Hi MIke:


IEC 320, Figure 1, specifies acceptable appliance couplers for
Class II products:

    INLET           CORD CONNECTOR           RATING
    -----           --------------           ------

     C2                  C1                   0.2 A
     C8                  C7                   2.5 A
    C10                  C9                   6   A
    C19                 C17                  10   A
    C24                 C23                  16   A

Not all of these may be commonly available in the USA.  However,
I would suggest Panel Components Corp. as a possible source for
non-USA power components.

C2/C1 is commonly used on shavers.

C8/C7 is commonly used on portable electronics.

I've not seen the others in use on products.


Best regards,
Rich




>   From [email protected] Mon Apr 21 22:30:55 PDT 1997
>   Received: from hpsdlo.sdd.hp.com by hpsdlfsg.sdd.hp.com with ESMTP
>       (1.37.109.16/15.5+IOS 3.21+sdd) id AA015517054; Mon, 21 Apr 1997 
> 22:30:54 -0700
>   Received: from powergrid.electriciti.com by hpsdlo.sdd.hp.com with ESMTP
>       (1.37.109.20/15.5+IOS 3.21+sdd) id AA182487115; Mon, 21 Apr 1997 
> 22:31:55 -0700
>   Received: from mike-elliott (line10.cs9.electriciti.com [198.5.214.20])
>       by powergrid.electriciti.com (8.8.5/8.8.5) with ESMTP id WAA10022;
>       Mon, 21 Apr 1997 22:37:30 -0700 (PDT)
>   Message-Id: <[email protected]>
>   From: "Mike Elliott" <[email protected]>
>   To: "Rich Nute" <[email protected]>
>   Cc: <[email protected]>
>   Subject: Re: IEC320 and Double insulation
>   Date: Mon, 21 Apr 1997 22:30:25 -0700
>   X-Msmail-Priority: Normal
>   X-Priority: 3
>   X-Mailer: Microsoft Internet Mail 4.70.1160
>   
>   Hi Rich,
>   
>   If I use Class II construction throughout my equipment and wish to
>   apply the box-within-a-box double-insulated symbol to it, what type of
>   power plug cord can I use? My handy-dandy Newark catalog shows only
>   3-conductor IEC-320-C13 terminated cordsets. Should I be seeking
>   IEC-320-C17 types? 
>   
>   --
>   Mike Elliott
>   Elliott ASE / Counterpoint 
>   fax: + 760 945 0219
>   [email protected]
>   http://www.counter-point.com/cpoint
>   http://www.elliottase.com/audio
>   
>   ----------
>   > From: Rich Nute <[email protected]>
>   > To: [email protected]
>   > Cc: [email protected]
>   > Subject: Re: IEC320 and Double insulation
>   > Date: Monday, 21 April, 1997 12:18 PM
>   > 
>   > 
>   > 
>   > 
>   > Hi Hans:
>   > 
>   > 
>   > The IEC 950/EN 60950 definition for a Class I product is:
>   > 
>   >     "Equipment where protection against electric shock is achieved
>   >      by:
>   > 
>   >      a)  using BASIC INSULATION, and also
>   > 
>   >      b)  providing a means for connecting to the protective earthing
>   >          conductor in the building wiring those conductive parts that
>   >          are otherwise capable of assuming HAZARDOUS VOLTAGES if the 
>   >          BASIC INSULATION fails.
>   > 
>   >      Notes
>   > 
>   >      1  CLASS I EQUIPMENT may have parts with DOUBLE INSULATION or
>   >      REINFORCED INSULATION, or parts operating in SELV CIRCUITS.
>   > 
>   >      2  For equipment intended for use with a power supply cord, this
>   >      provision includes a protective conductor as a part of the
>   cord."
>   > 
>   > Your product DOES use basic insulation.  
>   > 
>   > Your product IS provided with a means for connecting to the
>   protective
>   > earthing conductor in the building wiring.  (The fact that the
>   terminal
>   > is not at the supply end of the cord is irrelevant.)
>   > 
>   > The construction you describe is IMPLIED to be Class I by use of the
>   > two-wire plus ground IEC 320 connector.
>   > 
>   > I believe there is a requirement either in IEC 950 or IEC 536 that if
>   a
>   > protective grounding terminal is provided, the equipment is
>   considered
>   > Class I even if it is Class II construction throughout.  
>   > 
>   > You cannot apply the double-insulated symbol to a product with a
>   > grounding terminal.
>   > 
>   > 
>   > Best regards,
>   > Rich
>   > 
>   > 
>   > ps:  The power cord plug is NOT Class 0.  Class 0 is a product with
>   only
>   >      Basic Insulation and for use only in an earth-free insulating
>   >      environment which provides protection against electric shock in
>   the
>   >      event of a fault in Basic Insulation.
>   > 
>   >      At one time, the Euro authorities believed the normal indoor
>   >      environment to be an earth-free insulating environment, which
>   then
>   >      qualified two-wire, basic-insulated products for use in such an
>   >      environment.
>   > 
>   >      Some years ago, Class 0 construction was deemed unacceptable in 
>   >      Europe (although it appears to be acceptable in Japan).
>   > 
>   > 
>   > 
>   > 
>   