On 10 August 2015 at 21:26, Gene Heskett <[email protected]> wrote:
> To be specific, G92.1 is not clearing #5061, the g54 X offset.  Possibly
> not clearing #5062 or #5063, all of which I use to calibrate the machine

Why do you think that it should?

The Docs say:

G92.1 - reset axis offsets to zero and set parameters 5211 - 5219 to zero.

G92.2 - reset axis offsets to zero.

If you want to reset G54 to Zero the code is:

G10 L2 P1 X0 Y0 Z0

Again, from the docs:

G10 L2 P- <axes R->

P - coordinate system (0-9)

R - rotation about the Z axis

G10 L2 offsets the origin of the axes in the coordinate system
specified to the value of the axis word. The offset is from the
machine origin established during homing. The offset value will
replace any current offsets in effect for the coordinate system
specified. Axis words not used will not be changed.

Program P0 to P9 to specify which coordinate system to change.


-- 
atp
If you can't fix it, you don't own it.
http://www.ifixit.com/Manifesto

------------------------------------------------------------------------------
_______________________________________________
Emc-developers mailing list
[email protected]
https://lists.sourceforge.net/lists/listinfo/emc-developers

Reply via email to