Clause 2.5.2 of EN 60950 states that "class II equipment shall have no provision for protective earthing, except that it may be provided with a means for maintaining the continuity of protective earthing circuits to other equipment in a system. If class II equipment has an earth connection for functional purposes, the functional earth circuit shall be separated from parts at hazardous voltages by double or reinforced insulation."
I don't know if this would apply in your case. IEC 320 3-pin inlets are generally not allowed in class II equipment. Even if you provide a cord with your equipment there is a chance that if the cord is lost or damaged a generic power cord will be used. Patty Elliot TUV Rheinland of N.A. San Diego, CA (619) 792-2770 X37 [email protected] At 08:35 AM 4/21/97 -0700, [email protected] wrote: >Item Subject: cc:Mail Text > >Fellow professionals; > >Is there anything in the EN60950 regulations re: LVD that would prevent me >from using a IEC three prong receptacle in my product connected to a >special power cord with only two wires and to a class 0 plug (two prong for >Europe) and the mating IEC 320 connector at the other end? (assume that my >product is designed to be double insulated). > >Best Regards > >Hans >