Ilan, 

For DC Powered units for use in Restricted Access Locations (RAL) in a CO
environment, then a a field wiring compartment or box is not required. In such
instances, either a terminal block for field wiring or 6 inch leads for field
wiring is acceptable. You may chose to use a Listed field wiring junction box
which is more expensive than providing simply a terminal block or 6 inch leads
for field connections. One such manufacturer of junction boxes is Hoffman. 


Peter 


 Ilan Cohen <[email protected]> wrote: 




Most of you guys are probably familiar with the field wiring requirements
that ITE products must comply with. (mainly for DC powered units) 

When a unit does not comply and the terminal block is not suitable for field
wiring than a manufacture has an option of using 6" leads (not a very
favorable option but it is an option) or redesign of the power interface.

A solution to this problem can be provided with an external box, which will
be sold with the unit. The box clearly must comply with all the requirements
of UL60950 (Terminal block suitable for filed wiring, electrical enclosure,
access to Hazardous energies, etc.).

Does any one know of connection boxes like that that are off the shelf and
are UL approved for filed wiring?
Any other ideas?

Regards

Ilan

----------------------------------------------------------Ilan Cohen
Technical Director, Safety & Telecom Divisions
I.T.L (PRODUCT TESTING) Ltd.
26 Hacharoshet St, POB 211, Or Yehuda, Israel.
Tel 972-3-5339022, Fax 972-3-5339019
[email protected], website: http://www.itl.co.il 





This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
[email protected]
with the single line:
unsubscribe emc-pstc

For help, send mail to the list administrators:
Ron Pickard: [email protected]
Dave Heald: [email protected]

For policy questions, send mail to:
Richard Nute: [email protected]
Jim Bacher: [email protected]

Archive is being moved, we will announce when it is back on-line.
All emc-pstc ! postings are archived and searchable on the web at:
http://! www.ieee communities.org/emc-pstc




  _____  

Do you Yahoo!?
Yahoo! Tax Center <http://us.rd.yahoo.c
m/finance/mailsig/*http://tax.yahoo.com>  - File online, calculators, forms,
and more

Reply via email to