Here's how a local Denver area OSHA inspector explained it to me...

OSHA considers worker safety to be the responsibility of the company
employing them. Electrical safety for both the facility and it's
infrastructure and the equipment connecting into it's electrical system is
the responsibility of the work-place.  

Subpart S-Electrical 
ref. 1910.302(a) scope: states that this section covers electrical
installations and utilization equipment.

ref. 1910.399 definition for utilization equipment: equipment which utilizes
electric energy for mechanical, chemical, heating, lighting, or similar
useful purpose.

Comment:  Most any equipment that plugs into a 110V outlet has useful
purpose.

ref. 1910.303 (a) The conductors and "equipment" required or permitted by
this subpart shall be "acceptable" if "approved".

ref. 1910.399: "Equipment" is defined as, material, fittings, devices,
appliances, fixtures, apparatus, and the like, used as a part of, or "in
connection" with an electrical installation. 

Comment:  Anything that plugs into a standard 110V outlet is in connection
with an electrical installation.

ref. 1910.399: "Approved" is defined as Acceptable to OSHA. 

ref. 1910.399: "Accepted" is defined as accepted, certified or listed by a
nationally recognized testing laboratory (NRTL).  

In the case of purchased equipment which is not preapproved by a NRTL, said
equipment may be inspected or tested on site by a NRTL, or federal, state
municipal or local safety authority.  In the case of equipment manufactured
on site for on site uses, said equipment may deemed safe if tested or
inspected by methods indicated  in the previous statement or by the
manufacturer.  If the latter method is to be used testing must be per
national safety standards and test inspection information must be kept on
file, on site and made available to OSHA inspectors if called upon to do so.
 
Although they have the authority to do so, OSHA does not routinely inspect
business for compliance.  They do not have the time, money or personnel to
do so.
OSHA will check a business for safety concern/s if there is a complaint from
an employee within the organization.  In the latter case the extent of the
investigation is usually limited to the review of the complaint, but OSHA as
always has the option to look as far as they choose into safety aspects of
the business.

If there is a serious injury or death as a result of a safety related
concern OSHA may then look into all aspects of safety within the business.
This includes not only the physical aspects of safety (which would include
electrical safety hazards such as unsafe equipment), but records (e.g.
training, injury, illness, etc.)as well. 

Gail Birdsall
Compliance Engineer
Hach Co.

-----Original Message-----
From: geor...@lexmark.com [mailto:geor...@lexmark.com]
Sent: Tuesday, August 17, 1999 7:11 AM
To: emc-p...@majordomo.ieee.org
Subject: Re: U.S. National Product Safety "Laws"



This discussion is opening more issues than it is closing.
No one can merely "skim" through 29 CFR 1900 or the NEC and
find what they are looking for, so I may have missed what I
was looking for given the time that I had.

Like Doug, I cannot find a single definitive statement, or
combination thereof, that would require an "appliance", in
this case a PC or peripheral, to meet any requirement other
earth gounding and/or double insulation.

Likewise with the NEC.  Section 645 addresses ITE.  A good deal
is said about the "installation" for ITE, but little about the
actual ITE equipment itself.  Items that ARE mentioned include
that all exposed noncurrent-carrying metal parts of an ITE
"system" must be grounded or double insulated (645-15), and that
a marking of rated voltages etc. must be affixed (645-16).

So here is the challenge.  Can anyone "prove" that 29 CFR 1900
or the NEC specifically requires ITE to meet more than some
grounding/marking requirements, or be required to be approved by
an NRTL.  Proof is citing clearly stated sections obviously
applicable to typical ITE products.  Sorry, but vague references
to something "I once saw....." are not allowed.

Like many product safety professionals, I received much verbal
input on the "known" requirements when I took this position. It
is becoming more obvious that some "facts" passed down through
generations of PSEs may not be entirely accurate.  They are
definitely not clear, or this discussion would not be taking
place.

BTW, I would like the phone number of any lawyer capable of
providing "definitive" answers.


---------------------- Forwarded by George Alspaugh/Lex/Lexmark on 08/17/99
08:47 AM ---------------------------

roger.viles%wwgsolutions....@interlock.lexmark.com on 08/17/99 05:03:28 AM

Please respond to roger.viles%wwgsolutions....@interlock.lexmark.com

To:   dmckean%corp.auspex....@interlock.lexmark.com
cc:   emc-pstc%majordomo.ieee....@interlock.lexmark.com
Subject:  Re: U.S. National Product Safety "Laws"







Doug,

I agree entirely!

Yesterday I sent the below mail to a fellow emc-pstc groupie:


"I have struggled through the OSHA webpages before, including SubPart S:

SubPart Title: Electrical - Design Safety Standards for Electrical Systems

where it does clearly say:
"Approval. The conductors and equipment required or permitted by this
subpart
shall be acceptable only if approved."

Under definitions, approved refers to acceptable which is defined as:
"(i) If it is accepted, or certified, or listed, or labeled, or otherwise
determined to be safe by a nationally recognized testing laboratory"

So it is quite clear that conductors and equipment for electrical systems
must
be listed or similar.

However nowhere does it make clear what is covered under "equipment". Is a
PC
covered? Probably yes. Is a palmtop with mains adaptor covered? Maybe. Is a
pocket calculator covered? Surely not."

So I too would like a definitive answer! (Well, if the answer is definitive,
it
probably comes from a lawyer, so I might not like it!).

Regards,

Roger Viles
WWG

Doug McKean <dmck...@corp.auspex.com> on 17/08/99 04:48:09

Please respond to Doug McKean <dmck...@corp.auspex.com>

To:   emc-p...@majordomo.ieee.org
cc:    (bcc: Roger Viles/PLY/Global)

Subject:  Re: U.S. National Product Safety "Laws"

Dear Fellow Professionals,

Let me be the devil's advocate for the moment.
I normally do not like to pick apart standards,
but this one has been kicking around my mind
for years.

I will refer all to the following websites so we're
all on the same playing field.

 http://www.osha-slc.gov/OshStd_toc/OSHA_Std_toc.html
 http://www.osha-slc.gov/OshStd_toc/OSHA_Std_toc_1910_SUBPART_S.html

Would you please note that in 29 CFR 1910.301
"Introduction", that the "practical safeguarding
of employees in their workplaces" has four parts to it:

"...

    a) Electrical systems.
    b) Safety-realted work practices.
    c) Safety-related maintenance requirements.
    d) Safety requirements for special equipment.

 ..."

Of the four major divisions for safeguarding employees,
please note the first one - "Electrical Systems".

As stated in 29 CFR - 1910.399 "Definitions", a "system"
is defined as

"Utilization system. A utilization system is a system
 which provides electric power and light for employee
 workplaces, and includes the premises wiring system
 and utilization equipment."

Had the standard used the word "equipment", then as
such 29 CFR - 1910.399 "Definitions" would have used
the following definition

"Utilization equipment. Utilization equipment means
 equipment which utilizes electric energy for mechanical,
 chemical, heating, lighting, or similar useful purpose."

Therefore, people, I submit that since 29 CFR 1910 directs
it's attention to "systems", it is strictly concerned with
that which provides electrical power or lighting and does
NOT concern itself with "equipment", i.e. that utiliizes
said power.

Comments?

Regards,  Doug McKean



---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).