Thanks you guys !!!!

I have downloaded and compiled the develop code and now I cloud read the
INT array without any problem!

You are managing a great project with a great support !!!

Thanks,
Stefano


On 02/08/2020 21:08, Julian Feinauer wrote:
> Hi,
>
> sorry for the delayed working on it but I just took a look and think I fixed 
> the issue.
>
> It seems that arrays where not properly implemented in the S7 Driver (?).
>
> I opened up a PR (https://github.com/apache/plc4x/pull/175) and hope that 
> @Christofer Dutz finds some time to have a quick look (as he did most of the 
> work there) and merge it, if he agrees with it.
>
> If you could try out the branch and give your feedback I would be happy.
>
> Thanks for the excellent preparation of work! : )
>
> Julian
>
> Am 02.08.20, 20:40 schrieb "Julian Feinauer" <j.feina...@pragmaticminds.de>:
>
>     Hi,
>
>     I'm looking into it : )
>
>     J
>
>     Am 01.08.20, 16:17 schrieb "Christofer Dutz" <christofer.d...@c-ware.de>:
>
>         Hi Stefano,
>
>         I think such a Jira would be a good idea.
>
>         I’m currently working on the Beckhoff ADS and would try to have a 
> look as soon as possible.
>
>         Chris
>
>
>
>         Von: Stefano Bossi <stefano.bo...@gmail.com>
>         Antworten an: <dev@plc4x.apache.org>
>         Datum: Samstag, 1. August 2020 um 11:25
>         An: <dev@plc4x.apache.org>, Julian Feinauer 
> <j.feina...@pragmaticminds.de>
>         Betreff: Re: Reading Array of Int
>
>         Hi julian,
>
>         if you need or think could simplify the development I could open a 
> jira ticket and upload a couple of pcap capture for you.
>
>         As I wrote I am using the 0.7.0 version from Maven and I am talking 
> with a real Siemens 1200 with firmware 1.2 (pretty old but I didn't find a 
> way to upgrade it ).
>
>         Let me know.
>
>         Thanks for help.
>
>         Regards,
>         Stefano
>
>         On 30/07/2020 07:49, Julian Feinauer wrote:
>
>         Hey Stefano, I will try to have a look later today. Are you using 
> plc4x version 0.6 or 0.7?
>
>
>
>         Thank you!
>
>
>
>         Julian
>
>
>
>         Holen Sie sich Outlook für 
> Android<https://aka.ms/ghei36><https://aka.ms/ghei36>
>
>
>
>         ________________________________
>
>         Von: Stefano Bossi 
> <stefano.bo...@gmail.com><mailto:stefano.bo...@gmail.com>
>
>         Gesendet: Mittwoch, 29. Juli 2020, 12:32
>
>         An: dev@plc4x.apache.org<mailto:dev@plc4x.apache.org>; Christofer Dutz
>
>         Betreff: Re: Reading Array of Int
>
>
>
>         Thanks Chris,
>
>
>
>         yes definitely this is a workaround, I am experimenting and learning.
>
>
>
>         I really appreciate your time on the investigation of the issue.
>
>
>
>         Thanks,
>
>         Stefano Bossi
>
>
>
>
>
>
>
>         On 29/07/2020 12:08, Christofer Dutz wrote:
>
>
>
>         Well that’s a workaround, but not a fix …
>
>
>
>         We should focus on fixing this.
>
>
>
>         I’ll investigate the issue as soon as I’m done with the Beckhoff 
> ADS/AMS stuff …
>
>
>
>         Perhaps Julian could find some time to investigate?
>
>
>
>         Chris
>
>
>
>
>
>
>
>         Von: Stefano Bossi 
