Hi Niels,

I think this might be related to what happens when reading Strings in S7 
without providing a length.
In this case each string is 255 charaters long and it already exceeds the 
size-limit of 200 or so of a S7 1200.

In S7 we use some code to split up multiple tags into multiple requests, but 
rewriting the query to support automatic splitting of one single tag into 
multiple requests is quite a bit more difficult.

I thought you were reading multiple tags that in sum exceeded the 125 registers 
and for that case simply something similar to the S7 query updater should also 
work for other protocols.

Do I understand you correctly, that in your case you want to read one tag, that 
is bigger?

Chris

From: Niels Basjes <[email protected]>
Date: Sunday, 15. January 2023 at 16:38
To: [email protected] <[email protected]>
Subject: [Modbus] Handling 'too large' blocks of registers
Hi,

A few weeks ago some code of mine was merged to limit the number of
registers that can be requested in a single ModbusTag because asking for
more than 125 registers in a single request will always fail (because of
the way modbus works).
https://github.com/apache/plc4x/pull/721

One of the comments was asking if it can be automated in a generic way to
split a "too large" request into multiple smaller requests.
So If I ask for a block of 200 registers then plc4x would simply split it
into multiple requests (like 125 and 75 for example, or 100 and 100) and
afterwards merge the resulting registers of the two requests back into a
single block of 200 registers for the upstream application to analyze.

I said I would look into this and this is what I found while doing some
experimenting with my real solar converter.
This device uses the SunSpec standard for defining meaning to modbus
registers.

My current conclusion at this point is that it is impossible to handle this
at the modbus level and I'm looking for you guys to challenge me in this.

Why do I say this?
One of the logical values you can retrieve is the name of the Manufacturer
and the Model of the device that are both stored as UTF-8 in a set of 16
registers (i.e. usually 32 characters).
https://github.com/sunspec/models/blob/master/json/model_1.json#L27
https://github.com/sunspec/models/blob/master/json/model_1.json#L36

I found that if I try to fetch only a part of this logical value I get
either an error (INVALID_ADDRESS) or bad data.
When I fetch the entire value I get the 16 registers which hold the correct
data.

Output of my test program that fetches the Model of the device (which is in
my case "SB3.6-1AV-41" ).
ModbusTag[4x40021:UINT[16]]:  0x5342 0x332E 0x362D 0x3141 0x562D 0x3431
0x0000 0x0000 0x0000 0x0000 0x0000 0x0000 0x0000 0x0000 0x0000 0x0000
ModbusTag[4x40021:UINT[15]]: INVALID_ADDRESS
ModbusTag[4x40022:UINT[15]]:  0xFFFF 0xFFFF 0xFFFF 0xFFFF 0xFFFF 0xFFFF
0xFFFF 0xFFFF 0xFFFF 0xFFFF 0xFFFF 0xFFFF 0xFFFF 0xFFFF 0xFFFF

So if I retrieve the correct block I get it.
If I try to get 1 register less than I should I get an error.
If I try to get the registers starting from the 2nd register I get only
0xFFFF (important: NO error and a PlcResponseCode.OK !!)

I expect there to be many other modbus devices that have similar effects
when the logical value requires multiple registers.

So for now I come to the conclusion that fetching only part of the
registers that make up a logical variable in general will not work and (in
some cases) cannot be detected to have failed.

At this point my assessment is that the only way to handle this is by
actually knowing the meaning of the block of registers (i.e. which must be
read together in a single read) and work from there.

Note that the current SunSpec definition also has the concept of a 'sync'
group of points (logical values that consist of 1 or more registers) which
are grouped in the specification with the intent of "indicating
that the points in the group must be read and written atomically", which
effectively means you cannot read them individually from the modbus
standpoint.

Looking for your feedback on this.
Do you know of existing software to generically handle this ?

--
Best regards / Met vriendelijke groeten,

Niels Basjes