Hi Greg:
> > >Why does "True SELV" require basic insulation
> > >between SELV and earth?
> > >
> > >What is the hazardous voltage source, and what
> > >is the current path through the body if that
> > >basic insulation should fail?
> > >
> > >
>
> I believe (and I could be wrong) that it's a philosophy of keeping SELV
> intact under single fault conditions. If there's a single fault
bridging
> mains and earth, then an SELV circuit is exposed to mains voltage unless
> there is basic insulation protecting it. Since it is estamited that
close to
> 50% of the homes in the US have improperly grounded outlets, the earth
> connection itself is not taken into consideration as a reliable means of
> protection. In other words, for the purposes of the standard, an open
earth
> connection is not considered a fault.
Thanks for the explanation.
One implication of this explanation is that
an open earth connection is not a fault
condition, but a normal condition. (Failure
of basic insulation is the fault condition.)
No I think not -
1) Standards are not designed on the premise that they will not be obeyed.
2) Please remember that Earth Leakage current is limited so that it will not
be a hazardous source in the event of failure of Safety Earth Ground.
3) Remember also that SELV may reach an upper limit of 120Volts (for a
limited time) under single fault conditions - therefore the insulation
between SELV and ground must be adequate to prevent breakdown and
(potential) sustained fault currents.
This would suggest that it would be better to
double/reinforce insulate the mains against
earth, in which case SELV could be earthed.
Insulation is good and can (if one is careful not to compromise its
integrity - e.g. a detached wire/connector, reduced insulation) simplify
the equipment construction.
Please refer to Conformity August Show Issue p 38.
-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.
Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/
To cancel your subscription, send mail to:
majord...@ieee.org
with the single line:
unsubscribe emc-pstc
For help, send mail to the list administrators:
Ron Pickard: emc-p...@hypercom.com
Dave Heald: davehe...@attbi.com
For policy questions, send mail to:
Richard Nute: ri...@ieee.org
Jim Bacher: j.bac...@ieee.org
All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on "browse" and then "emc-pstc mailing list"