> <stefano.bo...@gmail.com><mailto:stefano.bo...@gmail.com><mailto:stefano.bo...@gmail.com><mailto:stefano.bo...@gmail.com>
>
>         Antworten an: 
> <dev@plc4x.apache.org><mailto:dev@plc4x.apache.org><mailto:dev@plc4x.apache.org><mailto:dev@plc4x.apache.org>
>
>         Datum: Mittwoch, 29. Juli 2020 um 11:41
>
>         An: 
> <dev@plc4x.apache.org><mailto:dev@plc4x.apache.org><mailto:dev@plc4x.apache.org><mailto:dev@plc4x.apache.org>
>
>         Betreff: Re: Reading Array of Int
>
>
>
>
>
>         I have adopted a workaround reading all the INT variable separated.
>
>
>
>         --connection-string 's7:tcp://192.168.1.192?controller-type=S7_1200' 
> --field-addresses '%DB1:274.0:INT' '%DB1:276.0:INT' '%DB1:278.0:INT' 
> '%DB1:280.0:INT'
>
>
>
>         In this way on the wire you have:
>
>         the query:
>
>
>
>         Frame 296: 111 bytes on wire (888 bits), 111 bytes captured (888 
> bits) on interface utun2, id 0
>
>
>
>         Null/Loopback
>
>
>
>         Internet Protocol Version 4, Src: 192.168.100.4, Dst: 192.168.1.192
>
>
>
>         Transmission Control Protocol, Src Port: 57188, Dst Port: 102, Seq: 
> 48, Ack: 50, Len: 67
>
>
>
>         TPKT, Version: 3, Length: 67
>
>
>
>         ISO 8073/X.224 COTP Connection-Oriented Transport Protocol
>
>
>
>         S7 Communication
>
>
>
>             Header: (Job)
>
>
>
>             Parameter: (Read Var)
>
>
>
>                 Function: Read Var (0x04)
>
>
>
>                 Item count: 4
>
>
>
>                 Item [1]: (DB 1.DBX 274.0 INT 1)
>
>
>
>                 Item [2]: (DB 1.DBX 276.0 INT 1)
>
>
>
>                 Item [3]: (DB 1.DBX 278.0 INT 1)
>
>
>
>                 Item [4]: (DB 1.DBX 280.0 INT 1)
>
>
>
>         the answer:
>
>
>
>         Frame 297: 89 bytes on wire (712 bits), 89 bytes captured (712 bits) 
> on interface utun2, id 0
>
>
>
>         Null/Loopback
>
>
>
>         Internet Protocol Version 4, Src: 192.168.1.192, Dst: 192.168.100.4
>
>
>
>         Transmission Control Protocol, Src Port: 102, Dst Port: 57188, Seq: 
> 50, Ack: 115, Len: 45
>
>
>
>         TPKT, Version: 3, Length: 45
>
>
>
>         ISO 8073/X.224 COTP Connection-Oriented Transport Protocol
>
>
>
>         S7 Communication
>
>
>
>             Header: (Ack_Data)
>
>
>
>             Parameter: (Read Var)
>
>
>
>                 Function: Read Var (0x04)
>
>
>
>                 Item count: 4
>
>
>
>             Data
>
>
>
>                 Item [1]: (Success)
>
>
>
>                 Item [2]: (Success)
>
>
>
>                 Item [3]: (Success)
>
>
>
>                 Item [4]: (Success)
>
>
>
>         [INFO ] 10:15:44.727 it.fox.datapicker.HelloPlc4x.printResponse() - 
> Value[value-0]: 10
>
>
>
>         [INFO ] 10:15:44.733 it.fox.datapicker.HelloPlc4x.printResponse() - 
> Value[value-1]: 11
>
>
>
>         [INFO ] 10:15:44.737 it.fox.datapicker.HelloPlc4x.printResponse() - 
> Value[value-2]: 12
>
>
>
>         [INFO ] 10:15:44.741 it.fox.datapicker.HelloPlc4x.printResponse() - 
> Value[value-3]: 13
>
>
>
>         Unfortunately my java knowledge are not so advanced to fix the bug in 
> reading the array in a single command, anyway there’s a workaround.
>
>
>
>         Hope this mail help some newbies like me to find the right way to 
