Just some anecdotal info . . . 
There was an occassion at a previous employ where, due to a brief mental 
hiccup on the part of several folks, a printed circuit get fabricated with
not enough spacing 
(damn close though to the required) between a mains trace and secondary in
an 
internal layer for a card-cage backplane. 
The discussion that ensued with knowledgable folks at a well-known NRTL
brought forth the following:
a) Extra tests - thermal aging and thermal cycling tests need to be
performed. Time consuming and expensive.
b) Tight quality control on the part of the fabricator to
ensure layer dimensions, adhesion, etc.
Reduces flexbility to change vendors at a moment's
notice.
c) Routine electric strength testing by us.
 
In short, they noted that while possible, it is difficult to maintain the
pollution degree 1 in a printed circuit. Typically the pollution degree
is applied to 'potted' items.
 
Taking all into consideration it was easier for us (and less expensive)
to respin the board. 
 
John Juhasz
Fiber Options
Bohemia, NY
 
 
 
 -----Original Message-----
From: [email protected] [mailto:[email protected]]
Sent: Friday, February 01, 2002 12:50 PM
To: [email protected]
Cc: [email protected]
Subject: Re: Pollution Degree vs. Creapage Distance



In a message dated 1/31/2002, Rick Busche writes:




Does the application of a solder mask allow for a change from pollution
degree 2 to pollution degree 1?  I understand that conformal coating
requires significant testing when used to reduce spacings per table 7, but
in this case I am only asking if solder mask can be used to improve the
pollution concern.





Hi Rick:

You do not mention which standard you are looking at, but if it is one of
the IEC 950 derivatives there are some clauses that specifically address the
questions you have.  For example, in EN 60950, Third Edition, clause
2.10.5.3 addresses printed circuit boards, and clause 2.10.6 addresses
solder mask.  To the extent you can use inner layers, clause 2.10.5.3 should
provide you some of the relief you seek.  

I have not ever tried to qualify a solder mask under clause 2.10.6 due to
the burden of the additional tests, but you may want to consider it.



Joe Randolph