If you have shock level differences between the grounds in two different buildings, either an entire building isn't connected to an earth electrode, or someone is paying a whopping electric bill to heat up mother earth. I suspect the shock situation you were talking about was a power cross condition, either to the cable or within equipment. I hope it was diagnosed and fixed.
The voltage differences between two buildings are generally very low, on the order of a couple volts, but due to fractional ohm impedances are capable of very high currents. Building maintenance procedures should routinely be checking for ground currents since they indicate faults in the power system. Note that in accordance with IEC 62102, 10base2 is an SELV circuit and should not be used for exposed plant (between building) wiring. Ethernet distance specs and application recommendations also go against exposed plant wiring. Ethernet 10base5 is considered a TNV-1 circuit and suitable for exposed plant use, is insulated and requires single point grounding. Optical fiber is a better recent development and the best answer for exposed plant lines these days. Note that IEC 62102 provides an extensive list of interconnect circuit types and what category they fit into with regard to shock level (SELV, TNV, hazardous, etc). It's an important reference for any engineer designing interconnect circuits in determining isolation needs. Bob Johnson ITE Safety From: [email protected] [mailto:[email protected]] On Behalf Of Knighten, Jim L Sent: Wednesday, March 05, 2003 7:51 PM To: Rich Nute Cc: [email protected]; [email protected] Subject: RE: Ethernet coax connection Rich, I think you must be correct. I do have anecdotal evidence of persons being "knocked on their butts" by grabbing hold of an Ethernet coax in a large facility and trying to connect it to a computer. My experience is in EMC and the 10Base2 Ethernet (coax) is a persistent offender. (Actually, the twisted pair stuff has its own set of EMC problems.) Regards, Jim Jim Knighten, Ph.D. Teradata, a Division of NCR http://www.ncr.com 17095 Via Del Campo San Diego, CA 92127 USA Tel: 858-485-2537 Fax: 858-485-3788 [email protected] -----Original Message----- From: Rich Nute [mailto:[email protected]] Sent: Wednesday, March 05, 2003 4:31 PM To: Knighten, Jim L Cc: [email protected]; [email protected] Subject: Re: Ethernet coax connection Hi Jim: > It is a potential shock hazard if the coax run is long and runs from > building to building (for instance) where the ground potentials may be > different in the different buildings. One can develop a large potential on > the shield of the cable, so that if you put yourself between the cable > shield and ground you may get a strong shock. That is the reason for > isolating the shield from more than one direct connection to ground. It is > a real issue. I don't believe the issue is that of electric shock. I don't believe the current and resistance of the neutral are high enough to develop 30 volts (the shock hazard limit). Instead, I believe the problem is that, with two connections, the shield is in parallel with the neutral. That means that some of the neutral current will pass through the shield, and will likely open a PWB trace somewhere. In the process, the PWB trace heating may start a fire. I believe the circuit is: (You may not be able to read this schematic if your mail reader is not set for plain ASCII text.) L Bldg A +---------+----------------------------+ | | | | | | | | | | (~) 120 V | | | load | | | | | | | |N | | +-------------+--------+---------+-----+ |utility | | | Bldg A | |ground | | | ground | |rod | | | rod |PE BNC shield ----- | | ----- +----->>-------+ --- | | --- | - | | - | | | | | | | | | | | | L Bldg B | +----------------------------+ | | | | | | | | | | | | | | load | | | | | | | | | N | | +--------+---------+-----+ | | Bldg B | | | ground | | | rod |PE | ----- +----->>-------+ --- BNC shield - You can see from the schematic that the shield is in parallel with both the neutral and the earth-ground. Being in parallel, it will carry some of the neutral current, depending on the respective resistances. Because of both the neutral and the earth-ground, the voltage should never approach 30 volts (1/4 of the mains voltage). But, there can be a very high current in the shield of the BNC cable. Best regards, Rich This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: [email protected] with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: [email protected] Dave Heald: [email protected] For policy questions, send mail to: Richard Nute: [email protected] Jim Bacher: [email protected] Archive is being moved, we will announce when it is back on-line. All emc-pstc postings are archived and searchable on the web at: http://www.ieeecommunities.org/emc-pstcTitle: RE: Ethernet coax connection
If you have shock level differences between the grounds in two different
buildings, either an entire building isn't connected to an earth electrode,
or someone is paying a whopping electric bill to heat up mother earth. I
suspect the shock situation you were talking about was a power cross
condition, either to the cable or within equipment. I hope it was diagnosed
and fixed.
