I too have had problems with TUV requiring brown/blue, so it became a
company standard from the inlet to the first component. UL and CSA had no
problem with this arangement.

> ----------
> From:         [email protected][SMTP:[email protected]]
> Reply To:     [email protected]
> Sent:         Thursday, July 30, 1998 8:02 AM
> To:   [email protected]
> Cc:   [email protected]
> Subject:      Re: EN60950 - Internal wiring colours
> 
> [email protected],Internet writes:
> >Unless I am missing something, I see no reason why I can't allow our
> >North American black and white wiring colours to be used for the line
> >and neutral wiring INSIDE a product, even though that product is
> >destined for CE-marking and European sales.  EN60950 only limits the use
> >of green/yellow wiring.  As far as I can see, it does not mandate the
> >blue/brown colour code.
> >
> >Does anyone disagree?  Thanks.
> >
> >
> >Regards,
> >
> >Jim Eichner
> >Statpower Technologies Corporation
> >[email protected]
> >http://www.statpower.com
> >Any opinions expressed are those of my invisible friend, who really
> >exists.  Honest.  
> >
> >
> Jim,
> 
> I know of no reason you cannot use other than brown / blue inside your
> product. I have had occasion to use both intermixed in a product. The TUV
> guys preferred that brown/blue was the mains wiring up to the primary of
> the transformer. The secondary side was mixed with black/white.
> 
> Never saw a requirement in writing but eventually got tired of explaining
> so we now use brown/blue exclusively for anything mains related. In fact,
> we prohibit brown/blue for use on any other voltage than mains. And as
> always, green / yellow is the only earth ground color; again, its use is
> exclusive. We have no problem from CSA with this scheme.
> 
> Regards,
> Scott [email protected]
> 