Not well addressed. You could
- request a formal interpretation from NFPA asking if light blue leads would be
sustantially equivlaent to white or gray as described in 400-22c, or
- request a code change to appear elsewhere in the code.

Bob

[email protected] wrote:

> The referenced NFPA 70 section 400-22c seems to apply only to appliances with
> jacketed cords. What about industrial equipment?
>
> Mike Sherman
> FSI International
>
> In a message dated 4/19/1999 1:32:11 PM Central Daylight Time,
> [email protected] writes:
>
> << About twenty years ago, the a group in the cable and computer industries
>  gathered together all the colors used worldwide for conductor identification
> and
>  tried to come up with a worldwide compromise. The light blue(neutral), brown
>  (phase), and green/yellow (earth) were the best choice to avoid miswiring
>  somewhere in the world. The US NEC was changed specifically to clarify this
>  compromise (ref.  NFPA 70 clause 400-22c), taking light blue as close to
> white
>  or gray.
>
>  You can probably get away with sending the US customary colors (white, black,
>  green) to some countries, but you will have to specifically check codes in
> each
>  case. Don't think an answer from one European country will answer for all of
>  Europe. Note: NFPA is a US originated organization working to promote itself
>  internationally, but does not apply to Europe except in some specific cases
> of
>  harmonization. The absence of a European Norm does not mean no laws apply.
>  National or local laws would be applicable.
>
>  Since we have a well researched solution, why fight it? Misunderstandings
> when
>  it comes to wiring power cords can be lethal, a terrible price to pay for
>  getting away with something less.
>
>  Bob Johnson
>
>  "Crane, Lauren" wrote:
>
>  > > Is it acceptable to ship equipment to Europe with neutral conductors
> (hook
>  > > up wire) that is white, particularly if the ends are marked with the
>  > > letter 'N' ?
>  > >
>  > > It seems to me that this would be acceptable to both the Machinery
>  > > Directive and the Low Voltage Directive. Neither of these directives have
>  > > a requirement for wire color in their Essential Requirements.
>  > >
>  > > Marking neutrals in this manner conforms to NFPA-79, an appropriate,
>  > > though US National, design standard for large semiconductor manufacturing
>  > > equipment.
>  > >
>  > > Conforming to NFPA-79, I think, demonstrates adequately addressing
>  > > electrical hazards to the extent of the concern of the Machinery
> Directive
>  > > and Low Voltage Directive
>  > >
>  > > EN 60204 requires that neutrals be colored light blue ONLY IF COLOR IS
>  > > USED TO IDENTIFY THEM. Quoting section 15.2.3 "Where a circuit includes a
>  > > neutral conductor identified by colour, the colour shall be light
>  > > blue...".
>  > >
>  > > Note that the definitions section of EN 60204 (3.38) says that the
> neutral
>  > > conductor is assigned the symbol 'N'.
>  > >
>  > > This is echoed in EN60439 "Specification for Low voltage switch gear and
>  > > control gear assemblies Part 1. Specification for type-tested and
>  > > partially type-tested assemblies." section 7.6.5.2 which says in part
> "Any
>  > > neutral conductor of the main circuit should be readily distinguishable
> by
>  > > shape, location, marking or colour..."
>  > >
>  > > I would be interested to know if anyone has experiences with this issue.
>  > >
>  > > Thanks in advance.....
>  > >
>  > > Lauren Crane
>  > > Eaton Corporation
>  > >
>  > > [email protected]
>   >>
>
> ---------
> This message is coming from the emc-pstc discussion list.
> To cancel your subscription, send mail to [email protected]
> with the single line: "unsubscribe emc-pstc" (without the
> quotes).  For help, send mail to [email protected],
> [email protected], [email protected], or
> [email protected] (the list administrators).


---------
This message is coming from the emc-pstc discussion list.