The voltage differences between two buildings are generally very low, on the
order of a couple volts, but due to fractional ohm impedances are capable of
very high currents. Building maintenance procedures should routinely be
checking for ground currents since they indicate faults in the power system.
Note that in accordance with IEC 62102, 10base2 is an SELV circuit and
should not be used for exposed plant (between building) wiring. Ethernet
distance specs and application recommendations also go against exposed plant
wiring. Ethernet 10base5 is considered a TNV-1 circuit and suitable for
exposed plant use, is insulated and requires single point grounding. Optical
fiber is a better recent development and the best answer for exposed plant
lines these days.
Note that IEC 62102 provides an extensive list of interconnect circuit types
and what category they fit into with regard to shock level (SELV, TNV,
hazardous, etc). It's an important reference for any engineer designing
interconnect circuits in determining isolation needs.
Bob Johnson
ITE Safety
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Knighten, Jim L
Sent: Wednesday, March 05, 2003 7:51 PM
To: Rich Nute
Cc: [email protected]; [email protected]
Subject: RE: Ethernet coax connection
Rich,
I think you must be correct. I do have anecdotal evidence of persons being
"knocked on their butts" by grabbing hold of an Ethernet coax in a large
facility and trying to connect it to a computer.
My experience is in EMC and the 10Base2 Ethernet (coax) is a persistent
offender. (Actually, the twisted pair stuff has its own set of EMC
problems.)
Regards,
Jim
Jim Knighten, Ph.D.
Teradata, a Division of NCR http://www.ncr.com
17095 Via Del Campo
San Diego, CA 92127
USA
Tel: 858-485-2537
Fax: 858-485-3788
[email protected]
-----Original Message-----
From: Rich Nute [mailto:[email protected]]
Sent: Wednesday, March 05, 2003 4:31 PM
To: Knighten, Jim L
Cc: [email protected]; [email protected]
Subject: Re: Ethernet coax connection
Hi Jim:
> It is a potential shock hazard if the coax run is long and runs from
> building to building (for instance) where the ground potentials may be
> different in the different buildings. One can develop a large potential
on
> the shield of the cable, so that if you put yourself between the cable
> shield and ground you may get a strong shock. That is the reason for
> isolating the shield from more than one direct connection to ground. It
is
> a real issue.
I don't believe the issue is that of electric shock. I don't believe the
current and resistance of the neutral are high enough to develop 30 volts
(the shock hazard limit).
Instead, I believe the problem is that, with two connections, the shield is
in parallel with the neutral. That means that some of the neutral current
will pass through the shield, and will likely open a PWB trace somewhere.
In the process, the PWB trace heating may start a fire.
I believe the circuit is:
(You may not be able to read this schematic if your mail reader is not set
for plain ASCII text.)
L Bldg A
+---------+----------------------------+
| | |
| | |
| | | |
(~) 120 V | | | load
| | | |
| | |
|N | |
+-------------+--------+---------+-----+
|utility | | | Bldg A |
|ground | | | ground |
|rod | | | rod |PE BNC shield
----- | | ----- +----->>-------+
--- | | --- |
- | | - |
| | |
| | |
| | |
| | L Bldg B |
+----------------------------+ |
| | |
| | |
| | | |
| | | load |
| | | |
| | |
| N | |
+--------+---------+-----+ |
| Bldg B | |
| ground | |
| rod |PE |
----- +----->>-------+
--- BNC shield
-
You can see from the schematic that the shield is in parallel with both the
neutral and the earth-ground. Being in parallel, it will carry some of the
neutral current, depending on the respective resistances.
Because of both the neutral and the earth-ground, the voltage should never
approach 30 volts (1/4 of the mains voltage). But, there can be a very high
current in the shield of the BNC cable.
Best regards,
Rich
-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.
Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/
To cancel your subscription, send mail to:
[email protected]
with the single line:
unsubscribe emc-pstc
For help, send mail to the list administrators:
Ron Pickard: [email protected]
Dave Heald: [email protected]
For policy questions, send mail to:
Richard Nute: [email protected]
Jim Bacher: [email protected]
Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
<<attachment: Robert_Johnson.vcf>>