Hi Chris, Hi Stefano,

Thanks a lot for your valuable feedback. It is highly appreciated.

I followed Stefanos suggestions and applied the simplifications. In addition I 
created a Wireshark capture which is attached to this email.

It seems it replies with “[Error code: This service is not implemented on the 
module or a frame error was reported (0x8104)]"

Does this mean the address is wrong or is it something else?

Best regards,
Sebastian


> On 31. Aug 2020, at 09:42, Stefano Bossi <stefano.bo...@gmail.com> wrote:
> 
> Hi Sebastian,
> 
> if you need some help in setup the wireshark capture software or open the 
> jira ticket I could help.
> 
> It’s definitely worth to follow the Chris suggestion to help him to spot the 
> real problem.
> 
> In the mean time I think you could simplify the PLC query in this way:
> 
> String Url: s7:tcp://172.3.4.5:102?controller-type=S7_1200
> 
> String field: %DB20:5.0:BOOL
> 
> As far as the address of the Data Block and the bool value are correct, 
> should work.
> There were nothing particular wrong in your query but the library is somewhat 
> “sensible” if something goes wrong in the dialogue with the PLC
> 
> An another thing you should pay attention is that the Data Block MUST be NOT 
> optimized; reading of optimized block is not currently supported. This 
> shouldn’t be your case because an attempt to read an optimized block raise an 
> exception or a null value.
> 
> Try and let us know.
> 
> Regards,
> Stefano
> 
> On 31/08/2020 08:48, Christofer Dutz wrote:
> 
> 
> 
>> Hi Sebastian,
>> 
>> could you possibly do a wireshark recording of this, create an issue in our 
>> jira and attach the capture there?
>> I am sure we haven't handled all things that could go wrong and with this 
>> information I might be able to improve the error handling.
>> 
>> Chris
>> 
>> 
>> 
>> 
>> Am 30.08.20, 18:28 schrieb "Sebastian Voss" 
>> <svdevl...@gmail.com>
>> :
>> 
>>     Hi,
>> 
>>     I’m trying to read a value from an Siemens S7-1200 PLC). This is my 
>> first project using the S7 protocol and plc4x. When I try to read a value 
>> the read request is not being executed (I also do not receive an error 
>> message or timeout). Would this be the normal behaviour when the field 
>> address is wrong? I’m out of ideas how to trace this down. Any hints would 
>> be highly appreciated.
>> 
>>     This is the simple program I created:
>> 
>>     String url = 
>> "s7://172.3.4.5:102?local-rack=0&local-slot=1&remote-rack=0&remote-slot=1&controller-type=S7_1200
>>  
>> <s7://172.3.4.5:102?local-rack=0&local-slot=1&remote-rack=0&remote-slot=1&controller-type=S7_1200>";
>>     PlcDriverManager manager = new PlcDriverManager();
>>     PlcConnection connection = manager.getConnection(url);
>> 
>>     boolean isConnected = connection.isConnected();
>>     boolean canRead = connection.getMetadata().canRead();
>> 
>>     System.out.println(isConnected);  // prints true
>>     System.out.println(canRead);  // prints true
>> 
>>     String field = "%DB20:DBX05.0:BOOL";
>>     PlcReadRequest request = connection
>>            .readRequestBuilder()
>>            .addItem("value-1", field)
>>            .build();
>> 
>>     PlcReadResponse response = request.execute().get();  // here is hangs 
>> forever
>> 
>>     System.out.println(response.getFieldNames());
>> 
>>     connection.close();
>> 
>>     Thanks a lot in advance!
>> 
>>     Best regards,
>>     Sebastian
>> 
>> 
> 
> 