HI Julian,

did you have the opportunity to have a look to the regression?

Do you want I open a ticket in jira ?

Regards,
Stefano Bossi



On 07/08/2020 14:23, Stefano Bossi wrote:
>
> Hi Julian,
>
> unfortunately I think I found a regression in your code.
>
> I am using the compiled 0.8.0-SNAPSHOT version of the library which
> fix the reading of INT Arrays, unfortunately this version isn’t no
> more able to real STRING Array !!!
> When I call a sync read of a STRING the
>
> |PlcReadResponse syncResponse = readRequest.execute().get(); |
>
> never come back, it freeze forever.
>
> Here are the captured frame when I ask for |--field-addresses
> '%DB1:6.0:STRING[6]'| via the HelloPlc4x
>
> Request:
>
> |S7 Communication Header: (Job) Parameter: (Read Var) Function: Read
> Var (0x04) Item count: 1 Item [1]: (DB 1.DBX 6.0 CHAR 8) Variable
> specification: 0x12 Length of following address specification: 10
> Syntax Id: S7ANY (0x10) Transport size: CHAR (3) Length: 8 DB number:
> 1 Area: Data blocks (DB) (0x84) Address: 0x000030 .... .000 0000 0000
> 0011 0... = Byte Address: 6 .... .... .... .... .... .000 = Bit
> Address: 0 |
>
> Answer:
>
> |S7 Communication Header: (Ack_Data) Parameter: (Read Var) Function:
> Read Var (0x04) Item count: 1 Data Item [1]: (Success) Return code:
> Success (0xff) Transport size: OCTET STRING (0x09) Length: 8 Data:
> fe04746573740000 |
>
> The PLC respond correctly |0474657374| -> |test| STRING.
>
> I have downgraded the library to the 0.7.0 just for testing and it
> works, the answer on the wire is the same and the |get()| call report
> the data correctly.
>
> Is this a regression?
>
> Thanks,
> Stefano Bossi
>
> On 03/08/2020 11:58, Julian Feinauer wrote:
>
>> Thank you Stefano, first for your feedback and second fort he
>> compliments.
>>
>>  
>>
>> We are doing our best and it feels really good if people see our
>> efforts <3
>>
>> Julian
>>
>>  
>>
>> *Von: *Stefano Bossi <stefano.bo...@gmail.com>
>> *Datum: *Montag, 3. August 2020 um 11:49
>> *An: *<dev@plc4x.apache.org>, Julian Feinauer
>> <j.feina...@pragmaticminds.de>, Christofer Dutz
>> <christofer.d...@c-ware.de>
>> *Betreff: *Re: Reading Array of Int
>>
>>  
>>
>> Thanks you guys !!!!
>>
>> I have downloaded and compiled the develop code and now I cloud read
>> the INT array without any problem!
>>
>> You are managing a great project with a great support !!!
>>
>> Thanks,
>> Stefano
>>
>> On 02/08/2020 21:08, Julian Feinauer wrote:
>>
>>     Hi,
>>
>>      
>>
>>     sorry for the delayed working on it but I just took a look and think I 
>> fixed the issue.
>>
>>      
>>
>>     It seems that arrays where not properly implemented in the S7 Driver (?).
>>
>>      
>>
>>     I opened up a PR (https://github.com/apache/plc4x/pull/175) and hope 
>> that @Christofer Dutz finds some time to have a quick look (as he did most 
>> of the work there) and merge it, if he agrees with it.
>>
>>      
>>
>>     If you could try out the branch and give your feedback I would be happy.
>>
>>      
>>
>>     Thanks for the excellent preparation of work! : )
>>
>>      
>>
>>     Julian
>>
>>      
>>
>>     Am 02.08.20, 20:40 schrieb "Julian Feinauer" 
>> <j.feina...@pragmaticminds.de> <mailto:j.feina...@pragmaticminds.de>:
>>
>>      
>>
>>         Hi,
>>
>>      
>>
>>         I'm looking into it : )
>>
>>      
>>
>>         J
>>
>>      
>>
>>         Am 01.08.20, 16:17 schrieb "Christofer Dutz" 
>> <christofer.d...@c-ware.de> <mailto:christofer.d...@c-ware.de>:
>>
>>      
>>
>>             Hi Stefano,
>>
>>      
>>
>>             I think such a Jira would be a good idea.