> read data from the PLC.
>
>
>
>         Regards,
>
>         Stefano
>
>
>
>         On 28/07/2020 11:38, Stefano Bossi wrote:
>
>
>
>         Dear plc4x forum,
>
>
>
>         I have found a possible problem in reading an array of INT.
>
>         I am using the HelloPlc4x app for testing and I am trying to read the 
> field address: '%DB1:274.0:INT[3]'
>
>
>
>         In the request, captured via wireShark I can see the query:
>
>
>
>         Frame 3: 75 bytes on wire (600 bits), 75 bytes captured (600 bits) on 
> interface utun2, id 0
>
>
>
>         Null/Loopback
>
>
>
>         Internet Protocol Version 4, Src: 192.168.100.4, Dst: 192.168.1.192
>
>
>
>         Transmission Control Protocol, Src Port: 54543, Dst Port: 102, Seq: 
> 1, Ack: 1, Len: 31
>
>
>
>         TPKT, Version: 3, Length: 31
>
>
>
>         ISO 8073/X.224 COTP Connection-Oriented Transport Protocol
>
>
>
>         S7 Communication
>
>
>
>             Header: (Job)
>
>
>
>             Parameter: (Read Var)
>
>
>
>                 Function: Read Var (0x04)
>
>
>
>                 Item count: 1
>
>
>
>                 Item [1]: (DB 1.DBX 274.0 INT 3)
>
>
>
>                     Variable specification: 0x12
>
>
>
>                     Length of following address specification: 10
>
>
>
>                     Syntax Id: S7ANY (0x10)
>
>
>
>                     Transport size: INT (5)
>
>
>
>                     Length: 3
>
>
>
>                     DB number: 1
>
>
>
>                     Area: Data blocks (DB) (0x84)
>
>
>
>                     Address: 0x000890
>
>
>
>         and the response:
>
>
>
>         Frame 4: 75 bytes on wire (600 bits), 75 bytes captured (600 bits) on 
> interface utun2, id 0
>
>
>
>         Null/Loopback
>
>
>
>         Internet Protocol Version 4, Src: 192.168.1.192, Dst: 192.168.100.4
>
>
>
>         Transmission Control Protocol, Src Port: 102, Dst Port: 54543, Seq: 
> 1, Ack: 32, Len: 31
>
>
>
>         TPKT, Version: 3, Length: 31
>
>
>
>         ISO 8073/X.224 COTP Connection-Oriented Transport Protocol
>
>
>
>         S7 Communication
>
>
>
>             Header: (Ack_Data)
>
>
>
>             Parameter: (Read Var)
>
>
>
>                 Function: Read Var (0x04)
>
>
>
>                 Item count: 1
>
>
>
>             Data
>
>
>
>                 Item [1]: (Success)
>
>
>
>                     Return code: Success (0xff)
>
>
>
>                     Transport size: INTEGER (0x05)
>
>
>
>                     Length: 6
>
>
>
>                     Data: 000a000b000c
>
>
>
>         The 3 INT I would like to read are there: 000a, 000b, 000c but in the 
> response of:
>
>
>
>         PlcReadResponse syncResponse = readRequest.execute().get();
>
>
>
>         only the first one is present.
>
>
>
>         I read in jira that there was a similar bug here 
> PLC4X-57<https://issues.apache.org/jira/browse/PLC4X-57><https://issues.apache.org/jira/browse/PLC4X-57><https://issues.apache.org/jira/browse/PLC4X-57><https://issues.apache.org/jira/browse/PLC4X-57>,
>  is this the same problem?
>
>
>
>         Thanks for your help.
>
>
>
>         Regards,
>
>         Steafano Bossi
>
>
>
>
>
>
>
>
>
>
>
>
>
>

Attachment: signature.asc