On  9 Oct 1996 [email protected] wrote:

> The question remains:  what do I have to do for CE Mark purposes to prove 
> that our insulation system is good for greater than Class 105C temperatures 
> given the presence of wire that has UL/CSA ratings of 105C but a higher 
> manufacturer's rating?

The CE Mark doesn`t require for UL/CSA ratings.  
However you have to sincerely investigate with the manufacturer what 
the real reasons are for the lower UL rating , and how it affects your 
application.

Then make your best judgement.If you honestly believe that the product 
is safe then you are free to make the CE MARK Self-Declaration. 

Best regards  
 
  -Teddy Rieber
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
ECI TELECOM , Power Supplies R&D Department
30 HASIVIM Street, PETAH TIKVA-49133 , ISRAEL
 E-mail :[email protected]
Tel:+972 3 9266119 ,Fax:+972 3 9266411
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~