>>
>>      
>>
>>             I’m currently working on the Beckhoff ADS and would try to have 
>> a look as soon as possible.
>>
>>      
>>
>>             Chris
>>
>>      
>>
>>      
>>
>>      
>>
>>             Von: Stefano Bossi <stefano.bo...@gmail.com> 
>> <mailto:stefano.bo...@gmail.com>
>>
>>             Antworten an: <dev@plc4x.apache.org> 
>> <mailto:dev@plc4x.apache.org>
>>
>>             Datum: Samstag, 1. August 2020 um 11:25
>>
>>             An: <dev@plc4x.apache.org> <mailto:dev@plc4x.apache.org>, Julian 
>> Feinauer <j.feina...@pragmaticminds.de> <mailto:j.feina...@pragmaticminds.de>
>>
>>             Betreff: Re: Reading Array of Int
>>
>>      
>>
>>             Hi julian,
>>
>>      
>>
>>             if you need or think could simplify the development I could open 
>> a jira ticket and upload a couple of pcap capture for you.
>>
>>      
>>
>>             As I wrote I am using the 0.7.0 version from Maven and I am 
>> talking with a real Siemens 1200 with firmware 1.2 (pretty old but I didn't 
>> find a way to upgrade it ).
>>
>>      
>>
>>             Let me know.
>>
>>      
>>
>>             Thanks for help.
>>
>>      
>>
>>             Regards,
>>
>>             Stefano
>>
>>      
>>
>>             On 30/07/2020 07:49, Julian Feinauer wrote:
>>
>>      
>>
>>             Hey Stefano, I will try to have a look later today. Are you 
>> using plc4x version 0.6 or 0.7?
>>
>>      
>>
>>      
>>
>>      
>>
>>             Thank you!
>>
>>      
>>
>>      
>>
>>      
>>
>>             Julian
>>
>>      
>>
>>      
>>
>>      
>>
>>             Holen Sie sich Outlook für Android<https://aka.ms/ghei36> 
>> <https://aka.ms/ghei36><https://aka.ms/ghei36> <https://aka.ms/ghei36>
>>
>>      
>>
>>      
>>
>>      
>>
>>             ________________________________
>>
>>      
>>
>>             Von: Stefano Bossi <stefano.bo...@gmail.com> 
>> <mailto:stefano.bo...@gmail.com><mailto:stefano.bo...@gmail.com> 
>> <mailto:stefano.bo...@gmail.com>
>>
>>      
>>
>>             Gesendet: Mittwoch, 29. Juli 2020, 12:32
>>
>>      
>>
>>             An: dev@plc4x.apache.org 
>> <mailto:dev@plc4x.apache.org><mailto:dev@plc4x.apache.org> 
>> <mailto:dev@plc4x.apache.org>; Christofer Dutz
>>
>>      
>>
>>             Betreff: Re: Reading Array of Int
>>
>>      
>>
>>      
>>
>>      
>>
>>             Thanks Chris,
>>
>>      
>>
>>      
>>
>>      
>>
>>             yes definitely this is a workaround, I am experimenting and 
>> learning.
>>
>>      
>>
>>      
>>
>>      
>>
>>             I really appreciate your time on the investigation of the issue.
>>
>>      
>>
>>      
>>
>>      
>>
>>             Thanks,
>>
>>      
>>
>>             Stefano Bossi
>>
>>      
>>
>>      
>>
>>      
>>
>>      
>>
>>      
>>
>>      
>>
>>      
>>
>>             On 29/07/2020 12:08, Christofer Dutz wrote:
>>
>>      
>>
>>      
>>
>>      
>>
>>             Well that’s a workaround, but not a fix …
>>
>>      
>>
>>      
>>
>>      
>>
>>             We should focus on fixing this.
>>
>>      
>>
>>      
>>
>>      
>>
>>             I’ll investigate the issue as soon as I’m done with the Beckhoff 
>> ADS/AMS stuff …
>>
>>      
>>
>>      
>>
>>      
>>
>>             Perhaps Julian could find some time to investigate?
