I read in !emc-pstc that Luiz Claudio Bonilla de Araujo
<[email protected]> wrote (in <[email protected]
.org>) about 'IEC 417 Protective Earth Symbol' on Wed, 4 Dec 2002:
>I have a doubt concerning IEC60335-1, paragraph 7.8, which is reproduced 
>below: 
>
>7.8 Except for TYPE Z ATTACHMENT, terminals used for connection to the 
>supply mains shall be indicated as follows: 
>
>terminals intended exclusively for the neutral conductor shall be indicated 
>by the letter N; 
>protective earthing terminals shall be indicated by the IEC 417 Protective 
>Earth Symbol. 
>Question: 
>
>Is it possible to have two protective earth symbols in the same appliance? 

Yes, the standard clearly says 'terminals'. If it said 'terminal', there
might be some doubt, but I can't see any reason why two terminals should
not be present, *IF*, when the protective earth conductor is connected
to the 'wrong' earth terminal in error, the product is still safe.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:
    http://ieeepstc.mindcruiser.com/
    Click on "browse" and then "emc-pstc mailing list"

Reply via email to