 

                            Exception in thread "main" 
org.apache.plc4x.java.api.exceptions.PlcRuntimeException: Error initializing 
field class PlcInteger 
                            at 
org.apache.plc4x.java.s7.readwrite.field.S7PlcFieldHandler.internalEncodeInteger(S7PlcFieldHandler.java:394)
 
                            at 
org.apache.plc4x.java.s7.readwrite.field.S7PlcFieldHandler.encodeShort(S7PlcFieldHandler.java:86)
 
                            at 
org.apache.plc4x.java.spi.messages.DefaultPlcWriteRequest$Builder.lambda$build$0(DefaultPlcWriteRequest.java:270)
 
                            at 
java.base/java.util.TreeMap.forEach(TreeMap.java:1002) 
                            at 
org.apache.plc4x.java.spi.messages.DefaultPlcWriteRequest$Builder.build(DefaultPlcWriteRequest.java:265)
 
                            at 
net.zylk.plc4x.test.protocols.WriteS7.main(WriteS7.java:102) 
                            Caused by: java.lang.NoSuchMethodException: 
org.apache.plc4x.java.api.value.PlcInteger.<init>([Ljava.lang.Short;) 
                            at 
java.base/java.lang.Class.getConstructor0(Class.java:3349) 
                            at 
java.base/java.lang.Class.getDeclaredConstructor(Class.java:2553) 
                            at 
org.apache.plc4x.java.s7.readwrite.field.S7PlcFieldHandler.internalEncodeInteger(S7PlcFieldHandler.java:392)
 
                            ... 5 more 

                            Maybe I am misunderstanding the sintax and how the 
values should be written? 

                            --- 
                            To try to offer some more information about this 
error: 
                            Digging into that class (S7PlcFieldHandler) I saw 
that there are some fields that are initialized based on the value of the 
datatype 

                            case INT: 
                            minValue = BigInteger.valueOf(Short.MIN_VALUE); 
                            maxValue = BigInteger.valueOf(Short.MAX_VALUE); 
                            fieldType = PlcInteger.class; 
                            valueType = Short[].class; 
                            castedValues = new Short[values.length]; 
                            break; 

                            Then, the line that throws the Exception seems to 
be trying to inferr a PlcInteger class constructor based on the datatype 

                            // Create the field item. 
                            try { 
                            return 
fieldType.getDeclaredConstructor(valueType).newInstance(castedValues); 
                            } catch (InstantiationException | 
IllegalAccessException | InvocationTargetException | NoSuchMethodException e) { 
                            throw new PlcRuntimeException("Error initializing 
field class " + fieldType.getSimpleName(), e); 
                            } 

                            However there appears to be a "mismatch" between 
the valueType (Short[]) and the constructor (Short) in the PlcInteger class, 
which leads me to think i am missing something on the write value sintax? 

                            Thank you in advance, any help will be welcome. 

                            Iñigo 



                            ----- 
                            the test class code: 

                            public class WriteS7 { 
                            private static final Logger _log = 
LoggerFactory.getLogger(WriteS7.class); 

                            public static void main(String[] args) throws 
PlcConnectionException { 

                            String connectionString = 
"s7://10.105.143.1:102?remote-rack=0&remote-slot=0&controller-type=S7_300"; 

                            _log.info(String.format("Establishing connection to 
%s", connectionString));; 

                            try (PlcConnection plcConnection = new 
PlcDriverManager().getConnection(connectionString)) { 
                            _log.info("Conecting... " + connectionString); 
                            if (!plcConnection.getMetadata().canWrite()) { 
                            _log.error(String.format("Connection %s doesn't 
support writing.", connectionString)); 
                            return; 
                            } 

                            PlcWriteRequest.Builder builderWriter = null; 
                            builderWriter = 
plcConnection.writeRequestBuilder(); 

                            // builderWriter.addItem("mivariable-26", 
"%DB20:DBX6.7:BOOL", false); //OK 
                            builderWriter.addItem("mivariable-2", 
"%DB20:DBB06:BYTE", (byte)0); //FAILS 
                            // builderWriter.addItem("mivariable-4", 
"%DB20:DBW06.0:INT", (short)2); //FAILS 


                            PlcWriteRequest writeRequest = 
builderWriter.build(); 
                            PlcWriteResponse writeResponse = 
writeRequest.execute().get(); 

                            
GeneralFunctions.printPlc4XWriteReponse(writeResponse); //print response 
                            } 

                            } 
                            } 


                            ----------------------------------------- 
                            Iñigo Angulo 

                            ZYLK.net :: consultoría.openSource 
                            Ribera de Axpe, 11 
                            Edificio A, modulo 201-203 
                            48950 Erandio (Bizkaia) 
                            +34 944272119 
                            -----------------------------------------

Reply via email to