>>
>>      
>>
>>      
>>
>>      
>>
>>             Chris
>>
>>      
>>
>>      
>>
>>      
>>
>>      
>>
>>      
>>
>>      
>>
>>      
>>
>>             Von: Stefano Bossi <stefano.bo...@gmail.com> 
>> <mailto:stefano.bo...@gmail.com><mailto:stefano.bo...@gmail.com> 
>> <mailto:stefano.bo...@gmail.com><mailto:stefano.bo...@gmail.com> 
>> <mailto:stefano.bo...@gmail.com><mailto:stefano.bo...@gmail.com> 
>> <mailto:stefano.bo...@gmail.com>
>>
>>      
>>
>>             Antworten an: <dev@plc4x.apache.org> 
>> <mailto:dev@plc4x.apache.org><mailto:dev@plc4x.apache.org> 
>> <mailto:dev@plc4x.apache.org><mailto:dev@plc4x.apache.org> 
>> <mailto:dev@plc4x.apache.org><mailto:dev@plc4x.apache.org> 
>> <mailto:dev@plc4x.apache.org>
>>
>>      
>>
>>             Datum: Mittwoch, 29. Juli 2020 um 11:41
>>
>>      
>>
>>             An: <dev@plc4x.apache.org> 
>> <mailto:dev@plc4x.apache.org><mailto:dev@plc4x.apache.org> 
>> <mailto:dev@plc4x.apache.org><mailto:dev@plc4x.apache.org> 
>> <mailto:dev@plc4x.apache.org><mailto:dev@plc4x.apache.org> 
>> <mailto:dev@plc4x.apache.org>
>>
>>      
>>
>>             Betreff: Re: Reading Array of Int
>>
>>      
>>
>>      
>>
>>      
>>
>>      
>>
>>      
>>
>>             I have adopted a workaround reading all the INT variable 
>> separated.
>>
>>      
>>
>>      
>>
>>      
>>
>>             --connection-string 
>> 's7:tcp://192.168.1.192?controller-type=S7_1200' --field-addresses 
>> '%DB1:274.0:INT' '%DB1:276.0:INT' '%DB1:278.0:INT' '%DB1:280.0:INT'
>>
>>      
>>
>>      
>>
>>      
>>
>>             In this way on the wire you have:
>>
>>      
>>
>>             the query:
>>
>>      
>>
>>      
>>
>>      
>>
>>             Frame 296: 111 bytes on wire (888 bits), 111 bytes captured (888 
>> bits) on interface utun2, id 0
>>
>>      
>>
>>      
>>
>>      
>>
>>             Null/Loopback
>>
>>      
>>
>>      
>>
>>      
>>
>>             Internet Protocol Version 4, Src: 192.168.100.4, Dst: 
>> 192.168.1.192
>>
>>      
>>
>>      
>>
>>      
>>
>>             Transmission Control Protocol, Src Port: 57188, Dst Port: 102, 
>> Seq: 48, Ack: 50, Len: 67
>>
>>      
>>
>>      
>>
>>      
>>
>>             TPKT, Version: 3, Length: 67
>>
>>      
>>
>>      
>>
>>      
>>
>>             ISO 8073/X.224 COTP Connection-Oriented Transport Protocol
>>
>>      
>>
>>      
>>
>>      
>>
>>             S7 Communication
>>
>>      
>>
>>      
>>
>>      
>>
>>                 Header: (Job)
>>
>>      
>>
>>      
>>
>>      
>>
>>                 Parameter: (Read Var)
>>
>>      
>>
>>      
>>
>>      
>>
>>                     Function: Read Var (0x04)
>>
>>      
>>
>>      
>>
>>      
>>
>>                     Item count: 4
>>
>>      
>>
>>      
>>
>>      
>>
>>                     Item [1]: (DB 1.DBX 274.0 INT 1)
>>
>>      
>>
>>      
>>
>>      
>>
>>                     Item [2]: (DB 1.DBX 276.0 INT 1)
>>
>>      
>>
>>      
>>
>>      
>>
>>                     Item [3]: (DB 1.DBX 278.0 INT 1)
>>
>>      
>>
>>      
>>
>>      
>>
>>                     Item [4]: (DB 1.DBX 280.0 INT 1)
>>
>>      
>>
>>      
>>
>>      
>>
>>             the answer:
>>
>>      
>>
>>      
>>
>>      
>>
>>             Frame 297: 89 bytes on wire (712 bits), 89 bytes captured (712 
>> bits) on interface utun2, id 0
>>
>>      
>>
>>      
>>
>>      
>>
>>             Null/Loopback
>>
>>      
>>
>>      
>>
>>      
>>
>>             Internet Protocol Version 4, Src: 192.168.1.192, Dst: 
>> 192.168.100.4
>>
>>      
>>
>>      
>>
>>      
>>
