Graham, 

Thanks for the comments!

Regarding the meaning of "N." I agree that those un-trained to work on
electrical systems might not understand the meaning of this character, but
it is the official 'symbol' for denoting a neutral conductor according to EN
60204-1, 1997 section 3.35 (and IEC 60204-1) and is, therefore, an
internationally accepted (and understood?!). At least, of course, within the
EN/IEC communities.
 
If standardized symbology is not reasonably acceptable for use, designers
become bound to the colloquial understanding of lay-personnel!

Regards
Lauren Crane

> -----Original Message-----
> From: Graham Rae Dulmage [SMTP:[email protected]]
> Sent: Monday, April 19, 1999 5:51 PM
> To:   Robert Johnson
> Cc:   Crane, Lauren; IEEE
> Subject:      Re: White neutrals in Europe
> 
> Both responses given so far are correct. It would be nice if we all
> eventually come
> to common technical agreement on common technical ground overtime. I worry
> that we sometimes push the technical aside and rush in with alternate
> opinions. In
> this
> case I see a lot of danger in shipping the product as described. One point
> could
> be what "N" means or stands for as marked on the cable may not be
> understood
> in another country that doesn't use English as its national language.
> Better safe
> than sorry. I once had a client who asked for instructions for proper
> power cords
> and voltage settings for 110 countries to be set up on a large
> spreadsheets. They
> provided the country names as they wanted them to be listed. I pointed
> out that in one instance 2 countries had the same first name and this
> could cause
> major problems. I lost the arguement until manufacturing did exactly what
> I thought
> they would, picked the wrong configuration list and on installation the
> whole
> shipped product blew up at a cost of $ 50K US plus the downtime for the
> customer who was using the equipment. I changed the country name to avoid
> confusion.
> 
> Regards
> 
> 
> G. Rae  Dulmage, B. Comm.,
> President TelApprove Services Corporation
> (613) 257 3015
> http://www.angelfire.com/on/telapprove
> 
> Robert Johnson wrote:
> 
> > About twenty years ago, the a group in the cable and computer industries
> > gathered together all the colors used worldwide for conductor
> identification and
> > tried to come up with a worldwide compromise. The light blue(neutral),
> brown
> > (phase), and green/yellow (earth) were the best choice to avoid
> miswiring
> > somewhere in the world. The US NEC was changed specifically to clarify
> this
> > compromise (ref.  NFPA 70 clause 400-22c), taking light blue as close to
> white
> > or gray.
> >
> > You can probably get away with sending the US customary colors (white,
> black,
> > green) to some countries, but you will have to specifically check codes
> in each
> > case. Don't think an answer from one European country will answer for
> all of
> > Europe. Note: NFPA is a US originated organization working to promote
> itself
> > internationally, but does not apply to Europe except in some specific
> cases of
> > harmonization. The absence of a European Norm does not mean no laws
> apply.
> > National or local laws would be applicable.
> >
> > Since we have a well researched solution, why fight it?
> Misunderstandings when
> > it comes to wiring power cords can be lethal, a terrible price to pay
> for
> > getting away with something less.
> >
> > Bob Johnson
> >
> > "Crane, Lauren" wrote:
> >
> > > > Is it acceptable to ship equipment to Europe with neutral conductors
> (hook
> > > > up wire) that is white, particularly if the ends are marked with the
> > > > letter 'N' ?
> > > >
> > > > It seems to me that this would be acceptable to both the Machinery
> > > > Directive and the Low Voltage Directive. Neither of these directives
> have
> > > > a requirement for wire color in their Essential Requirements.
> > > >
> > > > Marking neutrals in this manner conforms to NFPA-79, an appropriate,
> > > > though US National, design standard for large semiconductor
> manufacturing
> > > > equipment.
> > > >
> > > > Conforming to NFPA-79, I think, demonstrates adequately addressing
> > > > electrical hazards to the extent of the concern of the Machinery
> Directive
> > > > and Low Voltage Directive
> > > >
> > > > EN 60204 requires that neutrals be colored light blue ONLY IF COLOR
> IS
> > > > USED TO IDENTIFY THEM. Quoting section 15.2.3 "Where a circuit
> includes a
> > > > neutral conductor identified by colour, the colour shall be light
> > > > blue...".
> > > >
> > > > Note that the definitions section of EN 60204 (3.38) says that the
> neutral
> > > > conductor is assigned the symbol 'N'.
> > > >
> > > > This is echoed in EN60439 "Specification for Low voltage switch gear
> and
> > > > control gear assemblies Part 1. Specification for type-tested and
> > > > partially type-tested assemblies." section 7.6.5.2 which says in
> part "Any
> > > > neutral conductor of the main circuit should be readily
> distinguishable by
> > > > shape, location, marking or colour..."
> > > >
> > > > I would be interested to know if anyone has experiences with this
> issue.
> > > >
> > > > Thanks in advance.....
> > > >
> > > > Lauren Crane
> > > > Eaton Corporation
> > > >
> > > > [email protected]
> > >
> > > ---------
> > > This message is coming from the emc-pstc discussion list.
> > > To cancel your subscription, send mail to [email protected]
> > > with the single line: "unsubscribe emc-pstc" (without the
> > > quotes).  For help, send mail to [email protected],
> > > [email protected], [email protected], or
> > > [email protected] (the list administrators).
> >
> > ---------
> > This message is coming from the emc-pstc discussion list.
> > To cancel your subscription, send mail to [email protected]
> > with the single line: "unsubscribe emc-pstc" (without the
> > quotes).  For help, send mail to [email protected],
> > [email protected], [email protected], or
> > [email protected] (the list administrators).
> 
> 
> ---------
> This message is coming from the emc-pstc discussion list.
> To cancel your subscription, send mail to [email protected]
> with the single line: "unsubscribe emc-pstc" (without the
> quotes).  For help, send mail to [email protected],
> [email protected], [email protected], or
> [email protected] (the list administrators).

---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected]
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to [email protected],
[email protected], [email protected], or
[email protected] (the list administrators).

Reply via email to