Moshe Valdman asks about 12 volts DC applied between the
hand and other body parts.

1.  Resistance.  

    The human body resistance is not a constant.

    If you have measured yourself with an ohmmeter, you will
    have noticed that the body resistance is not a constant,
    and continually reduced in value for the duration of the
    measurement.

    The body resistance is a function of many variables,
    including contact location (on the body), contact area,
    skin condition, time of day, skin temperature, applied
    voltage, duration of applied voltage, etc.

    Depending on the preceding variables, the body resistance
    will measure (with an ohmmeter) anywhere from a maximum of
    1 megohm down to a minimum of 5 kohm.

    Increased voltage accelerates the decrease in body resistance.  

    Depending on the contact location, contact area, and duration
    of applied voltage, with 12 volts dc applied to the body, you
    can expect a continuous decrease in body resistance.
    
2.  Current.

    Current in the body is determined by Ohm's Law.  Given 12 
    volts DC, and continuosly decreasing body resistance, the
    current in the body will continuosly increase.

    The body resistance may approach 5 kohms, which means the body
    current would approach 2.4 milliamperes.

    Depending on the individual, some persons may experience a 
    sensation of electric shock after several minutes, while others
    will never experience a sensation of electric shock.

3.  Medical or other regulations.

    I don't know of any...

4.  Risks.

    Human reaction to electric current has a very high three-
    sigma variation.  Short-term (i.e., less than one minute) and 
    intermittant contact with 12 volts DC probably will have little 
    or no noticable effect.

    But, long-term effects of low voltage have not been studied.
    Fortunately, at low voltages such as 12 volts, I would expect
    that the body response would come on slowly so that one could
    anticipate any unwanted effects.

5.  Standards.

    IEC 479 is the reference standard for effects of current on the
    body.  

    But, this document does not address voltage sources such as 12 
    volts DC.  


Best regards,
Richard Nute


+=====================================================================+
|Richard Nute                        |Quality Department              |
|Hewlett-Packard Company             |Product Regulations Group       |
|San Diego Division                  |Phone : 619 655 3329            | 
|Postal: 16399 West Bernardo Drive   |FAX   : 619 655 4979            |
|        San Diego, California 92127 |e-mail: [email protected]        |
+=====================================================================+


Reply via email to