I created an issue with attachment
https://github.com/apache/plc4x/issues/743

On Sun, Jan 15, 2023 at 5:02 PM Christofer Dutz <[email protected]>
wrote:

> Could you do a wireshark dump and attach that to an issue?
>
> Chris
>
> From: Christofer Dutz <[email protected]>
> Date: Sunday, 15. January 2023 at 16:47
> To: [email protected] <[email protected]>
> Subject: Re: [Modbus] Handling 'too large' blocks of registers
> Hi Niels,
>
> I think this might be related to what happens when reading Strings in S7
> without providing a length.
> In this case each string is 255 charaters long and it already exceeds the
> size-limit of 200 or so of a S7 1200.
>
> In S7 we use some code to split up multiple tags into multiple requests,
> but rewriting the query to support automatic splitting of one single tag
> into multiple requests is quite a bit more difficult.
>
> I thought you were reading multiple tags that in sum exceeded the 125
> registers and for that case simply something similar to the S7 query
> updater should also work for other protocols.
>
> Do I understand you correctly, that in your case you want to read one tag,
> that is bigger?
>
> Chris
>
> From: Niels Basjes <[email protected]>
> Date: Sunday, 15. January 2023 at 16:38
> To: [email protected] <[email protected]>
> Subject: [Modbus] Handling 'too large' blocks of registers
> Hi,
>
> A few weeks ago some code of mine was merged to limit the number of
> registers that can be requested in a single ModbusTag because asking for
> more than 125 registers in a single request will always fail (because of
> the way modbus works).
> https://github.com/apache/plc4x/pull/721
>
> One of the comments was asking if it can be automated in a generic way to
> split a "too large" request into multiple smaller requests.
> So If I ask for a block of 200 registers then plc4x would simply split it
> into multiple requests (like 125 and 75 for example, or 100 and 100) and
> afterwards merge the resulting registers of the two requests back into a
> single block of 200 registers for the upstream application to analyze.
>
> I said I would look into this and this is what I found while doing some
> experimenting with my real solar converter.
> This device uses the SunSpec standard for defining meaning to modbus
> registers.
>
> My current conclusion at this point is that it is impossible to handle this
> at the modbus level and I'm looking for you guys to challenge me in this.
>
> Why do I say this?
> One of the logical values you can retrieve is the name of the Manufacturer
> and the Model of the device that are both stored as UTF-8 in a set of 16
> registers (i.e. usually 32 characters).
> https://github.com/sunspec/models/blob/master/json/model_1.json#L27
> https://github.com/sunspec/models/blob/master/json/model_1.json#L36
>
> I found that if I try to fetch only a part of this logical value I get
> either an error (INVALID_ADDRESS) or bad data.
> When I fetch the entire value I get the 16 registers which hold the correct
> data.
>
> Output of my test program that fetches the Model of the device (which is in
> my case "SB3.6-1AV-41" ).
> ModbusTag[4x40021:UINT[16]]:  0x5342 0x332E 0x362D 0x3141 0x562D 0x3431
> 0x0000 0x0000 0x0000 0x0000 0x0000 0x0000 0x0000 0x0000 0x0000 0x0000
> ModbusTag[4x40021:UINT[15]]: INVALID_ADDRESS
> ModbusTag[4x40022:UINT[15]]:  0xFFFF 0xFFFF 0xFFFF 0xFFFF 0xFFFF 0xFFFF
> 0xFFFF 0xFFFF 0xFFFF 0xFFFF 0xFFFF 0xFFFF 0xFFFF 0xFFFF 0xFFFF
>
> So if I retrieve the correct block I get it.
> If I try to get 1 register less than I should I get an error.
> If I try to get the registers starting from the 2nd register I get only
> 0xFFFF (important: NO error and a PlcResponseCode.OK !!)
>
> I expect there to be many other modbus devices that have similar effects
> when the logical value requires multiple registers.
>
> So for now I come to the conclusion that fetching only part of the
> registers that make up a logical variable in general will not work and (in
> some cases) cannot be detected to have failed.
>
> At this point my assessment is that the only way to handle this is by
> actually knowing the meaning of the block of registers (i.e. which must be
> read together in a single read) and work from there.
>
> Note that the current SunSpec definition also has the concept of a 'sync'
> group of points (logical values that consist of 1 or more registers) which
> are grouped in the specification with the intent of "indicating
> that the points in the group must be read and written atomically", which
> effectively means you cannot read them individually from the modbus
> standpoint.
>
> Looking for your feedback on this.
> Do you know of existing software to generically handle this ?
>
> --
> Best regards / Met vriendelijke groeten,
>
> Niels Basjes
>


-- 
Best regards / Met vriendelijke groeten,

Niels Basjes