Cables under raised floors are currently the subject of a proposal to change
the code regarding them as follows:
12-101 -( 645-5(d)(5)):
SUBMITTER: Rick Zupan, Lake Oswego, OR
RECOMMENDATION:
Revise as follows:
645-5(d)(5) Cable, other than those covered in (b) and (2) and those complying
with (a), (b) and (c) below, shall be listed as type DP cable having adequate
fire-resistant characteristics suitable for use under raised floors of an
information technology equipment room.
SUBSTANTIATION:
The local authority having jurisdiction has decided that barring explicit
language allowing it flexible cords cannot be used to plug into underfloor
receptacles, this should correct this.

The NEC code panel 12 statement in response reads:
"Requirements for the use of listed DP cable were put into the NEC because of
the panel's concerns that cables under the raised floor should pass the
vertical flame test. Permitting other than DP cables would not fall within the
purpose of the Code as outlined in 90-1. The Code already contains explicit
language prohibiting the use of other than DP-type cable."

This response is open for comment and will be acted upon in a meeting in
December regarding disposition of this and other proposed changes to the NEC.
Comments MUST be received by NFPA by 27 Oct 00. To comment, see
http://www.nfpa.org/submitterapp2.html
For other code information see http://www.nfpa.org/Codes/

My personal views are as follows:
The panel statement says that only DP cables but not flexible cords are
permitted beneath raised floors. This is historically incorrect.
- The allowance of receptacles beneath raised floors, 645-5(d)(2), prior to the
development of DP cables has always implied flexible cords would be permitted
below raised floors in order to plug into those receptacles.
- DP cables have not been intended for use as power cords. They were introduced
recently to the code and ITE standards for use as interconnecting cables.
- Type DP cables are not present in article 400, are not hard service cord
types, and therefore would not be usable for power cords on machines outside
computer rooms. Manufacturers would have to either market two machine types or
institute cord replacement in the field. Field rewiring is significantly less
safe and dependable than that done and tested in manufacturing facilities.
- During the introduction of DP cables it was never mentioned that DP cables
were required to replace flexible cords. Prohibiting the use of flexible cords
for power cords below raised floors, if it is desired by the committee, should
be the subject of a new proposal with full consideration of its impact on
current installations and providing a timetable for implementation.
- No current products or installations use DP cables for power cords since such
construction is not allowed by UL 1950. The only power cords presently
permitted by UL 1950 for floor mounted equipment are: SJ, SJE, SJO, SJOO, SJT,
SJTO, SVTOO, S, SE, SO, SOO, ST, STO, STOO.
- The interpretation that only DP cables could be used for power cordage below
raised floors would result in placement of receptacles and power cords above
the floor, increasing trip hazards and increasing the risk of damage to cords.
- Rejecting this proposal with the publication of the current panel statement
would have the result of a change to the code and current usage.
- Standard power cords run below raised floors constitutes essentially 100% of
current usage and has not been shown to be a problem.
I recommend accepting 12-101 as a correction to an error in the current code.


[email protected] wrote:

> Is it permissible to place electrical receptacles under the raised floor of
> a computer room?  Can power cords pass through openings in the raised floor
> or do all power connections need to be in conduit?  I have received two
> opinions; one stating that receptacles must be accessible above floor level
> and the other stating that receptacles can be placed below the floor.
>
> The United States National Electrical Code is a bit vague on the subject,
> although Article 645-5 (d) (2) seems to imply that conduit is only required
> up to the receptacle.  I can find no references to raised floor
> installations in the Canadian Electrical Code or BS 7671, IEE Wiring
> Regulations.
>
> Ted Eckert
> Regulatory Compliance Engineer
> American Power Conversion Corporation
> [email protected]
>


-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Jim Bacher:              [email protected]
     Michael Garretson:        [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]

Reply via email to