Don't forget, the low impedance path from the  black (high side of
switch) to water to human to water to neutral (white wire.) It doesn't go
to ground and may not even trip the GFI!

>>> <[email protected]> 09/02/97
06:33pm >>>
     

You forgot two major assumptions:

1) The impedance of the water and 
2)the impedance of the human in water.

In water, the human has orders of magnitude of lower impedance, and
therefore, 
the majority of the current will flow through the human assuming there is
a path
to ground. It is highly unlikely that there is no path to ground. In most
home 
building codes, plastic piping is not allowed due to fire codes (they melt) 
perhaps with the exception of waste pipe (most of them are cast iron)
Recently 
in the bay area, a girl was electrocuted in a swimming pool due to a
faulty 
lighting wire. Yes, the breaker triped but too late.

Also, don't forget that there are many unsuspecting grounds. The faucet,
dings 
and scrapes on the porcelain or enamel, wet wood, concrete, stucco,
morter etc. 
Those are all better conductors than tap water.

Hans

______________________________ Reply Separator
_________________________________
Subject: GFIs, Hairdryers, and Bathtubs ...
Author:  Non-HP-dmckean ([email protected]) at
HP-ColSprings,mimegw5
List-Post: [email protected]
Date:    8/13/97 9:51 AM


Recently somewhere back in the news (couple of weeks ago), 
two children died when one of them used a hairdryer in 
the tub.  A discussion this accident with some lead me 
to a counter-intuitive result from my experience in 
product safety. 
     
************************************************** 
     
Given Situation #1: 
     
1. Person in a tub of water sitting at the opposite 
   end of the tub than the drain. 
     
2. The tub is ungrounded with water in it.  Ungrounded 
   meaning that the drain is plastic piping. 
     
3. A 2-wire hair dryer (either On or OFF) is dropped 
   into  the water at the drain end of the tub. The person 
   in the tub is neither in contact with the hairdryer, 
   not anything that would be grounded. 
     
   The hairdryer has a plastic case. 
     
Result: 
     
1. Since there is no path to ground from the hairdryer 
   through the person in the tub to ground, no current 
   should flow *thru* the person in the tub. The person 
   is in no harm.  
     
2. Since no current is flowing through ground, 
   the GFI won't trip.  If the water allows sufficient 
   current to flow by shorting between the HOT and 
   NEUTRAL in the hairdryer, the breaker will trip.  
     
************************************************** 
     
Given Situation #2: 
     
Same as situation #1 except that the drain is now 
a grounded metal pipe. 
     
Is there a sufficient parallel path to be lethal 
to the person in the tub?  Seems as though the 
parallel path for the hairdryer is straight to 
the drain. 
     
Result: 
     
1. Person is still unharmed. 
     
2. GFI trips. 
     
************************************************** 
     
Are my conclusions correct? 
     
Is the only time one can be electrocuted in a tub 
when they are in contact with a ground and holding 
the hairdryer? 
     
Is a person really killed in a tub with hairdryer 
by drowning rather than electrocution? 
     
I'm beginning to doubt that I know exactly how 
a person is killed in a tub with a hairdryer. 
     
Or, am I making this way more complicated 
than it is? 
     
Comments? 
     
     
     
     

Reply via email to