Hi Folks

Having discussed the subject with John Woodgate before sending this message,
I have now to correct his statement below that the official interpretation
is that the LVD applies only to the supply side of equipment:- It does not,
and it does apply to both the supply AND the output side.

This is confirmed by the Feb 2001 version (which is later than the draft
that JW has of the same document) of the Commission "Guidelines on the
Application of Council Directive 73/23/EEC", which can be downloaded in PDF
form from the following URL:
http://europa.eu.int/comm/enterprise/electr_equipment/lv/guides/index.htm

See Numbered Page 3, "Which products are covered?", viz:

"7. The Directive applies to all electrical equipment6 designed for use with
a
voltage rating of between 50 and 1000 V for alternating current and between
75 and 1500 V for direct current. Voltage ratings refer to the voltage of
the
electrical input or output, not to voltages which may appear inside the
equipment.

Following discussions with Member States the Commission has taken the
position that the term "designed for use with a voltage range" shall be
understood at equipment having either a rated input voltage or a rated
output
voltage inside this voltage range. Internally there may be higher voltages.
Battery operated equipment outside the voltage rating is obviously outside
the
scope of the LVD. Nevertheless, the accompanying battery-charger as well as
equipment with integrated power supply unit within the voltage ranges of the
Directive, are in the scope of the LVD. This applies also, in the case of
batteryoperated
equipment with supply voltage rating under 50 V AC and 75 V DC,
for their accompanying power supply unit (e.g. Notebooks). "

The above guideline confirms that either the input OR the output voltage -
but not the internal voltages - is the critical factor. 

(Any one who wants to discuss this or related points further can contact me
on, or off-line.)

Regards

John Allen
Technical Consultant
Electromagnetics, Safety and Reliability Group
ERA Technology Ltd
Cleeve Rd
Leatherhead
Surrey KT22 7SA
Tel:    +44 (0) 1372-367025 (Direct)
        +44 (0) 1372-367000 (Switchboard)
Fax:    +44 (0) 1372-367102 (Fax)


-----Original Message-----
From: John Woodgate [mailto:[email protected]]
Sent: 09 October 2002 08:37
To: [email protected]
Subject: Re: CE Mark vs. e-Mark



I read in !emc-pstc that Jim Eichner <[email protected]> wrote (in
<67C475A5ECE7D4118AEC0002B325CAB603510F93@BCMAIL1>) about 'CE Mark vs.
e-Mark' on Tue, 8 Oct 2002:
> By the way, the LVD is in fact
>applicable, because the product in question creates 120Vac from the 12Vdc
it
>gets from the car.  

No. Although the wording of the LVD implies that the voltage limits
apply to internally-generated voltages, there is now an official
'interpretation' that they apply only to supply voltages.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk

Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:
    http://ieeepstc.mindcruiser.com/
    Click on "browse" and then "emc-pstc mailing list"

_____________________________________________________________________
This e-mail has been scanned for viruses by the WorldCom Internet Managed
Scanning Service - powered by MessageLabs. For further information visit
http://www.worldcom.com


*************************************************************************
Copyright ERA Technology Ltd. 2002. (www.era.co.uk). All rights reserved. 
The information supplied in this Commercial Communication should be treated
in confidence.
No liability whatsoever is accepted for any loss or damage 
suffered as a result of accessing this message or any attachments.

_____________________________________________________________________
This e-mail has been scanned for viruses by the WorldCom Internet Managed 
Scanning Service - powered by MessageLabs. For further information visit 
http://www.worldcom.com

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:
    http://ieeepstc.mindcruiser.com/
    Click on "browse" and then "emc-pstc mailing list"

Reply via email to