>>             Transmission Control Protocol, Src Port: 102, Dst Port: 57188, 
>> Seq: 50, Ack: 115, Len: 45
>>
>>      
>>
>>      
>>
>>      
>>
>>             TPKT, Version: 3, Length: 45
>>
>>      
>>
>>      
>>
>>      
>>
>>             ISO 8073/X.224 COTP Connection-Oriented Transport Protocol
>>
>>      
>>
>>      
>>
>>      
>>
>>             S7 Communication
>>
>>      
>>
>>      
>>
>>      
>>
>>                 Header: (Ack_Data)
>>
>>      
>>
>>      
>>
>>      
>>
>>                 Parameter: (Read Var)
>>
>>      
>>
>>      
>>
>>      
>>
>>                     Function: Read Var (0x04)
>>
>>      
>>
>>      
>>
>>      
>>
>>                     Item count: 4
>>
>>      
>>
>>      
>>
>>      
>>
>>                 Data
>>
>>      
>>
>>      
>>
>>      
>>
>>                     Item [1]: (Success)
>>
>>      
>>
>>      
>>
>>      
>>
>>                     Item [2]: (Success)
>>
>>      
>>
>>      
>>
>>      
>>
>>                     Item [3]: (Success)
>>
>>      
>>
>>      
>>
>>      
>>
>>                     Item [4]: (Success)
>>
>>      
>>
>>      
>>
>>      
>>
>>             [INFO ] 10:15:44.727 
>> it.fox.datapicker.HelloPlc4x.printResponse() - Value[value-0]: 10
>>
>>      
>>
>>      
>>
>>      
>>
>>             [INFO ] 10:15:44.733 
>> it.fox.datapicker.HelloPlc4x.printResponse() - Value[value-1]: 11
>>
>>      
>>
>>      
>>
>>      
>>
>>             [INFO ] 10:15:44.737 
>> it.fox.datapicker.HelloPlc4x.printResponse() - Value[value-2]: 12
>>
>>      
>>
>>      
>>
>>      
>>
>>             [INFO ] 10:15:44.741 
>> it.fox.datapicker.HelloPlc4x.printResponse() - Value[value-3]: 13
>>
>>      
>>
>>      
>>
>>      
>>
>>             Unfortunately my java knowledge are not so advanced to fix the 
>> bug in reading the array in a single command, anyway there’s a workaround.
>>
>>      
>>
>>      
>>
>>      
>>
>>             Hope this mail help some newbies like me to find the right way 
>> to read data from the PLC.
>>
>>      
>>
>>      
>>
>>      
>>
>>             Regards,
>>
>>      
>>
>>             Stefano
>>
>>      
>>
>>      
>>
>>      
>>
>>             On 28/07/2020 11:38, Stefano Bossi wrote:
>>
>>      
>>
>>      
>>
>>      
>>
>>             Dear plc4x forum,
>>
>>      
>>
>>      
>>
>>      
>>
>>             I have found a possible problem in reading an array of INT.
>>
>>      
>>
>>             I am using the HelloPlc4x app for testing and I am trying to 
>> read the field address: '%DB1:274.0:INT[3]'
>>
>>      
>>
>>      
>>
>>      
>>
>>             In the request, captured via wireShark I can see the query:
>>
>>      
>>
>>      
>>
>>      
>>
>>             Frame 3: 75 bytes on wire (600 bits), 75 bytes captured (600 
>> bits) on interface utun2, id 0
>>
>>      
>>
>>      
>>
>>      
>>
>>             Null/Loopback
>>
>>      
>>
>>      
>>
>>      
>>
>>             Internet Protocol Version 4, Src: 192.168.100.4, Dst: 
>> 192.168.1.192
>>
>>      
>>
>>      
>>
>>      
>>
>>             Transmission Control Protocol, Src Port: 54543, Dst Port: 102, 
>> Seq: 1, Ack: 1, Len: 31
>>
>>      
>>
>>      
>>
>>      
>>
>>             TPKT, Version: 3, Length: 31
>>
>>      
>>
>>      
>>
>>      
>>
>>             ISO 8073/X.224 COTP Connection-Oriented Transport Protocol
>>
>>      
>>
>>      
>>
>>      
>>
>>             S7 Communication
>>
>>      
>>
>>      
>>
>>      
>>
>>                 Header: (Job)
>>
>>      
>>
>>      
>>
>>      
>>
>>                 Parameter: (Read Var)
>>
>>      
>>
>>      
>>
>>      
>>
>>                     Function: Read Var (0x04)
>>
>>      
>>
>>      
>>
>>      
>>
>>                     Item count: 1
>>
>>      
>>
>>      
>>
>>      
>>
>>                     Item [1]: (DB 1.DBX 274.0 INT 3)
>>
>>      
>>
>>      
>>
>>      
>>
>>                         Variable specification: 0x12
>>
>>      
>>
>>      
>>
>>      
>>
>>                         Length of following address specification: 10
>>
>>      
>>
>>      
>>
>>      
>>
>>                         Syntax Id: S7ANY (0x10)
>>
>>      
>>
>>      
>>
>>      
>>
>>                         Transport size: INT (5)
>>
>>      
>>
>>      
>>
>>      
>>
>>                         Length: 3
>>
>>      
>>
>>      
>>
>>      
>>
>>                         DB number: 1
>>
>>      
>>
>>      
>>
>>      
>>
>>                         Area: Data blocks (DB) (0x84)
>>
>>      
>>
>>      
>>
>>      
>>
>>                         Address: 0x000890
>>
>>      
>>
>>      
>>
>>      
>>
>>             and the response:
>>
>>      
>>
>>      
>>
>>      
>>
>>             Frame 4: 75 bytes on wire (600 bits), 75 bytes captured (600 
>> bits) on interface utun2, id 0
>>
>>      
>>
>>      
>>
>>      
>>
>>             Null/Loopback
>>
>>      
>>
>>      
>>
>>      
>>
>>             Internet Protocol Version 4, Src: 192.168.1.192, Dst: 
>> 192.168.100.4
>>
>>      
>>
>>      
>>
>>      
>>
>>             Transmission Control Protocol, Src Port: 102, Dst Port: 54543, 
>> Seq: 1, Ack: 32, Len: 31
>>
>>      
>>
>>      
>>
>>      
>>
>>             TPKT, Version: 3, Length: 31
>>
>>      
>>
>>      
>>
>>      
>>
>>             ISO 8073/X.224 COTP Connection-Oriented Transport Protocol
>>
>>      
>>
>>      
>>
>>      
>>
>>             S7 Communication
>>
>>      
>>
>>      
>>
>>      
>>
>>                 Header: (Ack_Data)
>>
>>      
>>
>>      
>>
>>      
>>
>>                 Parameter: (Read Var)
>>
>>      
>>
>>      
>>
>>      
>>
>>                     Function: Read Var (0x04)
>>
>>      
>>
>>      
>>
>>      
>>
>>                     Item count: 1
>>
>>      
>>
>>      
>>
>>      
>>
>>                 Data
>>
>>      
>>
>>      
>>
>>      
>>
>>                     Item [1]: (Success)
>>
>>      
>>
>>      
>>
>>      
>>
>>                         Return code: Success (0xff)
>>
>>      
>>
>>      
>>
>>      
>>
>>                         Transport size: INTEGER (0x05)
>>
>>      
>>
>>      
>>
>>      
>>
>>                         Length: 6
>>
>>      
>>
>>      
>>
>>      
>>
>>                         Data: 000a000b000c
>>
>>      
>>
>>      
>>
>>      
>>
>>             The 3 INT I would like to read are there: 000a, 000b, 000c but 
>> in the response of:
>>
>>      
>>
>>      
>>
>>      
>>
>>             PlcReadResponse syncResponse = readRequest.execute().get();
>>
>>      
>>
>>      
>>
>>      
>>
>>             only the first one is present.
>>
>>      
>>
>>      
>>
>>      
>>
>>             I read in jira that there was a similar bug here 
>> PLC4X-57<https://issues.apache.org/jira/browse/PLC4X-57> 
>> <https://issues.apache.org/jira/browse/PLC4X-57><https://issues.apache.org/jira/browse/PLC4X-57>
>>  
>> <https://issues.apache.org/jira/browse/PLC4X-57><https://issues.apache.org/jira/browse/PLC4X-57>
>>  
>> <https://issues.apache.org/jira/browse/PLC4X-57><https://issues.apache.org/jira/browse/PLC4X-57>
>>  <https://issues.apache.org/jira/browse/PLC4X-57>, is this the same problem?
>>
>>      
>>
>>      
>>
>>      
>>